SF6 Switch/breaker at very low gas pressure

SF6 Switch/breaker at very low gas pressure

SF6 Switch/breaker at very low gas pressure

(OP)
I know you do not operate an SF6 breaker if gas pressure is low, but assume dead tank SF switch where there is at least a little positive pressure:
a) Is there a gas pressure level where there a risk of an internal line to ground fault?
b) If the breaker is open, is there a gas pressure where there is a risk of a flashover across open contacts?
If the pressure goes to 0, there is now a risk of air entering the tank. Again:
c) If there is a chance air has entered the tank, how large is the risk of an internal line to ground fault?
d) If there is a chance air has entered the tank, how large is the risk of flashover across open contacts?
Customer is reporting a 15kV SF6 padmount 5 way switch with very low gas pressure, and taking the switch out of service is going to be a major system disruption.

J.Horak

RE: SF6 Switch/breaker at very low gas pressure

Actually we specify three levels on our breakers. The first is alarm, the second is a trip, and the lowest is block trip.

RE: SF6 Switch/breaker at very low gas pressure

(OP)
Did you ever hear a discussion on whether there a point of low SF6 where internal flashover becomes a concern? I suppose in a well monitored breaker it is not realistic to go to 0 pressure without first getting an alarm and having time to isolate the breaker, but that is not the case here. Customer will lose loads if they take the switch out of service, and gauge shows a little pressure, so they are leaving it energized while they work to get the mfr to take a look.

J.Horak

RE: SF6 Switch/breaker at very low gas pressure

I think we have some of those distribution switches. And only a few have monitoring.
I think in some cases it becomes necessary to bite the bullet.
That said we only allow four way switches. When you get bigger, the problems get bigger.

For a breaker it could mean a bus outage, which is why we are moving from straight bus to ring, and breaker and a half.
But with higher voltage breakers, we have disconnects. With distribution gear all you have is elbows.

We moved to SF6 distribution switches, after we had problems with open air switches, and the alignment issues.
We are now looking at solid dielectric switches. Or in some cases reclosers.

Anyway the industry push is away from SF6.

RE: SF6 Switch/breaker at very low gas pressure

Generally speaking, the SF6 switchgear can withstand rated voltage even with SF6 gas pressure going down to zero.
The risk is when there is over voltage (due to single phase to ground faults in the system) or when there is a switching (due to Vacuum breaker or contactor switching etc.) or lightning surge.
Further, if the switchgear is left in service for quite sometime in service after the SF6 gas pressure came down to zero, there is risk of air entry and that can lead to partial discharges and flashovers.
How much time we have before any such thing happens depends on how big is the leak and how moist or polluted is the air in the area etc.
It is a calculated risk that should be taken after assessing the consequences versus benefits.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

Low-Volume Rapid Injection Molding With 3D Printed Molds
Learn methods and guidelines for using stereolithography (SLA) 3D printed molds in the injection molding process to lower costs and lead time. Discover how this hybrid manufacturing process enables on-demand mold fabrication to quickly produce small batches of thermoplastic parts. Download Now
Design for Additive Manufacturing (DfAM)
Examine how the principles of DfAM upend many of the long-standing rules around manufacturability - allowing engineers and designers to place a part’s function at the center of their design considerations. Download Now
Taking Control of Engineering Documents
This ebook covers tips for creating and managing workflows, security best practices and protection of intellectual property, Cloud vs. on-premise software solutions, CAD file management, compliance, and more. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close