Temporary Cofferdam design - What FOS should I use?
Temporary Cofferdam design - What FOS should I use?
(OP)
Hi all. I am working on a cofferdam design. Since this is a temporary structure, I am wondering if I can use FOS=1 for soil analysis as well as structural design? Thanks.
RE: Temporary Cofferdam design - What FOS should I use?
RE: Temporary Cofferdam design - What FOS should I use?
You may find something of use in the old USACE manual: https://www.publications.usace.army.mil/Portals/76...
RE: Temporary Cofferdam design - What FOS should I use?
RE: Temporary Cofferdam design - What FOS should I use?
RE: Temporary Cofferdam design - What FOS should I use?
For Sheetpiling cofferdams ( failure mode is shear ) F.S = 1.2 to 1.6 suggested ( Foundation Engineering by Bowles ).
IMO, F.S.=1.2 should be adopted for temporary cofferdam design .
Tim was so learned that he could name a
horse in nine languages: so ignorant that he bought a cow to ride on.
(BENJAMIN FRANKLIN )
RE: Temporary Cofferdam design - What FOS should I use?
The following applies for a "cofferdam".
See DRC1's comments on Cofferdam Factor of Safety.
Specifically: "Designing cofferdams is considerably different than typical structural or foundation engineering, and is based on considerable part on experience, contractors construction methods, and local conditions."
Also, my comment: "The shape, size, and connection details of a cofferdam are more important than a large safety factor for sizing the structural members."
RE: Temporary Cofferdam design - What FOS should I use?
www.PeirceEngineering.com
RE: Temporary Cofferdam design - What FOS should I use?
Thanks for your input. After speaking to a local geotech expert and the software designer, I will be doing the following.
FOS 1.2 for materials
FOS 1.2 for earth pressure (active side)
FOS 1.2 for moment, shear and prop forces
I am pretty much covering all angles here when it comes to FOS so I think I am on the safe side unless I have missed something.
The cofferdam is on land. But water table is high. I have taken this into consideration. The soft clay property has much to be desired but calculation showed base heave to be within spec.
Since this is a temporary design I am using total stress analysis. I have been advised to do an effective stress analysis which I have done and the forces look to be less than short term analysis.
So I am using the forces from total stress analysis for my structure design.
RE: Temporary Cofferdam design - What FOS should I use?
I also don't think its in anyone's benefit to skin this to its bones.
RE: Temporary Cofferdam design - What FOS should I use?
RE: Temporary Cofferdam design - What FOS should I use?
I would not rely on any improvement from that. You said there is a layer of soft CLAY at the base, likely no improvement at all in that layer.
If anything, there could be less passive resistance if anything. You will drive piles in CLAY and temporarily increase the pore pressure which will reduce your strength in the short term.
RE: Temporary Cofferdam design - What FOS should I use?
-----*****-----
So strange to see the singularity approaching while the entire planet is rapidly turning into a hellscape. -John Coates
-Dik
RE: Temporary Cofferdam design - What FOS should I use?
I have another alternative. Would doing the sinking method using sheet pile cofferdam as a guide be a better solution?
RE: Temporary Cofferdam design - What FOS should I use?
They can tell you if they've encountered your issue before and likely give you some preliminary guidance.
RE: Temporary Cofferdam design - What FOS should I use?
RE: Temporary Cofferdam design - What FOS should I use?
RE: Temporary Cofferdam design - What FOS should I use?
RE: Temporary Cofferdam design - What FOS should I use?
It seems to me like most of the above responders are talking about using a high safety factor(s) but no one except you defines the safety factor(s). Read various books and design manuals on retaining wall and sheeting design. If you are doing allowable stress design (with unfactored service loads and safety factors), The materials' allowable stresses will already have built-in safety factors. Generally, the only safety factor you would need to apply is one for the passive pressure during design or you use full passive resistance and just increase your calculated pile embedment to provide a safety factor on the passive resistance. If you start compounding safety factors (i.e., putting safety factors on materials, loads, and soil properties), you will have a safe but very expensive cofferdam.
www.PeirceEngineering.com
RE: Temporary Cofferdam design - What FOS should I use?
Has this contractor constructed a similar project in the past?
You have not mentioned the depth, but below, say, 9 meters, cofferdams can be really tricky.
IMHO, from the info posted, the best option is for a full depth (from top of ground) braced cofferdam.
Not a (potentially unstable) circular cofferdam.
RE: Temporary Cofferdam design - What FOS should I use?
RE: Temporary Cofferdam design - What FOS should I use?
Also circular has what I consider a glaring flaw in some circumstances. To be truly stable the external pressure needs to be uniform all around the circumference. No problem with this issue in water. Not too much problem with this on land. Use circular on the waterfront, like for a water intake structure, with part of the circle resisting only water pressure and the remainder resisting both water and soil pressure... a disaster waiting to happen, even it can be successfully dewatered.
At one of our generating stations we had an experienced Contractor who was "blinded" by the prospect of using less sheeting and having unobstructed interior space for circular compared to rectangular braced. This was for a water intake, half on land, half in the water. I tried to talk him out of it. Anyway, he tried and failed several times to construct circular... finally did the right thing (for this situation) and used braced rectangular, with no problems.