Hotel Electrical Loads
Hotel Electrical Loads
(OP)
I'm reviewing the electrical load of a 1000 bedroom hotel in London. I have not had much experience with the design of hotels but would suggest that a figure of about 2kW could be mutlipied by the number of bedrooms to give you the maximum demand of the entire building. This would include small power, lighting, a/c, cooking ect.
Is this a fair figure based on anyones experience?
Is this a fair figure based on anyones experience?
RE: Hotel Electrical Loads
RE: Hotel Electrical Loads
Some comparative data of load from other hotels in the area would be the best resource.
RE: Hotel Electrical Loads
Anyway PM me if you need more details (we're in Ireland), we can also help you with the card access system if you don't already have one....sorry, am I getting too commercial for this forum??
RE: Hotel Electrical Loads
a)For each room:
600 W for lights and general power
1500 W to 2000 w for HVAC if electric heaters are used. If hot water is used then less just the fan load. Please ask the HVAC designer the load for HVAC.
Therefore depending upon the type of heating anywhere between 1 to 2 kW per room.
b)Lighting and general power for areas excluding rooms. This could be estimated by using 40 VA/sq.m
c)Other HVAC loads: Chillers, pumps and fans. The HVAC designer will give these loads
d) Lifts: The lift designer will give this load.
e)Plumbing: Plumbing designer will give this load
f)Audio/Visual: Generally hotels have conference rooms with audio/visual facility . Audio/visual system designer will give this load
g)Kitchen: Kitchen consultant will give this load
h)Restaurants: Restaurant operator or kitchen consultant will give this load
i)Outdoor flood lighting, signage