MV cables crossing a Pipeline with cathodic protection
4

MV cables crossing a Pipeline with cathodic protection

MV cables crossing a Pipeline with cathodic protection

(OP)
Hi All

I have a case with an underground pipeline (equipped with cathodic protection) that I need to cross with a MV cables underground trench and couldn't find some reference or litterature regarding the possible impacts of the MV lines on the cathodic protection, minimum clearance...

Appreciate if anyone can support on this or provide some helpful reference standards.
Thanks & Regaards

RE: MV cables crossing a Pipeline with cathodic protection

2
Crossing pipelines with cables, especially buried ones, is not a big issue. happens all the time.

Overhead high voltage (> 30kV) in parallel can cause issues if you don't do something about it, but it shouldn't be anything to worry about.

Min clearance is usually 300-500mm - depends on the pipeline owner. But this is purely for protection against impact.

Remember - More details = better answers
Also: If you get a response it's polite to respond to it.

RE: MV cables crossing a Pipeline with cathodic protection

2
MV and crossing rather in parallel are low risk, it is probably not a concern, if further it is a multiplex/multicore I would not be concerned at all.

As noted above clearance concern is more defined by future maintenance considerations and utility/owner requirements.

AS/NZS 4853 is the applicable standard to my region of the world. It may not apply from you, however in the reference pretext it may provide some insight into other relevant/international standards.

RE: MV cables crossing a Pipeline with cathodic protection

(OP)
Thank you LittleInch and JezNZ for the valuable information

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

Low-Volume Rapid Injection Molding With 3D Printed Molds
Learn methods and guidelines for using stereolithography (SLA) 3D printed molds in the injection molding process to lower costs and lead time. Discover how this hybrid manufacturing process enables on-demand mold fabrication to quickly produce small batches of thermoplastic parts. Download Now
Design for Additive Manufacturing (DfAM)
Examine how the principles of DfAM upend many of the long-standing rules around manufacturability - allowing engineers and designers to place a part’s function at the center of their design considerations. Download Now
Taking Control of Engineering Documents
This ebook covers tips for creating and managing workflows, security best practices and protection of intellectual property, Cloud vs. on-premise software solutions, CAD file management, compliance, and more. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close