allowable settlement for substation equipment
allowable settlement for substation equipment
(OP)
Hi everyone,
I'm designing foundations for a transformer, breaker, disconnect switch, control building, and other substation equipment.
The foundations are located above a 20m deep soft clay layer, so I want to know the settlement criteria for those equipment.
I have read ASCE113 but I only found a deflection limit for structures.
The foundation that I am concerned about is the transformer foundation. Its size is about 8m x 5m x 0.6m and its loading is about 45 kN/m^2(kPa) or 0.94 ksf.
Where can I find an allowable settlement for those foundations?
I'm designing foundations for a transformer, breaker, disconnect switch, control building, and other substation equipment.
The foundations are located above a 20m deep soft clay layer, so I want to know the settlement criteria for those equipment.
I have read ASCE113 but I only found a deflection limit for structures.
The foundation that I am concerned about is the transformer foundation. Its size is about 8m x 5m x 0.6m and its loading is about 45 kN/m^2(kPa) or 0.94 ksf.
Where can I find an allowable settlement for those foundations?
RE: allowable settlement for substation equipment
RE: allowable settlement for substation equipment
The TX will have limits on levelness but maybe not global settlement.
Remember - More details = better answers
Also: If you get a response it's polite to respond to it.
RE: allowable settlement for substation equipment
These type of equipments are not that sensitive to have any worst kind of effects in case your foundations are within the allowable limits.
If you are worried or your substation Electrical engineer would discard your design when are having settlement of about 25-50mm depend on your type of foundation, it can cause some electrical field problem, then you should ask and discuss with the electrical department, but mostly that would not be a problem.
However another point is that, these type of supporting structure of substation equipment are usually not depedent on each other in a very restricted way, just cables are passed from equipment to another, excluding Gantry having Tension wire from Substation to Transmission line towers.
Follow your Geotechnical allowable settlement criteria.
Time is far more precious than you can imagine.