what is the meaning gross power output at generator terminal of GTG

RE: Hello everyone, please help me

Gross output power is the total electric power generated at the terminal of the electric generator. But not all of this power generated is transmitted to the grid. Some of the power are used for auxiliaries such as air conditioning, fans, pumps, lighting etc, all to keep the electric generator running efficiently. Net electrical power transmitted is the gross power generated minus the power consumed by these auxiliaries. I hope this helps.

RE: Hello everyone, please help me

Gross power output is the power as measured with a Wattmeter at the generator output terminal sand includes the auxiliaries mentioned by Ethan, but not accessories directly driven by the engine.
eg: excluding Engine fan, Engine water pump, battery charging alternator, etc.

--------------------
Ohm's law
Not just a good idea;
It's the LAW!

RE: Hello everyone, please help me

Gross power is the total power generated by the generator, including auxiliary power. The auxiliary power may be 8 to 10 % of the gross power. Therefore, we get net power less than the gross power.

Net power= Gross power - Auxilary power

RE: Hello everyone, please help me

waross wrote:

Quote:

Gross power output is the power as measured with a Wattmeter at the generator output terminal sand includes the auxiliaries mentioned by Ethan, but not accessories directly driven by the engine.
eg: excluding Engine fan, Engine water pump, battery charging alternator, etc.

To build on what Bill wrote: Or, for other prime movers, any such mechanical loads including shaft-driven lubricating or governor oil pumps, circulating blowers/fans for hydrogen-cooled alternator, the minimal but very essential load of any hydraulic governing system itself, if any; numerous other possible direct mechanical loads are possible, none of which will be measured at the alternator/generator output terminals.

CR

"As iron sharpens iron, so one person sharpens another." [Proverbs 27:17, NIV]

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login



News


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close