(OP)
Ok, be gracious with me. I am an SE on this site but have an HVAC question. I built a new house (one story ranch on a crawlspace) and the HVAC contractor installed a 15 SEER American Standard unit. As it was a perfectly straight shot from the outdoor unit thru the crawlspace to the air handler in the mechanical closet, the contractor used ½”ø rigid copper for one of the lines. Seemed like a good idea. However, when the unit runs I hear a vibration in the house and outside. It is kind of a beating vibration like “wah, wah, wah” I can’t imagine a unit leaving the factory with a vibration. I am figuring that the rigid line is causing this. They have been back a few times to add isolators etc. and it remains. I had this same unit at my old house and it was pretty damn quiet. Does anyone have any further insight about this?

Thanks
Replies continue below

Recommended for you

RE: HVAC Vibration

How is the pipe supported? Added isolators where?

It is possible for units to leave the factory with issues. I had a unit with some electrical issues, and the technician found that the wiring was backwards. He looked up data on its manufacturing, and it was wired at 3:30 PM on a Friday afternoon.

RE: HVAC Vibration

Run evaporator blower by itself. Hear the noise?

Run condenser fan by itself. Hear the noise?

RE: HVAC Vibration

These can be difficult to isolate.

The main noise producing element is the compressor. The internal dampers my be damaged or the resilient feet on the main unit are not installed correctly.

If the hard pipe is connected directly to the main unit with no flexible piping involved then that is a major source of vibration transmission.

Pictures help a LOT

Remember - More details = better answers
Also: If you get a response it's polite to respond to it.

RE: HVAC Vibration

(OP)
Yes, that is the unit - silver Series.
It is def. the outdoor unit. Running the AH by itself is pretty silent.
I'm having another company come by next week to get a second opinion and a fresh set of eyes on it.
I still think it is the rigid pipe causing it. I'll check back when I hear something.

Thanks

RE: HVAC Vibration

If it's audible outside as well it is more likely to be the main unit or something inside it is not properly damped or the rubber bushes have been damaged.

Also check the fan clearance or louvres for any signs of damage or foreign object (mouse?)

Remember - More details = better answers
Also: If you get a response it's polite to respond to it.

RE: HVAC Vibration

(OP)
Thanks. Def. not any fan interference.

RE: HVAC Vibration

How long is this copper pipe? There may be issues with it contracting ( I assume it's the chilled water supply line) and imposing force on the connection and hence forces going into the unit it wasn't designed for? Some level of flexibility is needed to avoid this.

Remember - More details = better answers
Also: If you get a response it's polite to respond to it.

RE: HVAC Vibration

(OP)
It is residential so it is a freon line. It has a an elbow in it going up thru the floor to the air handler which should absorb that stress

RE: HVAC Vibration

Go to the discharge end of the capillary tube and note for any undue noise by touch or hearing. A stethoscope may help if by hearing.

RE: HVAC Vibration

(OP)
Update:

Had another technician come out. He thinks the compressor is out of spec. It is pulling too many amps. The charge is ok. They are going to investigate further.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login



News


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close