wcaseyharman
- Oct 31, 2022
- 330
We had event on one of our thermal generating units where it appears an SCR went into lockup (latchup). The equipment is a 1982 vintage GE 7E gas turbine (74MW) with a GE 7A4 generator (13.8kV, 94MVA). The bridge is an original GE busfed half-controlled bridge with a Basler DECS400 front end upgrade applied in 2010. PPT secondary is 480V.
The event occurred several seconds after a transmission fault on the 115kV system about 30 miles away. The unit responded to the event, but the bridge appeared to get stuck - the control command went to full negative (-10V, minimum field voltage) but the field voltage stopped at 325V for 10 seconds. The field current rose accordingly and the unit tripped off on generator overvoltage. I calculated the field voltage for a 1 SCR lockup would be and I get 324V.
Has anyone else encountered SCR lockup? If so, what caused it and how did you fix it?
Thanks in advance!
Thanks in advance!