Hi All,
Performing a relatively "routine" check of an open discharge for a steam PSV, and we have come to an unexpected result.
Some problem information:
Saturated steam operating at 12psig; relief valve is set to 15psig. PSV capacity is ~5500lb/hr. Discharge elbow is NPS 4, sch.40.
Using the equation II-2.2.1 (a) (1) yields P1=4.34psia. "a" and "b" values that were used are for 15psia < P1 < 1,000psia.
Are the calculations in this code section not applicable due to this low P1? How should we proceed with calculating the maximum open discharge vent pipe? The contractor is suggesting a discharge pipe routing that has a number of elbows and there is no direct path through a wall or roof.
We have used App.II methods routinely in past projects, but usually with PSV setpoints around 100psi, so this low pressure issue has not come up before.
Any suggestions are welcome.
Thanks.
Performing a relatively "routine" check of an open discharge for a steam PSV, and we have come to an unexpected result.
Some problem information:
Saturated steam operating at 12psig; relief valve is set to 15psig. PSV capacity is ~5500lb/hr. Discharge elbow is NPS 4, sch.40.
Using the equation II-2.2.1 (a) (1) yields P1=4.34psia. "a" and "b" values that were used are for 15psia < P1 < 1,000psia.
Are the calculations in this code section not applicable due to this low P1? How should we proceed with calculating the maximum open discharge vent pipe? The contractor is suggesting a discharge pipe routing that has a number of elbows and there is no direct path through a wall or roof.
We have used App.II methods routinely in past projects, but usually with PSV setpoints around 100psi, so this low pressure issue has not come up before.
Any suggestions are welcome.
Thanks.