Need help on SDS screw capacity calculations (TJI Joist)

Need help on SDS screw capacity calculations (TJI Joist)

RE: Need help on SDS screw capacity calculations (TJI Joist)

Is 1/2" of embedment into the studs enough? Doesn't feel that way to me. As long as you specify screws long enough to get the minimum penetration into the studs, then I don't see the 4" ledger having any negative effect on screw capacity.

RE: Need help on SDS screw capacity calculations (TJI Joist)

Agree with Jayrod, think the 4x_ ledger is a bit much, I would consider an 1.75" LSL ledger that matches the height of the TJI roof joists. That gives you more room to work with the SDS screw length. I've never liked installing screws into the narrow edge of studs, I'd either use a post at this location to attach the ledger, or if this is existing construction, install blocking between the studs that is attached positively to the studs and then SDS into the blocking instead of the studs.

RE: Need help on SDS screw capacity calculations (TJI Joist)

Or let in the ledger into the studs so the vertical load is actually transferred in bearing as opposed to relying on the screws.

RE: Need help on SDS screw capacity calculations (TJI Joist)

Ah, missed it on first glance, but now I see why you drew a 4x_, for the twist strap to restrain the parapet out of plane load. There are alternate options that can be used instead of a twist strap.

How is this detail getting roof diaphragm load into the actual shear wall sheathing? I'd have to think a bit more on if I am comfortable loading a couple SDS screws in the narrow face in weak axis bending of the studs.

RE: Need help on SDS screw capacity calculations (TJI Joist)

(OP)
Actually, I sent a project with this typical detail (also before on some previous projects as usual but didn't have to submit any calc for this), but now city sends structural comments including SDS screw calculation manually

RE: Need help on SDS screw capacity calculations (TJI Joist)

SDS is a proprietary product, so you'll need to reference the Simpson design manual for capacities and minimum penetration requirements.

RE: Need help on SDS screw capacity calculations (TJI Joist)

Refer to the Simpson connector manual. What is the capacity of a single SDS screw with 0.5" of penetration at the applicable Load Duration? My guess is the value will be 0lbs, but you'll need to check with Simpson to confirm.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login



News


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close