2018 IMC - Historic Building Fire/Smoke Dampers
2018 IMC - Historic Building Fire/Smoke Dampers
(OP)
I am designing a VRF system for a historic 3 story courthouse early 1900s and adding energy recovery ventilators to provide dedicated OA. The building is old and does not have life safety drawings or a fire alarm/sprinkler system. Most interior partitions is masonry.
Is a life safety analysis required to identify wall ratings for fire or smoke dampers in the ventilation system ducts? Is there some kind of exception for older buildings like this?
Is a life safety analysis required to identify wall ratings for fire or smoke dampers in the ventilation system ducts? Is there some kind of exception for older buildings like this?
RE: 2018 IMC - Historic Building Fire/Smoke Dampers
RE: 2018 IMC - Historic Building Fire/Smoke Dampers
Are you stamping the final plans? if so, it is you who is on the hook. If you are sub to an architect, they are to find out and stamp whatever they determine.
Talk to JHA. We don't know if you are in Singapore, or Canada.
Unrelated to fire, you should add a cooling coil to ventilation air for dehumidification. Unless you are in arid climate.