My situation:
1. Tube lintel spanning 42.5 ft.
2. Carrying about 15' EIFS & 8" metal studs.
3. Window head height is about 11'
4. CC wind load of about 15 psf.
5. EIFS deflection criteria is L/240, which for this span is a little over 2".
6. I want to use 8" wide tube to hide it in wall and post off of face of columns.

I am worried about the head joint at the window for horizontal deflection. What is the maximum absolute horizontal deflection permissible at top of window? I have calls in to a couple of local window mfrs, but am interested to hear others' opinions.

My client has agreed that we can put in some additional vertical steel, but we are trying to avoid kickers. My preference is the tube lintel for ease of fabrication and erection.

Thanks in advance.

RE: Lintel/Window Head Deflection Limit?

I would say that the answer is depending on how the window-wall system is built, all, mullions and frames respect bearing structure or bearing points, and glazing itslef within the frames. Contact between the glass and the frame is understood must be prevented because both impact and heat source, heat sink there are known contributors to glass breakup.

In general, most well designed window framing should accommodate well serviceability deflections of about 1/400 in most circumnstances if only because this or 1/500 are both ordinary deflection limits at service level both for vertical deflection and sway in whichever the direction. Since they must accompany the building in such excursions, most window systems shouldn't have problem with that.

Note many codes (say EHE) and texts choose to establish as well a maximum deflection of 1 inch or even 1 centimeter at service level (not even under probabilistic loads, but characteristic ones). This means such texts and codes want the thing rigid and straight, and both camber and attent consideration of the excursions or the elements likely to suffer damage must be made. These requirements may force to select alternative structural solutions that suit better the requirements.

RE: Lintel/Window Head Deflection Limit?

L/240 is too liberal for dealing with glass.  I would not use anything less than L/360, the same that is usually applied for plaster.  I would contact the Technical Services Dept. of a window wall manufacturer and check what they expect for deflection limits.  My guess is L/360 is the mininum and more likely L/500, as suggested by ishvaaag.

Another thought is that most manufacturers use a slip channel detail around the window frames to help accomodate the expected building deflection.  

By the way, you don't have to worry only about the glazing.  I've seen steel stud partitions installed tight to a building from buckle due to deflection from the frame.  They too need to allow for deflection.

RE: Lintel/Window Head Deflection Limit?

Although building codes allow a deflection limit of L/240 (maximum deflection limit,dead load), a deflection of 2.13" at what I would consider a "Critical Component" is excessive.
Deflection at critical components should be limited from 1/2" to 1" for safety factors and component reliability. I would limit deflection to L/600 (0.85"), insuring component reliability.

RE: Lintel/Window Head Deflection Limit?

PorkChopBobby,

In addition to the comments about limiting the deflection, make sure you also consider how the deflections affect other components.  A horizontal deflection of 1/2" or 3/4" might sound okay to a window manufacturer, but what happens if the window head is 12" from the ceiling or underside of the slab?  What happens to the portion of stud above the slab if the rotation about the support is that great?

Your wind load for components and cladding is also at the extreme low end of the spectrum.  In the northeast USA, we seldom see walls under 25 psf, and more often than not, we are working above 30psf.

To date, I have not seen a 40ft + span on a wind girt like this.  I am working a project right now at 30psf where the tubes are HSS8x4x3/8 and spanning 24ft with something like 10ft of tributary wind area.  I can't imagine stretching that another 15ft+.  If you can make it work, be sure that it can support itself under its own weight.

On another thought, is this at the underside of a roof span?  Maybe you could use kickers above and cantilever the studs below the slab?  Similarly, a piece of tube at the top of the studs could also help counteract the forces at the bottom, if the necessary steel is there to connect it to.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

eBook - Integrating the Engineering Ecosystem
Aras Innovator provides multiple options for integrating data between systems, depending on the scenario. Utilizing the right approach to meet specific business requirements is vital. These needs range from authoring tools, federating data from various and dissimilar databases, and triggering processes and workflows. Download Now
Research Report - Simulation-Driven Design for SOLIDWORKS Users
In this engineering.com research report, we discuss the rising role of simulation and the paradigm shift commonly called the democratization of simulation. In particular, we focus on how SOLIDWORKS users can take advantage of simulation-driven design through two analysis tools: SOLIDWORKS Simulation and 3DEXPERIENCE WORKS. Download Now
White Paper - Industry 4.0 and the Future of Engineering Education
With industries becoming more automated, more tech-driven and more complex, engineers need to keep their skills and knowledge up to date in order to stay on top of this wave—and to be prepared for the Industry 4.0 future. The University of Cincinnati offers two online Master of Engineering degree programs designed specifically for practicing engineers. Download Now
eBook - The Design Gridlock Manifesto
In this eBook, you’ll learn 6 ways old CAD technology slows your company down and hear how design teams have put those problems to rest. “The Design Gridlock Manifesto” shares first-hand modern CAD experiences from 15 companies around the world. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close