Is Isolated Barrier Necessary for Equipment with Intrinsic Safety Certification Ex e ib mb I IC T6 G
Is Isolated Barrier Necessary for Equipment with Intrinsic Safety Certification Ex e ib mb I IC T6 G
(OP)
The equipment holds the certification Ex e ib mb I IC T6 Gb, where "ib" signifies intrinsic safety. This certification confirms that the equipment is specifically engineered to restrict electrical energy, prevent the occurrence of sparks, and minimize excessive heat that could potentially ignite an explosive environment. Given this "ib" certification, is it accurate to state that isolated barriers are not necessary since the equipment already meets the required safety standards?
RE: Is Isolated Barrier Necessary for Equipment with Intrinsic Safety Certification Ex e ib mb I IC T6 G
is an incorrect statement. If the Certification Drawing requires a barrier, then one is required,
RE: Is Isolated Barrier Necessary for Equipment with Intrinsic Safety Certification Ex e ib mb I IC T6 G
--------------------
Ohm's law
Not just a good idea;
It's the LAW!
RE: Is Isolated Barrier Necessary for Equipment with Intrinsic Safety Certification Ex e ib mb I IC T6 G
The requirement for ITL type certified conduit seals or cable glands applies, but is not part of the intrinsic safety section (504) of the national electric code.
Similar diagrams apply for equipment type certified for application under ATEX Directives.
RE: Is Isolated Barrier Necessary for Equipment with Intrinsic Safety Certification Ex e ib mb I IC T6 G
If that is not the diagram for your instrument, you need the one for the instrument being installed. Remember it is not only the field instrument that could ignite a flammable gas, it is also the possibility of power on the circuit that connects to the field instrument.