Single phasing delta Y transformers
Single phasing delta Y transformers
(OP)
This is at a wind farm site where the cables are underground going to multiple padmounts connected in parallel, standard setup. The main power transformer is Wye connected on the 34.5kV side. The collector string is connected delta-Wye. We had a padmount nearest to the substation (connected delta-wye) where the internal jumpers on A and B phase failed. Now we have a padmount with normal voltages, and the rest (about 8-10?) have only one phase connected (20kV to ground, 34.5kV nominal). When we energized (not knowing the internal jumpers had failed, that took a while to figure out) we had currents of (A/B/C/G)17/17/38/22 amps. The arrestors started failing on A and B phase and were replaced. We found the faulted padmount, have isolated that.
When we energized we blew more arrestors. They didn't really cause any issues, but the ground lead would pop off. The initial fault caused one phase of the substation breaker to fail, all the porcelain cracked, we caught that before it failed catastrophically. (the breaker bushing failure has nothing to do with the issue, was just an noted item, it was cracked before and the magnetic forces (6kA) caused the damage, but interesting)
It makes intuitive sense to me that they were over voltaged though the padmount, but I'm not sure the path. If only 1 phase is energized I don't see the path to over voltage the other phases.
Could you give me your take on why the arrestors saw over voltage?
When we energized we blew more arrestors. They didn't really cause any issues, but the ground lead would pop off. The initial fault caused one phase of the substation breaker to fail, all the porcelain cracked, we caught that before it failed catastrophically. (the breaker bushing failure has nothing to do with the issue, was just an noted item, it was cracked before and the magnetic forces (6kA) caused the damage, but interesting)
It makes intuitive sense to me that they were over voltaged though the padmount, but I'm not sure the path. If only 1 phase is energized I don't see the path to over voltage the other phases.
Could you give me your take on why the arrestors saw over voltage?
RE: Single phasing delta Y transformers
RE: Single phasing delta Y transformers
The jumpers are internal to the padmount, just dead front externally. I don't know the state of the padmount, we didn't open it up, but no visual signs. We did see secondary voltage on the first padmount (600/400 nominal) of Ag/Bg/Cg; AB/BC/CA of 230/230/400; 240/600/600 (A phase fuse blown?) volts and downstream padmounts 230/2/230; 230/230/400 volts.
When we finally energized the circuit after jumpering out the first padmount the nominal current was 38 amps (due to the cable capacitance) which was the C phase current. When we energized the circuit after jumpering the first padmount 3 arrestors blew, after replacement the system energized, no issues.
The ground current is in phase with the C phase, the only undamaged circuit. Getting a 22 amp ground fault on a 35kV system is hard to do, without it blowing up. I expect it's in the failed padmount, but the current in C phase was normal.
RE: Single phasing delta Y transformers