Temporary Trailer wastewater pumping options

Temporary Trailer wastewater pumping options

Temporary Trailer wastewater pumping options

(OP)
I am working on a group of temporary office/training buildings. 8 buildings totaling just under 19,000sf. We have calculated an occupant load of 491 people ~ rounding to 500. Based on some research I'm calculating about 13 gal/person/day ~ 6500gpd.
Due to site constraints, I can't tie into gravity sewer directly so I'm looking at a small pumping solution. obviously I don't need a 6500 gal tank/station but I am troubled with converting the gpd to gpm to size my pumps and tank. I suppose much of the flow will be used during the lunch hour and I would not want a situation where the flows backup into the trailers.
I've been looking at some prepackaged pumping solutions like Little Giant.
This project is in northern Florida for a US govt owned property so permitting and engineering requirements are atypical.
We don't have a detailed topo survey but based on a site visit, I believe we are looking at about 15'-20' max head depending on pump elevation inside the tank.
my quesitions:
1) is there a good resource to backup flowrate calculations?
2) Best way to convert GPD to gpm for pump sizing?
3) Am I underestimating the station design and should be looking at a much larger, standard, lift station?

Please keep in mind that this is not expected for a 30 year duration as it is temporary trailers, however you know how "temporary" ends up being more long term than originally planned. (see schools and churches for example)
I will state that the gov't does allow for contracting a pump-and-haul solution but I don't think they want to be forking over $ daily/hourly pump-and-haul.
FYI, this isn't my first foray into lift station design, it's just been a few (15) years.

RE: Temporary Trailer wastewater pumping options

Look into the use of a product like the E-One system. Size the pumps for a daily average flow 10,000 gpd/24 and a peak hourly flow of 6-7 times the daily average flow.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login



News


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close