Hello CK,
As you may be aware, capacitor bank switching can be a source of severe voltage transients. Transient (inrush) currents can be also severe. These transient voltages and currents occur primarily when a capacitor bank is energized. Voltage spikes over 2pu can be often be generated, especially if re-striking occurs in the breaker. Back-to-back switching of capacitor banks is even more potentially severe.
To minimize the voltage transients during switching, pre-insertion resistors and inductors are very commonly used in combination with the capacitor circuit switcher (ie breaker).
The 90 degree phase shift between the voltage and capacitor current also presents a challange. As the breaker contacts are seperating, the contacts will normally interrupt the current at a zero-crossing. For a purley capacitive load, the system voltage is a maximum during the zero-crossing of the current. The presence of maximum voltage during the current zero-crossing makes it much more difficult for the interruption device to successfully break the circuit. Hence re-strikes can be common during cap bank switching.
Cooper Power Systems and Josyn Electric have excellent technical articles in PDF format on their web sites. There are many papers that discuss the issues relating to cwitching devices.
Also, a very good reference text is "Electrical Transients in Power Systems", by Allan Greenwood. Mr. Greenwood was at the forefront of vacuum switching develpoement in the early 1970's, while working for GE. His text book is an outstanding referance book, a true invaluable classic.
Regards,
Chris