Have a 60 conductor 14 AWG cable going out 300' in 1.5" plastibond conduit to level switches, open/closed valve position switches and pressure switches out in a tank farm. While performing a monthly interlock check found that the inputs to the DeltaV DI card never changed state from "1" to "0". The input wires have 60 volts of induced voltage. Every 20' of the plastibond conduit we tied the sections to ground and the voltage came down by 4 volts for evey ground added. Now the induced voltage is down to 32V AC which is under the "off" threshold (34V AC) of the input to the DI.
We are grasping at straws here to rectify this problem. Now in the process of putting snubbers 1uF cap in series with a 100 ohm resistor to put a 2500 ohms AC load to ground to discharge this induced voltage.
Anybody have any ideas on this? Thanks Frank.....
We are grasping at straws here to rectify this problem. Now in the process of putting snubbers 1uF cap in series with a 100 ohm resistor to put a 2500 ohms AC load to ground to discharge this induced voltage.
Anybody have any ideas on this? Thanks Frank.....
RE: DeltaV DI 8 channel 120V AC Isolated induced voltage problem
14 guage wire seems excessivly large. How much current is switched?
RE: DeltaV DI 8 channel 120V AC Isolated induced voltage problem
RE: DeltaV DI 8 channel 120V AC Isolated induced voltage problem
RE: DeltaV DI 8 channel 120V AC Isolated induced voltage problem
Try some 1-watt 33-68KO reisitors across the inputs of your logger.
RE: DeltaV DI 8 channel 120V AC Isolated induced voltage problem
What is the DELTAV DI card? What does it do? Why haven't you
notice this problem before?
Send me your E-mail addr and fax#
<nbucska@pcperipherals.com>
RE: DeltaV DI 8 channel 120V AC Isolated induced voltage problem
Check page 19 for the specs.
Here is what appears to be working. Put a snubber of 1uF cap in series with a 100 ohm resistor to put a 2500 ohms AC equivalent load to ground to discharge this induced voltage.
RE: DeltaV DI 8 channel 120V AC Isolated induced voltage problem
RE: DeltaV DI 8 channel 120V AC Isolated induced voltage problem
'Delta V' is the name of a DCS marketed by Emerson, who bought out the original vendor Fisher-Rosemount a year or two ago.
'DI' is a digital input card for the above system.
Kbradio,
Have you lost a system ground connection? The sudden appearance of this problem indicates an abrupt change in the system behaviour. If you haven't changed the installation, or added any plant which is near, or routes its power near, the inputs to your DI card wiring, that is the line of inquiry I would initially pursue.
-----------------------------------
Start each new day with a smile.
Get it over with.
RE: DeltaV DI 8 channel 120V AC Isolated induced voltage problem
Added snubbers across the 12 discrete inputs to drain the induced voltages to ground through a 2500 ohm impedance a 1uF cap in series with a 100 ohm resistor. It appears the 8 channel discrete input card with its 60K ohm input impedance doen't have a built in snubber circuit across all 8 of its inputs.