Commissioning an internal floating roof tank and prepping for Maintenance

Commissioning an internal floating roof tank and prepping for Maintenance

Commissioning an internal floating roof tank and prepping for Maintenance

(OP)
We are putting our first internal floating roof tank into service. Does anyone have any guidance for whether we need to take special precautions for LEL in the upper section of the tank during initial fill. My understanding as as we fill it in order to float it off the legs the vapor will be pushed out a breather vent until the roof begins to fully float on the liquid. Once it it floating the double seals and large vent on the top will be sufficient to prevent LEL build up in the upper section. But I am concerned during the initial fill. The material is a hexane like material.

And in 3 years when we have to take it our of service for an internal inspection and set the roof on its legs by emptying it slowly, air will be drawn through a vacuum break into the section below the floating roof as we fully empty. Again I am concerned about LEL below the roof at that point.

The tank is grounded but is that really enough. The amount of static to light off a hydrocarbon is very tiny (one source says hexane is 0.011 mj) . Trying think of commissioning and prepare for maintenance procedures

thanks

RE: Commissioning an internal floating roof tank and prepping for Maintenance

I repeat what I said in your other post.

You need to assume that the interior of the tank is at or above LEL at ALL times. An IFR reduces considerably the amount of vapour which is otherwise vented out through the roof vents, but it doesn't eliminate it.

IMHO this - "Once it it floating the double seals and large vent on the top will be sufficient to prevent LEL build up in the upper section" is NOT CORRECT.

When first filling the amount of vapour being released into the tank space is large and you need to consider how this excess quantity of vapour is released from the tank vents and if it causes any further risk due to a vapour cloud from the main tank vents.

When you empty for maintenance you might need to think about flooding the interior of the tank with Nitrogen as you lower the liquid level below the roof level to reduce the risk of an explosion.

Remember - More details = better answers
Also: If you get a response it's polite to respond to it.

RE: Commissioning an internal floating roof tank and prepping for Maintenance

The key is to limit this transitional time between the 'lean' and 'rich' atmospheres so you don't stay in the explosive range. Standard floating roof storage tank RAGAGEP though does not typically take any special precautions into account (when designed and operated to API650, API 2510, NFPA 30, NFPA 499, NFPA 780, etc. and meeting and operated per 40 CFR applicable CC or Kb subarts). The downside to trying to do things like nitrogen purge for the vapor space above the roof is that you still have a point where you go from rich to lean or back again as the nitrogen is introduced or removed...there is no way to avoid 'paying that bill' without just a continuous blanket or other vapor handling system.

RE: Commissioning an internal floating roof tank and prepping for Maintenance

The initial fill has to be very slow (flowrate <1m/s), until the rood is fully afloat. We usually start by filling another tank and then slow "cracking" the valve on the tank that will be put back in service. However, there are risk involved as the space in the tank between the product and the roof will be within the explosive range .

From my point of view, the safest way is to float the roof using inert gas such as CO2 or N2. We usually fill through the sample point pipes for couple of hours and then starting the filling process. The risk here is that the inert gas might lead to O2 deficiency and should be considered when entering into the roof (i.e. leg repositioning).

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

Low-Volume Rapid Injection Molding With 3D Printed Molds
Learn methods and guidelines for using stereolithography (SLA) 3D printed molds in the injection molding process to lower costs and lead time. Discover how this hybrid manufacturing process enables on-demand mold fabrication to quickly produce small batches of thermoplastic parts. Download Now
Design for Additive Manufacturing (DfAM)
Examine how the principles of DfAM upend many of the long-standing rules around manufacturability - allowing engineers and designers to place a part’s function at the center of their design considerations. Download Now
Taking Control of Engineering Documents
This ebook covers tips for creating and managing workflows, security best practices and protection of intellectual property, Cloud vs. on-premise software solutions, CAD file management, compliance, and more. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close