Longitudinal Split in wood

Longitudinal Split in wood

Longitudinal Split in wood

(OP)
Hi All -

I have inspected an attic with wood trusses. It was built 40-years ago. I found numerous number of split members. The members are in both tension members and compression members. I could not identify a pattern. They are random. This image represents the type of cracks I found.

I did a quick analysis of the truss and found it to be fine (4/12 Fink truss spans 28').

What could the cause of suck split be?

Thanks in advance.

RE: Longitudinal Split in wood

Is it all the way through the section? Cracks and checks are fairly common in lumber. I believe there's guidance in the NDS, sorry I don't know the reference directly, or the lumber grading agencies that discuss amount of allowable checks/cracks.

RE: Longitudinal Split in wood

As long as they aren't more than halfway through the member and not in the vicinity of the truss plates, I wouldn't be all that worried.

RE: Longitudinal Split in wood

That looks like the tree pith, especially given the knot locations. Do you have a closer view?

RE: Longitudinal Split in wood

JKJohn,

I agree with Eric C., looks like pith, i.e. the center of the tree. If a crack does not propagate thru the thickness of the member, across the member. It is usually not significant.


Jim


RE: Longitudinal Split in wood

This is a 4x12, correct? That's a pretty beefy member, so it's not unusual to see significant checks around the middle of the member. It's probably just a differential drying type of action. Make sure it doesn't go all the way through (probably not).

While it looks terrible, checking does NOT affect the flexural strength of a member. It does affect the shear strength. If you look at the 1991 or 1997 NDS there should be a factor to INCREASE the shear strength of beams that do NOT have checks like this. Sort of a backwards way of doing it.

The newer NDS codes, I believe, do NOT have this factor. But, from a first principals standpoint it could still be applied.... Long complicated story about why the codes essentially doubled the shear capacity for all wood beams.

I'm not certain about whether it affects tensile or compressive strength. But, if my memory is correct, I don't think it does. Though intuitively I would think it would affect the tensile strength.

RE: Longitudinal Split in wood

Josh - if that's a 4x12, I'd hate to be the one to handle that roll of tape! I think the OP was saying a 4/12 is the slope of the top chord. Proportions look like a 2x4 to me. Maybe a 2x6.

RE: Longitudinal Split in wood

You're probably right. The picture does look a little odd to me.

If it's a small member 2x4 2x6 or such, then that type of checking / splits would be pretty odd. And, it does look like lower grade wood. Maybe worth doubling up the members that are split like this, though I don't want to nail into them much in fear that it'll split more. Anyone use adhesives to double up a damaged member like this?



RE: Longitudinal Split in wood

I agree about that probably being a 2x4. As far as how this affects the truss, tough to say definitively without more info regarding the stresses in the chord, and the depth of the split.

JoshPlum, if you are trying to justify adding a member alongside, my suggestion would be to use a structural epoxy. My experience in the wood product manufacturing industry is that standard construction adhesive simply is not effective enough on wood to wood connections to develop appropriate load sharing. Not sure I agree that it would be as simple as sistering a new chord alongside this truss chord, however.

RE: Longitudinal Split in wood

If the checking creates two separate members, it is significant as S andI are significantly decreased.

Mike McCann, PE, SE (WA, HI)


Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

Low-Volume Rapid Injection Molding With 3D Printed Molds
Learn methods and guidelines for using stereolithography (SLA) 3D printed molds in the injection molding process to lower costs and lead time. Discover how this hybrid manufacturing process enables on-demand mold fabrication to quickly produce small batches of thermoplastic parts. Download Now
Design for Additive Manufacturing (DfAM)
Examine how the principles of DfAM upend many of the long-standing rules around manufacturability - allowing engineers and designers to place a part’s function at the center of their design considerations. Download Now
Taking Control of Engineering Documents
This ebook covers tips for creating and managing workflows, security best practices and protection of intellectual property, Cloud vs. on-premise software solutions, CAD file management, compliance, and more. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close