Commissioning an internal floating roof tank and prepping for Maintenance
We are putting our first internal floating roof tank into service. Does anyone have any guidance for whether we need to take special precautions for LEL in the upper section of the tank during initial fill. My understanding as as we fill it in order to float it off the legs the vapor will be pushed out a breather vent until the roof begins to fully float on the liquid. Once it it floating the double seals and large vent on the top will be sufficient to prevent LEL build up in the upper section. But I am concerned during the initial fill. The material is a hexane like material.
And in 3 years when we have to take it our of service for an internal inspection and set the roof on its legs by emptying it slowly, air will be drawn through a vacuum break into the section below the floating roof as we fully empty. Again I am concerned about LEL below the roof at that point.
The tank is grounded but is that really enough. The amount of static to light off a hydrocarbon is very tiny (one source says hexane is 0.011 mj) . Trying think of commissioning and prepare for maintenance procedures
thanks
thanks
RE: Commissioning an internal floating roof tank and prepping for Maintenance
You need to assume that the interior of the tank is at or above LEL at ALL times. An IFR reduces considerably the amount of vapour which is otherwise vented out through the roof vents, but it doesn't eliminate it.
IMHO this - "Once it it floating the double seals and large vent on the top will be sufficient to prevent LEL build up in the upper section" is NOT CORRECT.
When first filling the amount of vapour being released into the tank space is large and you need to consider how this excess quantity of vapour is released from the tank vents and if it causes any further risk due to a vapour cloud from the main tank vents.
When you empty for maintenance you might need to think about flooding the interior of the tank with Nitrogen as you lower the liquid level below the roof level to reduce the risk of an explosion.
From my point of view, the safest way is to float the roof using inert gas such as CO2 or N2. We usually fill through the sample point pipes for couple of hours and then starting the filling process. The risk here is that the inert gas might lead to O2 deficiency and should be considered when entering into the roof (i.e. leg repositioning).