No more "Rings", radials for everyone.

No more "Rings", radials for everyone.

No more "Rings", radials for everyone.

(OP)
After attending a course to update my "Testing & Inspection" knowledge. I was surprised to hear the course instructor say that with the alignment of BS7671 regulations with european legislation that the UK 13 amp socket will be phased out and, the end of the "ring circuit" is nigh (probably not before time). I was informed that this is already in the pipeline and would be a reality within the next couple of years. Is this indeed the case?

Anyone have any more info on this?

RE: No more "Rings", radials for everyone.

Coming from another strange place I have to ask - "Whats a ring circuit?"

Don

RE: No more "Rings", radials for everyone.

(OP)
Don
A ring circuit is unique to UK installations. The circuit is used for power outlets and is connected in the following manner. A cable (2.5mm csa) is taken from a fuse, or circuit breaker, within a distribution board and looped between all the socket outlets in the circuit. This cable is then looped from the last socket in the chain back to the same fuse in the distribution board. This has the effect of supplying the sockets with a parallel feed cable, effectively dividing the current through each leg of the parallel path. The fuse or beaker is rated at 30 - 32 amps and because each plug (UK 13 amp) has an individual fuse inside it, this provides overcurrent protection to each appliance plugged into the circuit. More info can be obtained from BS7671:1992 or various other publications such as "The Electricians Guide to the 16th Edition of the IEE Regulations" by J F Whitfield, published by EPA Press.

I hope this goes some way to answering your query.

RE: No more "Rings", radials for everyone.

What about a CENELEC harmonization of standards with IEC Standards?

RE: No more "Rings", radials for everyone.

(OP)
I believe that the harmonisation of CENELEC and IEC Standards is part of the same process, but don't quote me on that one. If it is then it could take some time for all this  to be finalised.

RE: No more "Rings", radials for everyone.

alang
  Thanks for that you,ve cleared the fog out for me. Comment only: do that down here and you stand a real good chance of loosing your licence  if the supply authority finds out or your "crown jewels" if the next sparky finds you. I can see the rationale of reducing IR drop but it would make it a s**t to trace the circuits and crowd the db. We use up to 32A on 2.5mm2  2c&e pvc/pvc tps type cabling but one end only at the db

Again thanks
Don

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

Low-Volume Rapid Injection Molding With 3D Printed Molds
Learn methods and guidelines for using stereolithography (SLA) 3D printed molds in the injection molding process to lower costs and lead time. Discover how this hybrid manufacturing process enables on-demand mold fabrication to quickly produce small batches of thermoplastic parts. Download Now
Design for Additive Manufacturing (DfAM)
Examine how the principles of DfAM upend many of the long-standing rules around manufacturability - allowing engineers and designers to place a part’s function at the center of their design considerations. Download Now
Taking Control of Engineering Documents
This ebook covers tips for creating and managing workflows, security best practices and protection of intellectual property, Cloud vs. on-premise software solutions, CAD file management, compliance, and more. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close