I have a system similar to the one in the image above. It's a two stage mechanical refrigeration unit with a flash economizer, using propane as a refrigerant to cool a process stream. The compressor is a screw compressor, so positive displacement.
If I'm understanding this system correctly, the expansion valve at the chiller inlet would only change the vapor-liquid ratio in the chiller and 1st stage compressor section. As long as the compressor is capable of dealing with the amount of vapor that is formed in that particular section, the pressure should stay within normal operating range. Am I understanding correctly?
RE: Pressure Control in two-stage refrigeration system
RE: Pressure Control in two-stage refrigeration system
But the 2nd stage discharge pressure would still be limited by whatever the accumulator temperature since it can't exceed the vapor pressure corresponding to that temperature?
RE: Pressure Control in two-stage refrigeration system
RE: Pressure Control in two-stage refrigeration system
So hypothetically, what would happen if the outlet pressure from stage 2 is pushed based the vapor pressure? Would the vapor simply condense? Would the outlet temperature from the condenser simply increase to match the new discharge pressure?
I imagine it's hard to fully answer this question without knowing the specific control logic of the system.
RE: Pressure Control in two-stage refrigeration system
RE: Pressure Control in two-stage refrigeration system
Do you know where i can find an SOP for an industrial refrigeration process? I found documents online that describe the system but I really want to learn more about the controls and how engineers change the various process variables.