Seasonal Buildings, Snow Load and Risk Category
Seasonal Buildings, Snow Load and Risk Category
(OP)
I am designing a group of buildings for a summer campgrounds in a high (~60 PSF) snow load area. The buildings will be unoccupied and winterized/unheated during the winter.
Buildings are risk category II
My thoughts regarding snow loads
1. Design snow load using a Ct of 1.0, Risk Category II
2. Use a Ct for unheated structures since the buildings will be unheated in the winter.
My reasoning to use Ct of 1.0 is that when the building is unheated it'll be unoccupied and arguably Risk Cat I. If the buildings end up getting used during the winter (not unoccupied) then they'll be heated.
Curious to hear others thoughts.
Buildings are risk category II
My thoughts regarding snow loads
1. Design snow load using a Ct of 1.0, Risk Category II
2. Use a Ct for unheated structures since the buildings will be unheated in the winter.
My reasoning to use Ct of 1.0 is that when the building is unheated it'll be unoccupied and arguably Risk Cat I. If the buildings end up getting used during the winter (not unoccupied) then they'll be heated.
Curious to hear others thoughts.
RE: Seasonal Buildings, Snow Load and Risk Category
RE: Seasonal Buildings, Snow Load and Risk Category
I mean the Ct factor in determining snow loads from ASCE 7
RE: Seasonal Buildings, Snow Load and Risk Category
I'd use 1.2 for my Ct. If one of these collapses, the owner (or their insurance company) will still be looking for a pound of flesh to offset their loss whether it was occupied or not. Skimping on this puts a real nice target on your back.
RE: Seasonal Buildings, Snow Load and Risk Category
RE: Seasonal Buildings, Snow Load and Risk Category
RE: Seasonal Buildings, Snow Load and Risk Category
The flip-side of this is that your argument is logical, and the commentary to ASCE 7 mentions this exact scenario!
Now, if I was going to take this approach, I would still use Ct=1.2, but would use Is=0.8 for Risk Cat. I. Using Ct=1.0 and Is=1.0 makes it confusing/misleading if you'll be communicating that information, like if it's including with your general notes.
RE: Seasonal Buildings, Snow Load and Risk Category
It is one of those things where my mentor failed to explain to me. So if the building the department list it on their website the roof snow load, do I multiply this Ct? I notice the snow load they list on their websites are typically higher than the snow load if I were to compute it from ground snow load from ASCE. I will sharpen my pencil next time.
RE: Seasonal Buildings, Snow Load and Risk Category
If this is a summer cabin with no insulation (which is likely) then Ct=1.0 makes sense. But, if the cabins will at some point be used in the winter, I think there's a good chance that the owner would insulate the roofs making them Ct=1.1. If they're paying for the heat, they'll definitely have a strong incentive to do this. And if that's the case, all of a sudden the roof will no longer meet code if you design it per your method. If you do proceed this way, I would add a note on the plans describing this scenario.
RE: Seasonal Buildings, Snow Load and Risk Category
It's important to recognize the distinction between Roof snow load and Ground snow load.
RE: Seasonal Buildings, Snow Load and Risk Category
RE: Seasonal Buildings, Snow Load and Risk Category
RE: Seasonal Buildings, Snow Load and Risk Category
RE: Seasonal Buildings, Snow Load and Risk Category
RE: Seasonal Buildings, Snow Load and Risk Category
RE: Seasonal Buildings, Snow Load and Risk Category
Especially now that 7-16 is split into two books. I like the ACI 318 format with the commentary in line
RE: Seasonal Buildings, Snow Load and Risk Category
And they're written in such a way that is easy to follow (with some funny old-timey language in there too).
But you're right, let's bog down ASCE 7 so much that we need two books, of which most professionals won't read more than 5% of either one. Don't get it.