DC drive, current curve

DC drive, current curve

DC drive, current curve

(OP)
Hello all
Can anyone here in the forum explain the reason for the steep peaks in this current curve measured in a dc drive (ASEA Tyrak8) at high load. The fault was detected after a disconnect for overcurrent, from the drive's electronic overload protection. The system could be restarted shortly after and then apparently operating normally. The current limit was then adjusted to In. DC-motor runs fine as before. Have checked trigger pulses, but not on thyristors, too dangerous during operation. Current measurement is from the drive's current transformers in the 3 phases. The peaks in the current curve is only present at high load. The customer did not want to spend time on troubleshooting at the time as the system was working satisfying and also was hard to do without.

RE: DC drive, current curve

My guess is that the thyristors under high load have overlapping on periods (trigger angle too small or before zero crossing), or something related.
Could the current limit (brickwall) be set too high?


RE: DC drive, current curve

(OP)
Thank you for your interest.
The current limit is set according to the motor In = 527A which is much lower than the drive In = 800A, the overcurrent protection is set to motor In x 1.05.
Yes, the peaks are there when the thyristors overlap and from what I have been able to find about thyristor rectifiers, this commutation will take place with high current for a time determined by, among other things, the impedance of the network. That could fit with a weak phase as the peaks are there along with current in a certain phase, but if there should be a weak connection in a phase I would expect, at this high current, very large heat generation here. Are there parts of a network that will be able to handle that.

RE: DC drive, current curve

The current limit setting does not matter if the trigger circuit is misbehaving.
The usual case with AC is that the trigger circuit turns the thyristor on, and it turns off at the following zero crossing.
If the trigger circuit fires early, the result can be current flowing between phases. If the overlap increases much more (possible if the cause is a failing component), expect the thyristor protection fuses to open.
I have seen these event, but I do not myself do the troubleshooting. Perhaps one of the troubleshooters here can provide some hints.

ASEA has a rebuild kit that replaces the entire controller, a scheduled rebuild might be a reasonable approach depending on what troubleshooting finds. Link

RE: DC drive, current curve

Check input L1 saturation current level.
Seem that one or even two of them enter in (partial) saturation above a current value.

RE: DC drive, current curve

If the AC conductors are accessible, you can see in which branch ie the thyristor is problem with ampere clamps by measuring current. That won't help you now, but it can help with defect repair in order to shorten the repair time.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

Low-Volume Rapid Injection Molding With 3D Printed Molds
Learn methods and guidelines for using stereolithography (SLA) 3D printed molds in the injection molding process to lower costs and lead time. Discover how this hybrid manufacturing process enables on-demand mold fabrication to quickly produce small batches of thermoplastic parts. Download Now
Design for Additive Manufacturing (DfAM)
Examine how the principles of DfAM upend many of the long-standing rules around manufacturability - allowing engineers and designers to place a part’s function at the center of their design considerations. Download Now
Taking Control of Engineering Documents
This ebook covers tips for creating and managing workflows, security best practices and protection of intellectual property, Cloud vs. on-premise software solutions, CAD file management, compliance, and more. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close