"...I have an issue with medium voltage switch gear "schneider ", the control relays always overheated at coil measured by infra camera 80 °c , 110 VDC , and the actual VDC supplied is 122 VDC , but Relay withstand 125 VDC ..."
I have the following opinion for your consideration.
1. No matter what the temperature inside the relay cabinet is, the coil temperature 80 o C is acceptable.
2. Note: Temperature measurement using infra-red camera is always very tricky, affected very much by the emissivity setting and on which spot measurement is taken. You can easily check with a spirit (NOT mercury) thermometer or by coil copper resistance.
3. As pointed out by Mr. davidbeach, some ac/dc relays are intended for momentary say < 1s energization. Some dc relays insert series resistor in the coil circuit after energization when the magnetic iron core gap is closed/contact is closed.
4. SI unit for temperature measurement is o C.
Che Kuan Yau (Singapore)