Pipe Bracing for Tall Building Sway
Pipe Bracing for Tall Building Sway
(OP)
Hello I am a PE with 6 years of experience mainly focusing on mechanical pipe supports for skyscrapers in NYC.
We have two senior engineers at my company who have differing views on the need for bracing on top of the building. Think 1000' tall skyscraper.
I am struggling to find in the codes if I have to design lateral or seismic bracing for the piping towards the top of these buildings.
I have read MSS-SP 58, MSS-SP 127, and the NYC building codes.
As far as I can tell based on MSS-SP 127 any pipe subject to wind load needs some type of bracing. In general we put seismic supports on piping involved in life safety but for HW,PCW, CHW piping we do not include any type of bracing.
Just curious if anyone can point me to a specific code that covers building sway for mechanical pipe supports.
Thanks!
We have two senior engineers at my company who have differing views on the need for bracing on top of the building. Think 1000' tall skyscraper.
I am struggling to find in the codes if I have to design lateral or seismic bracing for the piping towards the top of these buildings.
I have read MSS-SP 58, MSS-SP 127, and the NYC building codes.
As far as I can tell based on MSS-SP 127 any pipe subject to wind load needs some type of bracing. In general we put seismic supports on piping involved in life safety but for HW,PCW, CHW piping we do not include any type of bracing.
Just curious if anyone can point me to a specific code that covers building sway for mechanical pipe supports.
Thanks!
RE: Pipe Bracing for Tall Building Sway
While it's not a life safety item it seems prudent to minimize damage from design loads (such as seismic acceleration) for the headers.
RE: Pipe Bracing for Tall Building Sway
Lots of ways to skin that cat. Can you show us what your proposed brace scheme looks like?
--Einstein gave the same test to students every year. When asked why he would do something like that, "Because the answers had changed."
RE: Pipe Bracing for Tall Building Sway
This goes into the realms of Good Engineering Practice and the general sections of any piping design code which is do whatever is required to prevent failure of your pipe.
Code writers can't be expected to know everything and consider every set of circumstances and given the very few numbers of 1000ft high buildings this is one of them.
Read the intro and general sections at the start of your piping code if you need some sort of crutch for what is to me a simple must do.
Remember - More details = better answers
Also: If you get a response it's polite to respond to it.
RE: Pipe Bracing for Tall Building Sway
you won't find a code.
consider this reference as a guide: https://wbdg.org/FFC/DOD/UFGS/UFGS%2023%2005%2048....