Removing expansion tank after system is hot
Removing expansion tank after system is hot
(OP)
What do you think of this one? On a hot water heating system, what if you removed the expansion tank after the system is hot? Everything has expanded and the pressure is stable. worse case, if everything gets cooled down, the pressure would drop. Auto fill would have to be isolated so as to not allow additional water.
The reason for this would be to utilize the floor space where the existing expansion tank sits. This is a temporary (less than 6 months) scenario using a rental boiler while the building boilers are replaced.
Can the expansion tank be removed once the system is hot?
The reason for this would be to utilize the floor space where the existing expansion tank sits. This is a temporary (less than 6 months) scenario using a rental boiler while the building boilers are replaced.
Can the expansion tank be removed once the system is hot?
RE: Removing expansion tank after system is hot
However when the system cools down you will be drawing a vacuum / less than atmospheric pressure. Not all seals on valves etc are designed for negative pressure so gas could easily enter the system or you could collapse some of the equipment like the HX or any vessel that is connected to it. Even if it was perfect, air and water vapour can leak out creating gas bubbles gathering in high places once the system warms up again.
I hate the word "temporary" as it starts people going down tracks which they otherwise wouldn't and increase risk dramatically. The time something is in operation is simply not relevant to this sort of discussion.
So a wholly bad decision IMHO.
Remember - More details = better answers
Also: If you get a response it's polite to respond to it.
RE: Removing expansion tank after system is hot
...to the vapor pressure of water at your system temperature (e.g. ~1 psia @ 100F). Any pumps in the system will not be happy. Realistically you will probably just suck in air through joints or the air eliminator(s) and the system would no longer be liquid full.
RE: Removing expansion tank after system is hot
Do it properly or you will have endless issues and breakdowns with your system. IMHO.
Remember - More details = better answers
Also: If you get a response it's polite to respond to it.
RE: Removing expansion tank after system is hot
RE: Removing expansion tank after system is hot
Using NIST REFPROP for pure water, keeping density constant when going from 120F at 30 psig to 119F, a mere one degree F of cooling, gives you a pressure of about -13 psig. Similarly, one degree of heating gives you ~114 psig, etc.
Comparing 30 psig to 120 psig, 3x the pressure, it takes another one degree or so to start boiling:
RE: Removing expansion tank after system is hot
The volumes to be fair will be very small but at the high point it will be sub atmospheric, so depends on elevation of the system to know what pressure is at any point.
But it's the expansion that will be either very high pressure or constant dripping of the relief valve.
Remember - More details = better answers
Also: If you get a response it's polite to respond to it.
RE: Removing expansion tank after system is hot
Remember - More details = better answers
Also: If you get a response it's polite to respond to it.
RE: Removing expansion tank after system is hot
And there has to be a relief valve y each boiler anyway. If not, you soon will be in the expulsive business.
RE: Removing expansion tank after system is hot
I should though have referred to this valve as a pressure regulating valve which could be a spring type or a control valve type. And yes it would operate quite a lot which is why typically they are not used in this sort of scenario. But it's a lot better than what the OP was proposing.. .
Remember - More details = better answers
Also: If you get a response it's polite to respond to it.
RE: Removing expansion tank after system is hot
RE: Removing expansion tank after system is hot
RE: Removing expansion tank after system is hot
Remember - More details = better answers
Also: If you get a response it's polite to respond to it.
RE: Removing expansion tank after system is hot
RE: Removing expansion tank after system is hot
Where I live I would consult boiler code, IMC, and the local mechanical codes to begin with. I also would ask AHJ.
FWIW, I wouldn't do it, even if code allows it.
RE: Removing expansion tank after system is hot
RE: Removing expansion tank after system is hot
RE: Removing expansion tank after system is hot
it's just not that simple. I need to keep the air separator where it is for existing operation while I am piping up the temporary. I don't have a temporary air sep, so I would have to find a way to use the existing as the temporary also without taking the system down. Twice as many tees and valves to make it work.
RE: Removing expansion tank after system is hot
What is this system? All AHUs or some radiators or other places that would trap air and let you vent it?
We can't see your system so have no idea how complex it is.
Or just fit an air separator with a long bit of pipe on the top and fit a manual vent and bleed it every day?
Remember - More details = better answers
Also: If you get a response it's polite to respond to it.
RE: Removing expansion tank after system is hot
Both systems have rol-air-trols that are coming out and new ones installed. It is the temporary that concerns me. I am connecting to supply and return mains that leave the plant. I am providing temp pumps, boilers and chillers. But as of now, no one thought about the air separators and expansion tank that won't exist in the system once we switch to the rentals. So I guess I need to provide rental ones. Not sure if I can even get rental rol-air-trols. I'm sure I can get the expansion tanks.
RE: Removing expansion tank after system is hot
You really don't need anything fancy for your "temporary" system.
Remember - More details = better answers
Also: If you get a response it's polite to respond to it.
RE: Removing expansion tank after system is hot
Not sure what your sizes and pressures are like or if anyone is in a position to come at you about this but I am always wary of inadvertently making a "pressure vessel". With the air scoop type configuration I would be more comfortable arguing that its just a wide spot in the pipe meant to temporarily to lower the fluid velocity.
RE: Removing expansion tank after system is hot
The design includes a wider cross-section (for low velocity) some magical mesh inside to cause air to form bubbles, and are located at a low pressure/high temperature section of the system to facilitate air to become bubbles. Main reason is to remove oxygen.
An air vent just releases the air that collects at a high point. An air -separator typically has an air-vent as well. But you also have them in the piping system (at top) to let air out that collects. They don't actively dissolve air. Main function is to remove air that already is a gas, so the water can flow. There are auto-vents. You don't have to bleed them manually. In normal sealed systems we close the air-vent off with a valve after a time of operation to avoid any potential leaks. They should be opened up for a few days seasonally. In a system that constantly brings in new water (and oxygen), you need to constantly remove air.
RE: Removing expansion tank after system is hot
It's better than nothing and at that size with flow going through it doesn't become a PV IMHO, but I know others might not think that way.
Remember - More details = better answers
Also: If you get a response it's polite to respond to it.
RE: Removing expansion tank after system is hot
Your 6-month "temporary" setup includes seasonal changes that may impact usage of the system substantially, I'd be very hesitant to agree to "temporary" accommodations without seeing a year or two of thermal data to ensure with high confidence you'll only be seeing a small temperature change during the entire duration (and an additional 6 months of buffer time for project delays).
The safer bet vs. removing the tank would be to check that expected temperature change and size a tank at the absolute minimal to account for your corresponding volume change. You might be able to get by with a tank small enough to fit, and cheap enough to not run up the budget, which will avoid all of the issues presented in discussion already.
If you're taking sections of pipe offline for rework and putting them back into service an air separator should not be removed. The only way you'll get away with no air separator is if you can guarantee no leaks, no low pressure events, and no service valves being opened for the duration of the "temporary" work to ensure you're not introducing large amount of air into the system.
And I keep writing "temporary" in quotes because temporary solutions that work have a bad habit of being left in place, or worse, becoming normal practice.
RE: Removing expansion tank after system is hot
For a permanent system I wouldn't cheap out on air/dirt removal. For this system, where someone talks about not even using an expansion tank, i wouldn't spend any money.
But you are right, those "temporary" solutions can be in for decades. which is why JHA likely treats them the same way as permanent systems.
RE: Removing expansion tank after system is hot
RE: Removing expansion tank after system is hot
That's what they ALL say.
10 years later.....
Remember - More details = better answers
Also: If you get a response it's polite to respond to it.
RE: Removing expansion tank after system is hot
RE: Removing expansion tank after system is hot
RE: Removing expansion tank after system is hot
One second, one minute, one hour, one day, one month, one year, one decade IT DOESN'T MATTER. Design it like it is going to be there for ever and very little will go wrong. IMHO.
Remember - More details = better answers
Also: If you get a response it's polite to respond to it.
RE: Removing expansion tank after system is hot
The expansion tank should not be ignored, even if you need a temporary location. If the system stays hot the whole time, all good. If the system cools down, might be good too. If make-up water is connected, and there is no expansion tank, just don’t heat the system back up again.