Dear all,
We have this big motor for our upcoming project(conceptual stage). What would be the most suitable operating voltage for it. Assuming that its starting method is Direct-on-Line (DOL). Our available operating voltages (at 50Hz) are:-
a) 3.3kV
b) 6.6kV
c) 11kV
Is it advisable to use 6.6KV or otherwise(with reasons)? Thanks for your help.
rgds,
Zak
We have this big motor for our upcoming project(conceptual stage). What would be the most suitable operating voltage for it. Assuming that its starting method is Direct-on-Line (DOL). Our available operating voltages (at 50Hz) are:-
a) 3.3kV
b) 6.6kV
c) 11kV
Is it advisable to use 6.6KV or otherwise(with reasons)? Thanks for your help.
rgds,
Zak
RE: Operating Voltage for 2.7MW Induction Motor
In general as the horsepower increase the voltage of the most-economic (motor purchase cost) motor increases.
Larger cables are required to carry higher current for the lower voltages. (a big consideration if motors are far from source)
I would think the breakers for the lower voltage choice might be more expensive since more current must be interrupted for same fault mva. (Then again, fault mva might be somewhat lower at the lower volt system.. depending on your system).
RE: Operating Voltage for 2.7MW Induction Motor
1. Robert W. Smeaton, "Switchgear and Control Handbook," Second Edition, Mc-Graw-Hill Book Co., 1987
Reference 1 Table 3B "Standard Voltages for Large Polyphase Induction Motors" indicates:
Voltage [V], 60Hz: HP
460 or 575 100-600
2300 200-4000
4000 or 4600 400-7000
6600 1000-12000
13200 3500-25000
Suggestion: 50Hz will require to reduce those HPs somewhat
M.G. Say, Alternating Current Machine book indicates lower limits of ratings that may typically be (50Hz):
150kW for 3.3kV
300kW for 6.6kV
1MW for 11kV
Definitely, the HP will be decisive in an economical voltage level selection.
RE: Operating Voltage for 2.7MW Induction Motor
I feel 6.6kv wil be optimal for DOL START what is your power transformer rating.you have to do voltage drop study before going for this option
When you have 6,6kv supply 3.3 kv is not advisable because you have breakers in thr market most are 11 kv