Sulfuric acid injection for Cooling Water pH control
Sulfuric acid injection for Cooling Water pH control
(OP)
All,
There is a project at our site to inject sulfuric acid into one of our cooling towers to help descale or prevent scaling of our HX tubes. The cooling tower is a 3-cell design, with each cell's water level equalized. Circulation rate is about 20000 GPM total for the tower. Construction of the tower is FRP, converted from previous construction of wood. The basin is constructed of carbon steel. The proposal is to inject acid into the water level of each basin cell, with a pH probe on the water circulation loop. This will be managed by our chemical treatment vendor, Nalco. I have some concerns
How will this impact the corrosion rate of the carbon steel basin? Is there a chance of localized corrosion at the basin where the acid is added? While the pH of the bulk fluid might be within range, at the points where the injection occurs, there could be a very low pH localized there.
When a cell is shut down say for fan maintenance, we shut down/lock out the fan, return water, and make up water to that cell. If the acid isn’t turned off, the pH will get extremely low in that cell’s basin. This is a risk. Obviously this should be controlled by LOTO, but if it’s missed this will be a big problem
When the tower is shut down for maintenance and basin is drained, any drips coming out of the acid addition tubing after the basin is empty will hole-through the basin. The tubing has to be free draining to prevent this from occurring. I could see this happening if we just block in the acid without clearing the line afterward.
These were just the main things I could come up with. I plan on speaking with Nalco to see if other customers with this setup have any issues, but also wanted to poll the forum here for their experiences.
Thanks!
There is a project at our site to inject sulfuric acid into one of our cooling towers to help descale or prevent scaling of our HX tubes. The cooling tower is a 3-cell design, with each cell's water level equalized. Circulation rate is about 20000 GPM total for the tower. Construction of the tower is FRP, converted from previous construction of wood. The basin is constructed of carbon steel. The proposal is to inject acid into the water level of each basin cell, with a pH probe on the water circulation loop. This will be managed by our chemical treatment vendor, Nalco. I have some concerns
How will this impact the corrosion rate of the carbon steel basin? Is there a chance of localized corrosion at the basin where the acid is added? While the pH of the bulk fluid might be within range, at the points where the injection occurs, there could be a very low pH localized there.
When a cell is shut down say for fan maintenance, we shut down/lock out the fan, return water, and make up water to that cell. If the acid isn’t turned off, the pH will get extremely low in that cell’s basin. This is a risk. Obviously this should be controlled by LOTO, but if it’s missed this will be a big problem
When the tower is shut down for maintenance and basin is drained, any drips coming out of the acid addition tubing after the basin is empty will hole-through the basin. The tubing has to be free draining to prevent this from occurring. I could see this happening if we just block in the acid without clearing the line afterward.
These were just the main things I could come up with. I plan on speaking with Nalco to see if other customers with this setup have any issues, but also wanted to poll the forum here for their experiences.
Thanks!
-Mike
RE: Sulfuric acid injection for Cooling Water pH control
==============================================================================
Budget and chemical availabilty are also very important concerns ... Any scheme selected today may, of course, not be the best scheme for tomorrow !!
Sulfuric acid injection may or may not be the best choice for your facility
This paper may help:
https://www.cedengineering.com/userfiles/An%20Intr...
MJCronin
Sr. Process Engineer
RE: Sulfuric acid injection for Cooling Water pH control
acid strength?
degree of premixing?
pH measurement prior to injecting into tower basin?
This is a process design and control issue, so there is no quick answer
RE: Sulfuric acid injection for Cooling Water pH control
Typically their water comes from pretreated water in a separate reservoir or basin, for sediment removal and water treatment, and premixing.
RE: Sulfuric acid injection for Cooling Water pH control
Contact the supplier of chemical treatment in your facility. Not all treatments require Ph adjustment.
Check with Big Companies to get a meaningful answer.
Pierre
RE: Sulfuric acid injection for Cooling Water pH control
1. It is usually premixed/diluted to some degree. Yes this plumbing is usually made of exotic materials.
2. The injection needs to be at a location with significant turbulence, such as right after a pump in order to assure good rapid mixing.
3. You need to be careful where you are measuring pH for your control. Measure too close to the injection and the system will try to over correct. Measure too far away and the lag time will cause large swings in pH.
Get expert advice about this system and control.
Buy a prepackaged system to use. They are expensive and worth every penny.
= = = = = = = = = = = = = = = = = = = =
P.E. Metallurgy, consulting work welcomed
RE: Sulfuric acid injection for Cooling Water pH control
RE: Sulfuric acid injection for Cooling Water pH control
-Mike
RE: Sulfuric acid injection for Cooling Water pH control