I am trying to calculate the peak demand in amps to a space. The utility company has informed me that the max reading to the space in a 15 minute period was 29.7 kWh. If i have 120/208 V service to the space, am I correct in calculating this as:
I=kWh/(V*T)=29.7*1000/(.25*208*SQRT(3))= 329.76 amps?
This doesn't seem right. I am concerned about the time. Should this just be 1 hour? I am not familiar with exactly what they mean by a reading within a 15 minute period.
I appreciate any help you can provide.
I=kWh/(V*T)=29.7*1000/(.25*208*SQRT(3))= 329.76 amps?
This doesn't seem right. I am concerned about the time. Should this just be 1 hour? I am not familiar with exactly what they mean by a reading within a 15 minute period.
I appreciate any help you can provide.