LRG Vs Solid Grounded system
(OP)
I hear my colleague saying Low resistance grounding is selected only because where High resistance system cannot be used (charging current 3Ic is >10A) and there is no great advantage of using it, rather use solid grounded system.
Any comments!
I believe it also provides easy ground fault relaying and lower Arc flash hazard exposure.
Any comments!
I believe it also provides easy ground fault relaying and lower Arc flash hazard exposure.
RE: LRG Vs Solid Grounded system
Low-resistance grounding at medium voltage allows for selective coordination of ground fault while still greatly limiting ground fault damage compared to solid-grounding.
High-resistance grounding further limits ground fault damage, but it is difficult to coordinate - so when a ground fault is detected the entire system is generally shut down. On HRG systems, ground faults are normally detected based on the voltage instead of current. It works well for limited systems such a generators with a unit step-up transformer. It's less common in industrial systems with extensive medium-voltage distribution. Hybrid sytsems are sometimes used whereby grounding is switched between high and low resistance grounding depending on the fault location.
Dave
RE: LRG Vs Solid Grounded system
It is popular to limit the earth fault currents to around 300A and this is to limit the possibility of damage to the iron core laminations in motors when the fault happens to be in the stator winding slots.
It is an economical and practical possibility to rewind a motor affected by winding fault but the core damage means expensive repair or rebuilding of core.
IEEE Red book has good discussion on the earthing options for MV systems.
RE: LRG Vs Solid Grounded system
Regards.
System earthings in LV
https://www.se.com/au/en/download/document/ECT172/
Earthing systems worldwide and evolutions
https://www.se.com/au/en/download/document/ECT173/