Using Non Shrink Precision Grout for Precast Concrete
Using Non Shrink Precision Grout for Precast Concrete
(OP)
I am going to use Quickcrete's Cement based Non Shrink Precision Grout for a Pre-Cast Communications Vault and Lid I am making. The vault is 4x6x4. 3" thick Side Walls. I am adding 25#'s of 3/8" Pea Rock to each 60#pound bag of Grout per the instructions to keep its High Strength Properties. The reason I want to use this is because 9500#PSI 65.5 MPa 3 day Strength and its flow-ability. I will be adding 1/2 fiberglass rebar to the precast for strength as well. I talked to Quickcrete and they said it could be done. Let me know your thoughts.
RE: Using Non Shrink Precision Grout for Precast Concrete
Rod Smith, P.E., The artist formerly known as HotRod10
RE: Using Non Shrink Precision Grout for Precast Concrete
RE: Using Non Shrink Precision Grout for Precast Concrete
With that out of the way, on to my next question. Why do you need high strength concrete/grout for this?
Rod Smith, P.E., The artist formerly known as HotRod10
RE: Using Non Shrink Precision Grout for Precast Concrete
RE: Using Non Shrink Precision Grout for Precast Concrete
Rod Smith, P.E., The artist formerly known as HotRod10
RE: Using Non Shrink Precision Grout for Precast Concrete
RE: Using Non Shrink Precision Grout for Precast Concrete
The difference between handling a 4000lb box and a 7000lb box would not seem to be that significant, but I guess if it matters, it matters.
Btw, the capacity of the walls and the slabs for bending is barely changes for different concrete strengths. I hope you're not reducing the wall thickness based on the use of higher strength concrete; it doesn't really work that way. Reducing the wall thickness requires increasing the reinforcing to maintain the bending strength, but that only goes so far; you also need enough concrete over the reinforcing to protect it from corrosion. The inch or so of cover you get with a 2 1/2" thick wall won't be enough to keep the steel from rusting for very long.
Rod Smith, P.E., The artist formerly known as HotRod10
RE: Using Non Shrink Precision Grout for Precast Concrete
RE: Using Non Shrink Precision Grout for Precast Concrete
What's the 'wet' density of the grout you're planning on using? At 4" thick and 145pcf (typical for concrete), I calculate about 4800 lbs for just sides and bottom slab.
Rod Smith, P.E., The artist formerly known as HotRod10
RE: Using Non Shrink Precision Grout for Precast Concrete
RE: Using Non Shrink Precision Grout for Precast Concrete
Btw, by my math, you're still over 3800 lbs, with a 4" wall.
Rod Smith, P.E., The artist formerly known as HotRod10
RE: Using Non Shrink Precision Grout for Precast Concrete
RE: Using Non Shrink Precision Grout for Precast Concrete
RE: Using Non Shrink Precision Grout for Precast Concrete
RE: Using Non Shrink Precision Grout for Precast Concrete
RE: Using Non Shrink Precision Grout for Precast Concrete
Ok, hold up a second...your "box" only has 3 sides? That would change everything. That makes two of the sides unsupported cantilevers (according to your calculations, the 2 6' long sides), and that's a recipe for failure if it's going in the ground and will be subjected to soil loads.
Have you looked into plastic boxes?
Rod Smith, P.E., The artist formerly known as HotRod10
RE: Using Non Shrink Precision Grout for Precast Concrete
RE: Using Non Shrink Precision Grout for Precast Concrete
RE: Using Non Shrink Precision Grout for Precast Concrete
RE: Using Non Shrink Precision Grout for Precast Concrete
Rod Smith, P.E., The artist formerly known as HotRod10
RE: Using Non Shrink Precision Grout for Precast Concrete
You are going to get WAY better quality control if you buy concrete from a concrete plant than you are if you try to mix it yourself. I can basically guarantee you you aren't going to get the result you want here. You're talking about mixing somewhere between a 1 and 1 1/2 full yards of concrete. Have you ever mixed concrete by hand? This is a LOT of concrete.
RE: Using Non Shrink Precision Grout for Precast Concrete
RE: Using Non Shrink Precision Grout for Precast Concrete
Originally, this was proposed to be a conventional concrete stitch pour, but in the end, the contractor wanted to cast the stitch pour and apply the prestress in ~4 hours. Minimum strength at stressing was required to be 25 MPa (3600 psi). No readily supplied concrete mix was able to do this, so in the end the option was to go with a fast-setting grout with coarse aggregates (up to 10 mm / 3/8") added to it (25 MPa (3600 psi) strength in 4 hours, about 100 MPa (14,500 psi) at 28 days). An awful lot of planning and testing was put into the mix design to satisfy everyone that the strength would be achieved, and that there would be no issues with flash setting, shrinkage, excessive heat of hydration, etc. etc. The grout-aggregate mix was delivered from the supplier's batch plant in a concrete mixer.
So, I believe it can be done, but the grout-aggregate mix shouldn't be substituted for concrete without a lot of consideration.