Noisy Pump

Noisy Pump

Noisy Pump

(OP)
Hello all,

We are currently looking at an application where there has been a complaint that the pump is too noisy. The pump has been replaced once and the system is only two years old.

The system is a boiler loop feeding a plate heat exchanger, the pump is an inline circulator and temperature is controled with a three-way valve. My concerns with the system is that: there is no air seperator/air release, there is no check valve after the pump, there is no expansion tank, and finally the system was never balanced properly.

The problems I envision are: air in system causing cavitiation-like damage, flow from other pumps spinning impeller in reverse while not operating and causing start-up problems, pump running through the pump curve as head is lower than expected and velocity through pump and heat exchanger is too high.

I am going out to check the installation. Is there anything else I should be looking for, and do my assumptions about the possible (probable) causes of the problem look reasonable?

Thanks all,

RE: Noisy Pump

What are the temperatures after PHE and in the bypass line of 3 way valve? If the difference is high then you will have some hammering.

I think you covered everything on hudraulics. Also check bearings and floating of shaft(impeller may be touching the casing).

Regards,

RE: Noisy Pump

Consider hiring a pump expert for this.
But, if you have the situation whre no one minds you learning on their dime, here are some things to start with.

You did not state why the pump was replaced, where the damage was, what kind of damage.  Cavitation damage is very specific and easy to diagnose, well maybe easy for experienced knowledgeable persons anyway.

Air cannot cause cavitation, ever.  Air does not usually damage pumps unless the amount of air is sufficient to cause vibration, expose the seal faces, etc.

Your application often has pumps with very high specific speeds and high suction specific speeds.  If qualified experts selected the pumps they are probably Ok, unless someone changed the specs (you know, value engineering).

If the pump is as I said high Ns and Nss, then those buggers are very tricky suckers to work with indeed and you really should find help.

PUMPDESIGNER

RE: Noisy Pump

The first things that I would want to check out for myself are:

1-  How much STRAIGHT pipe is connected to the pump suction port?  If it isn't at least 10 diameters, the orderliness of the flow into the pump is likely to be compromised, and the "real" NPSHr can be greatly increased.

2-  How does NPSHa compare with NPSHr under all potentially troublesome operating conditions?  Bear in mind that the the stated NPSHr represents the pump already having lost 3% of head to cavitation.  For quiet operation, your pump may need NPSHa to be anywhere from 2 to 15 or even 20 times the "3%" NPSHr.

3-  Make sure of the accuracy of all of the pump "curves."  It matters very much whether they are from actual pump tests or just generic curves for the pump model.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

eBook - Integrating the Engineering Ecosystem
Aras Innovator provides multiple options for integrating data between systems, depending on the scenario. Utilizing the right approach to meet specific business requirements is vital. These needs range from authoring tools, federating data from various and dissimilar databases, and triggering processes and workflows. Download Now
Research Report - Simulation-Driven Design for SOLIDWORKS Users
In this engineering.com research report, we discuss the rising role of simulation and the paradigm shift commonly called the democratization of simulation. In particular, we focus on how SOLIDWORKS users can take advantage of simulation-driven design through two analysis tools: SOLIDWORKS Simulation and 3DEXPERIENCE WORKS. Download Now
White Paper - Industry 4.0 and the Future of Engineering Education
With industries becoming more automated, more tech-driven and more complex, engineers need to keep their skills and knowledge up to date in order to stay on top of this wave—and to be prepared for the Industry 4.0 future. The University of Cincinnati offers two online Master of Engineering degree programs designed specifically for practicing engineers. Download Now
eBook - The Design Gridlock Manifesto
In this eBook, you’ll learn 6 ways old CAD technology slows your company down and hear how design teams have put those problems to rest. “The Design Gridlock Manifesto” shares first-hand modern CAD experiences from 15 companies around the world. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close