Spot Sampling of Fresh Concrete per EN 12350-1
Spot Sampling of Fresh Concrete per EN 12350-1
(OP)
For my British mates although the Canucks, Yanks and others can add their 2 cents or twopence to the thread.
ASMT C 172 requires sampling of fresh concrete to be a composite sample whereby the initial 10% and last 90% of the discharge is ignored and not used.
EN 12350-1 permits spot or composite sampling (thinking specifically for slump). Section 4.2 states that the composite sample, as per ASTM C 172 let the first and last part of the mixer to be disregarded in sampling. For spot sampling, it doesn't actually specify that the initial part of the discharge is to be disregarded. Yet, as per the reference seen in : https://qaqcconstruction.com/2017/04/01/sampling-o... suggests that it must be disregarded.
I am looking for "practice" experience for spot sampling.
ASMT C 172 requires sampling of fresh concrete to be a composite sample whereby the initial 10% and last 90% of the discharge is ignored and not used.
EN 12350-1 permits spot or composite sampling (thinking specifically for slump). Section 4.2 states that the composite sample, as per ASTM C 172 let the first and last part of the mixer to be disregarded in sampling. For spot sampling, it doesn't actually specify that the initial part of the discharge is to be disregarded. Yet, as per the reference seen in : https://qaqcconstruction.com/2017/04/01/sampling-o... suggests that it must be disregarded.
I am looking for "practice" experience for spot sampling.
RE: Spot Sampling of Fresh Concrete per EN 12350-1
Of all the projects you have attended, how often have you seen the testing staff actually follow ASTM C172? I feel that I have followed it, on rare occasions. Typically, I see the discharge aimed into the wheelbarrow and the pour resumed.
RE: Spot Sampling of Fresh Concrete per EN 12350-1
RE: Spot Sampling of Fresh Concrete per EN 12350-1
I'm sure we could share thousands of stories about how standard procedures aren't followed in real life. It keeps life interesting.
RE: Spot Sampling of Fresh Concrete per EN 12350-1
If C94 is followed, the first part of the load should be the same as the last part of the load. Why is conflicting with its own committee requirements? Welcome to standards development in ASTM
RE: Spot Sampling of Fresh Concrete per EN 12350-1
RE: Spot Sampling of Fresh Concrete per EN 12350-1
RE: Spot Sampling of Fresh Concrete per EN 12350-1
RE: Spot Sampling of Fresh Concrete per EN 12350-1
I won't yell at anybody on the job site, but I can be really ornery if they want to start trouble.
RE: Spot Sampling of Fresh Concrete per EN 12350-1
On occasion the tech "decided" that his sample was bad and needed to take another one a few minutes later.
This is not following the standard to the letter, but it accomplished the intent.
The only issue I have ever had from the plant were trucks that were late, and the batch expired. Which to be fair was not the drivers fault 99% of the time.