Sizing current transformer for monitoring motor current.
2

Sizing current transformer for monitoring motor current.

Sizing current transformer for monitoring motor current.

(OP)
I am going to monitor the motor current of a 100hp motor with a fla of 99 amps.  Should I get a 600/5 amp current transformer to handle the lock rotor current or just a 100/5 amp?
paffy
Replies continue below

Recommended for you

RE: Sizing current transformer for monitoring motor current.

Suggestion: The CTs must have enough iron to transfer the current proportionally at least to the locked-rotor current. Therefore, 600/5 appears to be more appropriate than 100/5 CT. This rule is usually applied when CTs are used with overload relays, NEMA starter 5 and up. When you monitor current, it depends on the monitoring intent, and the full load current. Perhaps, one may select a smaller ratio than 600/5; however a larger than 100/5.

RE: Sizing current transformer for monitoring motor current.

Off the top of my head I can only remember the data for one motor circuit in our plant (the one I worked on last week).  4KV 700hp motors with approximately 100A FLA.  They used 600:5 CT's in that application... I assume they designed it right.  Those CT's drove both protection and indication.

It seems like the general considerations for selecting CT should include the following:
- I believe that higher-ratio CT will be more expensive.  Therefore select lowest ratio that meets your requirements.
- Continuous current (at the level protected by the circuit) should not exceed  the CT rating. From this requirement, if motor is overload protected at 125%, then CT ratio needs to be 125:5 or higher (I think 150:5 is the next higher standard ratio).
- CT saturation should not interfere with protective relay operation or cause misoperation.  If CT is for indication  only, then you probably don't care.  If the CT drives an instantaneous relay for short circuit protection, then you would want to check the available fault current and verify that your CT will perform reasonably.  For example a C100 with 1 ohm burden max, you don't want to use a relay with rating of less than 1/20 of the available fault current.
- CT should coordinate with the relay.  If you have a specific relay in mind, that might limit your choice of CT's from a standpoint of the current ranges that the relay can accept.

RE: Sizing current transformer for monitoring motor current.

There is a recent post in the electric-power-engineering forum entitled "ct calculation" which covers similar topic with lots of links.

RE: Sizing current transformer for monitoring motor current.

If you are driving an analog current meter (5A input full scale), you'll peg out the meter unless you select approx 600/5 or higher depending on your expected inrush current.

See my noncommercial website of motor monitoring/maintenance links at:
http://geocities.com/pschimpf/motorpage.htm

RE: Sizing current transformer for monitoring motor current.

Whoops.  I added that blurb about my website as a signature.  But it gets merged in with the text in a way that I don't like.  My website has nothing that addresses
your question.

ps - does anyone know how to delete or modify a post?

RE: Sizing current transformer for monitoring motor current.

Cool web page electricpete!

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login



News


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close