Is Isolated Barrier Necessary for Equipment with Intrinsic Safety Certification Ex e ib mb I IC T6 G

Is Isolated Barrier Necessary for Equipment with Intrinsic Safety Certification Ex e ib mb I IC T6 G

Is Isolated Barrier Necessary for Equipment with Intrinsic Safety Certification Ex e ib mb I IC T6 G

(OP)
The equipment holds the certification Ex e ib mb I IC T6 Gb, where "ib" signifies intrinsic safety. This certification confirms that the equipment is specifically engineered to restrict electrical energy, prevent the occurrence of sparks, and minimize excessive heat that could potentially ignite an explosive environment. Given this "ib" certification, is it accurate to state that isolated barriers are not necessary since the equipment already meets the required safety standards?
Replies continue below

Recommended for you

RE: Is Isolated Barrier Necessary for Equipment with Intrinsic Safety Certification Ex e ib mb I IC T6 G

The instructions for this device will include a "certification Drawing" which will explain if barriers are needed, if there is a circuit length limit, and possible other certification constraints.

Quote (John668)

Given this "ib" certification, is it accurate to state that isolated barriers are not necessary since the equipment already meets the required safety standards?
is an incorrect statement. If the Certification Drawing requires a barrier, then one is required,

RE: Is Isolated Barrier Necessary for Equipment with Intrinsic Safety Certification Ex e ib mb I IC T6 G

If by isolated barrier you mean conduit seals or cable seals, these may be required to prevent the migration of gas outside the explosive zone.

--------------------
Ohm's law
Not just a good idea;
It's the LAW!

RE: Is Isolated Barrier Necessary for Equipment with Intrinsic Safety Certification Ex e ib mb I IC T6 G

Looks like a picture is needed. I have attached a copy of a certification book for a device that is listed under FM, UL, and CE rules as appropriate to use in intrinsically safe (Limited Energy) circuits .

The requirement for ITL type certified conduit seals or cable glands applies, but is not part of the intrinsic safety section (504) of the national electric code.
Similar diagrams apply for equipment type certified for application under ATEX Directives.

RE: Is Isolated Barrier Necessary for Equipment with Intrinsic Safety Certification Ex e ib mb I IC T6 G

If that is the control diagram for the instrument you are using, you are required to make the installation in accordance with that diagram. 504.10(A).
If that is not the diagram for your instrument, you need the one for the instrument being installed. Remember it is not only the field instrument that could ignite a flammable gas, it is also the possibility of power on the circuit that connects to the field instrument.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login



News


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close