Pump Question

Pump Question

Pump Question

(OP)
I'm trying to size a pump for a heating and cooling application for a chemical process.  They need about 80 gpm with 275-300 ft of head using 55% ethylene glycol.   The temperature range is 0 degrees F to 135 degrees F.  I've been looking a centrifugal pumps but keep ending up at the top of the pump curve.  Would a gear pump be a better use?  Or will I run into problems with the gear pump because of the temperature swings and thermal expansion of the gears?  Is there a "rule of thumb" that says if above a certain head pressure a gear pump is better application?

Thanks

RE: Pump Question

Not sure what you mean about "top of the curve", but I assume it means something like the pumps you are looking at are barely able to meet the flow demand, or on the edge.

80 gpm @ 300 feet of head is absolutely not a problem for centrifugal pumps.

Unless there is something you are not telling us, piston pumps would never be considered for that application.

Solution - You are not looking at the right pumps or right manufacturer.
That basic requirement of 80 gpm @ 300 feet is doable with 10,000 different pumps by 500 different manufacturers to start off, some will be eliminated by other criteria such as NPSHr, Ns, Nss, Efficiency, curve geometry, range, etc.

PUMPDESIGNER

RE: Pump Question

(OP)
What I mean by top of the curve is that a small change in pressure creates a big change in flow or I am essentially in the flat part of the curve.  I've been using the Bell & Gossett program to size the pump, but a difference in 5 psi may mean a change of 20 gpm.

I have spoken with Viking and they think a lobe pump would be the best application because of the thiness of ethlyene glycol at 135 degrees F.  I said that I might be able to change some of the arrangement and change the pressure drop to 200 feet of head.  They thought a gear pump might work.  I don't have much experience with lobe pumps. What do you think?

RE: Pump Question

There is no inherent problem in running on the flat part of a centrifugal pump curve; the pump will run at the intersection of the pump curve and the system curve whatever. If you are running pumps in parallel then you would have to beware. In this instance it is normal practice to fit a discharge restriction orifice to each pump before they common to prevent problems (you need a slightly higher head pump therefore).
If you are trying to run with no control on the system,then you will get fluctuation, but if you want no fluctuation you will have some sort of control system.

I cannot see anything in what you are saying that prevents the use of a centrifugal pump.

RE: Pump Question

B&G has a centrifugal pump that will work in this application.  Contact your local rep and they can help with the sizing.  If you have just a single circut, check out the B&G triple duty valve, it is a shut off, check and flow control valve all in one.  You can set the valve to your desired flow rate.  As tonyh mentioned, this will require a slightly higher head pump, but B&G has all the information you need to calculate the additional pressure loss.

RE: Pump Question

Although meant to render a constant flow rate at constant speed of rotation, gear pumps may be mechanically sensitive to temperature variations and shocks in regard to the thermal expansion of its parts, and the resulting changes in clearances, and possible pump or seal damage.
0oF is a cryogenic condition that may require pre-cooling of the pump. Anyway, materials of construction should be selected accordingly.

As for myself, I don't see why a centrifugal couldn't meet the requested operating conditions with suitable flow control devices.

EG is considered somewhat toxic and should be handled with care.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close