Minimum ground clearance required as per IEC for Transmission line

Minimum ground clearance required as per IEC for Transmission line

Minimum ground clearance required as per IEC for Transmission line

(OP)
Hi all,

In which IEC, it is mentioned the minimum ground clearance for different voltage transmission lines.

Regards,
Balaji

RE: Minimum ground clearance required as per IEC for Transmission line

Google say 60071

Did you even try to do some research?

Remember - More details = better answers
Also: If you get a response it's polite to respond to it.

RE: Minimum ground clearance required as per IEC for Transmission line

@ balaji.srinath
Did you try IEC 61936-1 title Power installations exceeding 1kV AC and 1.5kV DC Pt 1.. See whether any data therein that your are looking for.
Che Kuan Yau (Singapore)

RE: Minimum ground clearance required as per IEC for Transmission line

(OP)
Hi littleinch & che12345

In both the IEC standards 60071 & 61936, Ground clearance w.r.t Transmission line is not mentioned..only phase-phase & phase-earth (conductor - conductor & rod - structure) is mentioned w.r.t BILs.

Regards,
Balaji K

RE: Minimum ground clearance required as per IEC for Transmission line

Clearance above ground seems to be a country by country thing based on historical clearance and country specific reasons.

Most trucks are max 5m, maybe 5.5 so add that to the phase to earth distance and add a bit for safety.

The "bit" probably varies between countries.

Remember - More details = better answers
Also: If you get a response it's polite to respond to it.

RE: Minimum ground clearance required as per IEC for Transmission line

Hi Balaji,
to my knowledge, the only requirements regarding clearances are reported in the European Standard EN 50341-1. 
In principle, the armonized standard requires basic clearances and reports the attendant formulae.
A "basic" height of 5 m is assumed for objects beneath OHLs in "normal" areas; electric (lightning or switching) clearances shall be added to the 5 m to obtain the clearances.
National annexes (EN 50341-2-XX) report specific values for each country.

Si duri puer ingeni videtur,
preconem facias vel architectum.

RE: Minimum ground clearance required as per IEC for Transmission line

IEC 60919: “Overhead lines - Design criteria, construction and maintenance.”

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login



News


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close