Relief Valve Location
2

Relief Valve Location

Relief Valve Location

(OP)
Hey All,

I am looking to see if someone can help me with this, is there a code section that deals with the location/placement of a PSV/PRV Pressure Safety/Relief Valve.

Meaning, that the valve should be affixed directly to piping or a pressure vessel, and the discharge should be piped through the roof or 6" above finished floor.

Mainly looking at it from a safety aspect, where there are PSVs that are on a tank or piping at eye level with nothing piped to the floor or through the roof protecting people that might be present in a mechanical space if the relief was to activate and discharge.

Thanks in advance,

RE: Relief Valve Location

2
Might be worth your while reviewing the recommendations in API-STD-520 Part II - Installation.

Note there is a separate forum for safety relief valves.


*** Per ISO-4126, the generic term
'Safety Valve' is used regardless of application or design ***

*** 'Pressure-relief Valve' is the equivalent ASME/API term ***

RE: Relief Valve Location

In general the codes are not prescriptive in these as there are too many options, fluids and local restrictions.

What they do is specify performance requirements. SO in inlet terms there is a maximum pressure loss from the vessel or piping to the inlet of the valve which I believe is 3% of the set pressure. That often means very close / direct mounting.

Where the exhaust / vent goes is a safety issue both for venting to a "safe location" as the P&IDs say and avoiding jetting out their fluid where people might be present. This is part of the safety / hazard review as it is so individual to the location that it can't be prescribed by the code.

Remember - More details = better answers
Also: If you get a response it's polite to respond to it.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login



News


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close