VSD Current and Voltage Input Measurement
VSD Current and Voltage Input Measurement
(OP)
Hi,
I tried to measure the current and voltage of an induction motor driven by a VSD. The measurement was taken at the input of the VSD, and the results are as follows:
Voltage:
Current:
The waveforms are heavily distorted, especially the current waveform. Is this normal? Could it be caused by harmonic distortion? Note that the voltage waveform also appears distorted even when the motor is not running.
Thanks,
Angga
I tried to measure the current and voltage of an induction motor driven by a VSD. The measurement was taken at the input of the VSD, and the results are as follows:
Voltage:
Current:
The waveforms are heavily distorted, especially the current waveform. Is this normal? Could it be caused by harmonic distortion? Note that the voltage waveform also appears distorted even when the motor is not running.
Thanks,
Angga
RE: VSD Current and Voltage Input Measurement
I’ll see your silver lining and raise you two black clouds. - Protection Operations
RE: VSD Current and Voltage Input Measurement
As to why there might be input harmonics on the voltage waveform when the motor is not turning - it depends on the drive setting. Is it truly OFF - or are you set to ZERO SPEED? For example, at zero speed, the current is fluctuating to hold the rotor in position.
Converting energy to motion for more than half a century
RE: VSD Current and Voltage Input Measurement
The trapezoidal voltage waveform looks quite strange since voltage distortion values are usually fairly small. Is the supply coming from a utility source?
RE: VSD Current and Voltage Input Measurement
The voltage waveform could be distorted if there are other polluting VFDs or soft-starters in your supply.
ACW
RE: VSD Current and Voltage Input Measurement
--------------------
Ohm's law
Not just a good idea;
It's the LAW!
RE: VSD Current and Voltage Input Measurement
In response to your questions:
Yes, the distorted voltage is not when the VSD is truly off, but when the motor is set at zero speed. Please see below the voltage waveform at the moment when the VSD switch is turned on:
The supply is not from the big power grid, but we have an isolated power grid consisting of around 12 GTGs.
Zlatkodo,
Yes, it does have a soft starter, but it is not shown on the drawing above. The transformer schematic is like this:
Could you please explain how exactly the soft starter distorts the voltage waveform?
RE: VSD Current and Voltage Input Measurement
I’ll see your silver lining and raise you two black clouds. - Protection Operations
RE: VSD Current and Voltage Input Measurement
We have checked the VSD's cooling fan unit and other items according to the manual, but we could not find any problems with the VSD.
Therefore, we tried to measure the voltage and current to observe any fluctuations that might occur. Unfortunately, the waveform during the trip was not captured by the Power Quality Analyzer, and both the VSD and motor control relay do not have the ability to generate COMTRADE files.
The question is, is it possible that this distorted voltage is causing the IGBT high temp trip?
RE: VSD Current and Voltage Input Measurement
I’ll see your silver lining and raise you two black clouds. - Protection Operations
RE: VSD Current and Voltage Input Measurement
What is nominal VSD current value? Is a constant or variable load? Open loop or control loop (what kind of control loop)?
What motor type and nominal power/current/speed?
Ambient temperature, VSD input voltage, output current, IGBT temperature, motor speed before trip?
Such distorstion are somehow "normal" for any device with standard rectifier (diode + capacitor).
Most probable voltage grid is much below nominal value (but above undervoltage trip), VSD output voltage is below nominal (maybe application request motor at full speed / full load or near), so motor request more current, so IGBTs currents are higher too (maybe close to overload settings).
Higher IGBTs current mean higher losses and for same ambient temperature and cooling conditions lead to higher heatsink temperature.
RE: VSD Current and Voltage Input Measurement
The “camel hump” current distortion waveform is absolutely classic for a 6 pulse VFD, or any other non-linear diode bridge rectifier based power device. The flat topping of your voltage waveform is indicative of a weak power source feeding a non-linear load. The diode bridge charges the DC bus by drawing current only at the peaks of each sine wave. After the initial power up sequence in which there is a current limiting system to pre-charge the DC bus softly, the capacitors on the bus will attempt to pull power from the source at the available fault current. In a locally generated system, that can affect the AVR to cause flat topping of the voltage waveform. A line reactor ahead of the VFD is one way to help mitigate this effect because it slows the rise time of the current pulses going into the bus. You also likely do not have a DC bus choke on that drive either, that would help too. Both in concert is the best.
" We are all here on earth to help others; what on earth the others are here for I don't know." -- W. H. Auden
RE: VSD Current and Voltage Input Measurement
The VSD was able to record some parameters with a sampling time of 5 minutes. Below is the trend prior to the IGBT over-temp trip. The trend for the events is quite similar. From the trend, it seems like the voltage was constant (referring to the DC bus voltage):
The load is an ESP oil pump, which I think can be considered a variable load. The motor's FLA is 82 A at 60 Hz. The control is an enhanced V/f closed-loop control. The VSD rating is 440 kVA (3 PH, 1400-2500 V, 105 A).
The soft start reactor is the old control, VSD unit was added later
Note:
The speed was kept at 52/53 Hz because the motor current rose up to 90 A when we tried to increase the frequency to 60 Hz
RE: VSD Current and Voltage Input Measurement
" We are all here on earth to help others; what on earth the others are here for I don't know." -- W. H. Auden
RE: VSD Current and Voltage Input Measurement
The use of VSDs is actually relatively new in our field, and harmonics have never been a concern, so there are no company regulations regulating VSDs and the harmonics generated by loads, especially VSDs.
What standards can we use as a reference for regulating the harmonics on an isolated power grid?
RE: VSD Current and Voltage Input Measurement
" We are all here on earth to help others; what on earth the others are here for I don't know." -- W. H. Auden
RE: VSD Current and Voltage Input Measurement
I’ll see your silver lining and raise you two black clouds. - Protection Operations
RE: VSD Current and Voltage Input Measurement
" We are all here on earth to help others; what on earth the others are here for I don't know." -- W. H. Auden
RE: VSD Current and Voltage Input Measurement
VSD current is much below nominal so temp trip reason may be excesive ambient temp, insufficient cooling, too high VSD switching frequency, IGBT snubbers damage or important harmonics in IGBT - motor circuit.
These tripping arised suddenly or more and more frequently?
What length is VSD-motor cable and what is VSD switching frequency set?
RE: VSD Current and Voltage Input Measurement
This VSD unit was installed only at the end of last year and has never been run for a long time. The problems varied. Initially, there was a high running ampere as previously described ("the speed was kept at 52/53 Hz because the motor current rose up to 90 A when we tried to increase the frequency to 60 Hz"), and lastly, the problem was the repetitive IGBT hot temperature issue.
The problem of high motor current even though the frequency has not reached 60 Hz has not been resolved yet.
What can be analyzed from this incident?
We suspected that there was a motor voltage supply mismatch. Some important notes regarding voltage are:
- Motor nameplate voltage is 2736 V.
- SVC (surface voltage calculation), motor voltage + voltage drop = 2813 V.
- VSD voltage rating is 2600 V.
- Because the VSD voltage rating is only a maximum of 2600 V, the VSD supplier recommended that the transformer voltage supplying the VSD be set around 2700 V.
The cable length from the VSD unit to the motor is 3413 ft, and the VSD switching frequency is 1.6 kHz.RE: VSD Current and Voltage Input Measurement
Motor have not enough voltage/torque,so when you try 60Hz VSD output, motor current increase above nominal and can't reach desired speed.
At about 1km cable there are problems with capacitive currents, voltage increase and dv/dt that may affect motor isolation and create VSD overstress; need to add output reactors and maybe output filters.
What's values for motor base frequency and motor voltage parameters in VSD?
RE: VSD Current and Voltage Input Measurement
You appear to be running on the ragged edge of full load motor current.
A higher voltage would help lower the current at a given Hz.
I don't see mention of an output filter. Did I miss something?
A quick google search on "VFD cable lengths" indicates that filters are recommended for lengths exceeding 80 to 100 FT, depending on the site.
In some SAGD pads that I visited, they used one of two different mitigation techniques.
Some pads used 4160 Volt VFDs and a large filter adjacent to the VFD.
Other pads used a 4160 Volt VFD and a 4160/600 Volt transformer to run 600 Volt submersible motors.
Our work consisted in inspecting and bringing the grounding up to code minimums.
Despite my interest, I was unable to gather any information comparing the relative effectiveness, efficiency and cost of the two mitigation methods.
What is the nominal head that your ESP is pumping into? What is the maximum difference in discharge head, relative to the nominal head.
Valving from a full tank to an empty tank may increase the dynamic head and the motor current. This may happen faster than your PID control can stabilize, causing an overload, heat related trip.
Any surface condition that reduces the dynamic head may cause an over load.
--------------------