Required airflow and the fan & filter combination for the starter cells in MCC.
Required airflow and the fan & filter combination for the starter cells in MCC.
(OP)
Hello everyone,
I am designing MCC. I need to calculate air flow and the fan & filter combination to achieve this for the starter cells.
For information.
• Attached excel sheet gives part numbers for soft starters and contactors
• This MCC is in an A/C controlled room.
• The external ambient temperature is 40ºC.
• Cell with CR01 will most likely have an auto transformer in it so we can add the watts lost at a later stage for that one.
The cells that need this cooling requirement are the following with the * symbol.
Could someone please guide me how can I calculate it?
Your help will be much appreciated.
Thanks
I am designing MCC. I need to calculate air flow and the fan & filter combination to achieve this for the starter cells.
For information.
• Attached excel sheet gives part numbers for soft starters and contactors
• This MCC is in an A/C controlled room.
• The external ambient temperature is 40ºC.
• Cell with CR01 will most likely have an auto transformer in it so we can add the watts lost at a later stage for that one.
The cells that need this cooling requirement are the following with the * symbol.
Could someone please guide me how can I calculate it?
Your help will be much appreciated.
Thanks
RE: Required airflow and the fan & filter combination for the starter cells in MCC.
electrical enclosure air conditioner
RE: Required airflow and the fan & filter combination for the starter cells in MCC.
I did research on it. The thing that I am not able to understand is, how to calculate heat dissipation and internal temperature.
For example, in the CR01 section, we currently have only 1 400Amp mccb( LV432693 OR C40N32D400), with Full load current = 309.5.
How can I calculate heat dissipation for this?
RE: Required airflow and the fan & filter combination for the starter cells in MCC.
As both mccb are Circuit Breaker , it almost do not dissipate heat, except from the electronic circuit , if they have, that shall be a small heat amount.
You can ask to the 1 400Amp mccb( LV432693 OR C40N32D400) vendor for it.
RE: Required airflow and the fan & filter combination for the starter cells in MCC.
Heat gain is from outside air temp + solar heat gain + internal heat gain.
Heat loss = heat conducted through walls and roof (assuming internal temp. is > outside temp)
Set up your equation with internal temp. as the unknown. Simple algebra.
RE: Required airflow and the fan & filter combination for the starter cells in MCC.
Heat loads for electrical equipment are usually provided by the manufacturer of the electical equipment devices or if not there are industry recommendation guidelines that provide estimated loads for an specific electric device.
RE: Required airflow and the fan & filter combination for the starter cells in MCC.
External ambient temperature is 40 degrees
Power dissipation of electrical component (Circuit breaker) is 57.6 watts
Dimensions of the enclosure (1827mm, 560mm, 600mm)
Can someone please guide me if there is an equation to calculate max internal temperature inside the enclosure, or how can we do that?
Best Regards,
RE: Required airflow and the fan & filter combination for the starter cells in MCC.
so it shall be about 25 C degree .
So the 57.6 watts will be dissipated by the enclosure steel walls with almost no temperature increase.
The 40 degree is the external ambient temperature outside the building , the A/C will take charge controlling the INTERNAL ambient temperature.
RE: Required airflow and the fan & filter combination for the starter cells in MCC.
RE: Required airflow and the fan & filter combination for the starter cells in MCC.
The actual temperature inside the enclosure can be determind simplistically by a straight heat transfer equation
Q = h(A)(dT)
Q is internal heat dissipation of electrical components in cabinet
A = surface area of cabinet
h = overall heat transfer coeficient (inside air film + metal panel + outside air film)
dT = resulting temperature difference at Q
RE: Required airflow and the fan & filter combination for the starter cells in MCC.
thread391-489365: Electrical Enclosure Heating Calculations
thread248-340558: how to calculate hvac capacity in a cabinet in an easy way??