Typical Anchor Bolt Projection 1
DaveAtkins
I am working on a project where anchor bolt projection is a critical dimension. These are on grade bus stop platforms, where the custom designed shelter (designed by me, not an off the shelf shelter) will be anchored to a mat footing on grade, after which a topping slab containing a snow melt system will be placed over the mat footing.
I have instructed the design team we need a 6" topping slab, based on 4" anchor bolt projection at the shelter column base plates, and 2" cover over the anchor bolt tip. I believe 4" is a typical anchor bolt projection, but have been unable to find confirmation online. I plan to use 1-1/2" grout, and estimate the base plate will be no more than 1" thick (haven't designed them yet).
Is 4" a reasonable dimension for anchor bolt projection?
DaveAtkins
See no reason why that wouldn't work. 1 1/2" of threads above the baseplate. You could reduce 1/2" if you wanted but give a little less margin for install error.
This is copy and paste from PIP STE05121 Anchor Bolt Design Guide ;
( Anchor bolts should project a minimum of two threads above the fully engaged nut(s).)
Typical for Single Nuts , Projection = grout thick + base plate thick.+ 2.0 X anchor bolt dia.
As HTURKAK noted, it will depend on the height of the nut, which is a function of the anchor bolt diameter and the type of nut(s).
A couple of cautions... make sure your anchorrods are weldable and check to see that your grout can be used to 1-1/2" thickness... 1-1/2" grout seems a little thick.
Rather than think climate change and the corona virus as science, think of it as the wrath of God. Do you feel any better?
I'd say that 4" is perfect as a minimum for 3/4" bolt and washer with 1/2" vertical placement tolerance.