Hello,
I would like to comment on the postings offered above on this thread.
Often the confusion stems from the notion that there is such a thing in the B1.3 rules as "Category M fluids" or "Lethal Service fluids" - there is no such thing. When THE OWNER determines the "Fluid Service" that will prevail in the design, fabrication and testing of the PIPING SYSTEM, the fluid contained in the pipe is only one consideration. Sodium Hydroxide is neither a "Category M fluid nor is it a "Normal Service" fluid. By the way, "lethal service" is an ASME B&PV Code term, NOT a B31 term. However, you will likely find that THE OWNER will decide to specify "Category M fluid service" for piping systems about as often as the pressure vessels in the system are specified for lethal service - not very often.
"Caustic should be classified as Normal Fluid Service" - well, no. Again, caustic fluids are just fluids to B31.3. When THE OWNED specifies the Fluid Service FOR THE PIPING SYSTEM, the fluid contained within the pipe AND the particular set of operating circumstances as well as the safeguards that will be in place must be considered.
A very important point - The ASME B31 Code for Pressure Piping, B31.3, Process Piping DOES NOT "classify" Sodium Hydroxide piping systems or any other piping systems. ONLY THE OWNER can do that (using the guidance provided in the B31.3 Code).
I cannot over emphasize the ABSOLUTE NEED to get THE OWNER involved in making this decision.
The opinions provided above are my opinions only and they do not necessarily reflect the opinions of ASME International, or the consensus opinions of the entire B31.3 Code Committee.
Best regards, and a happy holiday season, John