transformer for connecting 34.5 to 12.47 kV
transformer for connecting 34.5 to 12.47 kV
(OP)
All,
I'm looking to specify an 8 MW transformer for connecting two four wire distribution systems that are in phase. This can be accomplished with an auto-connection, but will this be the most cost effective way to go? I know that's commonly the case at transmission voltages, but unsure at the lower voltages.
It will have a deenergized tap changer on the 34.5 side, and an LTC on the 12.47. Power might flow in either direction.
Full system unbalanced loading must be accommodated as discussed in thread238-514665: Do I need a tertiary?. From that thread it appears the load unbalance might be handled by either a tertiary or a five limb core. Shall I leave that choice to the manufacturer as suggested by davidbeach, or are there other considerations?
Thanks.
I'm looking to specify an 8 MW transformer for connecting two four wire distribution systems that are in phase. This can be accomplished with an auto-connection, but will this be the most cost effective way to go? I know that's commonly the case at transmission voltages, but unsure at the lower voltages.
It will have a deenergized tap changer on the 34.5 side, and an LTC on the 12.47. Power might flow in either direction.
Full system unbalanced loading must be accommodated as discussed in thread238-514665: Do I need a tertiary?. From that thread it appears the load unbalance might be handled by either a tertiary or a five limb core. Shall I leave that choice to the manufacturer as suggested by davidbeach, or are there other considerations?
Thanks.
RE: transformer for connecting 34.5 to 12.47 kV
When one this sentence into the German to translate wanted, would one the fact exploit, that the word order and the punctuation already with the German conventions agree.
-- Douglas Hofstadter, Jan 1982
RE: transformer for connecting 34.5 to 12.47 kV
RE: transformer for connecting 34.5 to 12.47 kV
RE: transformer for connecting 34.5 to 12.47 kV
I have also heard the voltage ratio might be a problem. Our supplier serves our 69kV system with a 230 kV auto, so there must be no hard limit here.
I'm still waiting to hear from manufacturer three. In the meantime, I'm considering using specs that allow for either configuration.