The multiple editions of AISC's manual.
I've met an array of engineers that all have their favorite version of AISC's manual (most importantly the Specification). This post is not about the benefits of one versus another. Rather, I'm trying to understand how other engineers fulfill the obligation of using the latest standards adopted by code. By default, it seems like we should all have multiple editions of the manual/specification and know what changes exist in each. However, some people strictly utilize the 9th Edition ASD manual, others the 15th edition, and some in-between, etc.
From what I can tell, subsequent editions of the manual have been focused on creating the lightest and most efficient structures. There are more provisions provided today that will allow certain scenarios to be calculated with a "refined" factor of safety. If that's the case, why doesn't AISC provide exceptions that allow interpretations of older codes.
Can anyone share on how they manage the ongoing updates to each edition?
RE: The multiple editions of AISC's manual.
1/ Use the newest edition or edition referenced by the AHJ for any brand-new construction.
2/ Use the existing edition for existing construction that you are checking. If there is something severely different or improved that has occurred between editions, I would use the "safest" answer but also be cognizant that what exists has existed.
3/ Use best engineering practices regardless of edition, but reference the AHJ's necessary edition on the drawings.
I think the role of the engineer is to make the construction/building safe. I always start with the current code since my standards/methods/tools are all designed for that case. If necessary, I would sharpen my pencil and look at understanding how it has worked.
TL;DR: I approach it from a safety + time management point of view.
As OP alluded to, the Specification is the important part. That is the portion that is legally adopted by the building code. And it is available as a free download from AISC, so there's no excuse for not having it. The rest of the manual is just supporting information and design aids. So as long as you comply with the Specification, you can use the manual however you see fit. But do your due diligence to determine if there is any outdated information that would make your design not comply with the current code.
The biggest differences (other than the really in the weeds analysis stuff) are probably the materials (steel grades, and which spec is standard for such and such shape), and the shape database. Every version has a slightly different database of shapes - some versions add more shapes, some reduce the number. I know recently there has been an initiative by AISC and Bentley/RAM to survey structural firms across the country to get a feel for which shapes are most commonly used and which shapes are rarely used. I'm not sure of the inner workings (can't be that complicated though), but the program they have set up is to send Bentley/RAM your RAM Structural System models of any "significant" structures that the firm has completed. Then I'd assume Bentley extracts/outputs the material takeoffs and adds it to their database. My understanding is that they are trying to reduce the number of rolled sections if possible. Why? Not sure, other than to make life easier for the mills, and so they can save paper in their next edition of the spec....:)
Somewhat sidenote:
A firm I used to work for had a somewhat kinda sorta similar program in place: we'd go through our completed "significant" projects and run the material takeoffs from our RAM models (tonnage, essentially), and compare that with the actual final tonnage of ALL primary and miscellaneous structural steel on the project that which the fabricators would provide us with. This would include every single piece of miscellaneous steel and loose pieces, etc. - deck edge angles, kickers, gusset plates, baseplates, backing bars for full pen welds (crazy, right?), yadda yadda. This only works with the bigger detailers/fabricators because they model the crap out of the entire building using SDS2 or Tekla or whatever. We'd use this to give the clients a somewhat "calibrated" expected tonnage based on square footage and "fanciness" of the project. Pretty neat. IIRC the final tonnage was anywhere between 20-35% higher than the RAM material takeoffs. I think we had about 10 or so large projects in the database when I left.
But...AISC 360 is probably the only code that might be considered (by the user...) kosher to "use" older versions of since it's really more of a reference of sorts, if that makes sense? I.e., nobody is using old versions of ASCE 7 or ACI 318 or IBC, etc. Those evolve much faster and to a greater extent, as I'm sure everyone is aware. NDS might be another code that some people still use slightly out of date versions of (Not so much SDPWS though).
15th Edition is definitely the best out of the 3, as far as connection design goes.
I once had to check the work of a senior engineer. He referenced his textbook from 1962. It was bogus.
More on topic...
I have a 13th b/c of steel class in colleges. Enough co-workers had the 14th edition that I didn't bother to buy one (1 nice thing about 14th and bolting is the increased capacity in bolt shear based on "short connection length"). My current employer bought everyone a 15th edition, so I also have one of those.
When checking an existing structure, I'll start with the current edition. If it tells me that I'm already failing before doing anything to it, then I try to go back to the spec that it was designed under. Though, I usually find it passed more due to the code loading at the time it was designed instead of the analysis/capacity differences.
I agree completely. I've done a lot of work with HSS over the last few years and struggled mightily with the 15th ed. It took me a while, but I figured out why.
There are two basic approaches to laying out such provisions:
Option 1: Detailed cook-book approach that the engineer can follow whether he or she understands what's going on or not. All inclusive, so the engineer doesn't need to know where else to look.
Option 2: lay out the big picture and rely on the engineer's knowledge of the applicable limit states and where to go look for Paul Harvey's "Rest of the Story" (Part 9 in this case).
The 15th ed. Chapter K is in No Man's Land in between these two options.
It doesn't help that Design Guide 24 doesn't coordinate with the 15th edition. You end up having to piece together how to do these checks with the 15th ed. Chapter K, 15th ed. Part 9, and filling in some blanks with the old Design Guide 24.
That's a clear trademark violation of Standards Australia.
On the other hand, 24 years of changes to our steel code amount to adding block shear and correcting typos, so there's definitely a silver lining.
* You no longer check allowable stress versus actual stress; you calculate an ultimate capacity and divide it by omega and compare it to demand
* P-big delta and P-little delta are handled explicitly; you no longer reduce the allowable stress to account for buckling, etc.
Interestingly, when I want to do a quick check of something, I find myself reverting to checking stress, not capacity.
DaveAtkins
IMHO, when AISC imposed LRFD on the industry (around 1979), they made some strategic mistakes:
- They removed the detailing information and some other useful tables from from the manual. This pissed off a lot of people.
- They didn't sell the change to LRFD.
A lot of engineers were very comfortable with the ASD formulae, presentation and just used to doing it. LRFD was a foreign language. So AISC in their wisdom said: "We're changing everything you're used to. Buy our new more expensive manual without as much stuff in it. Or go to the steel manual down the street."I do very little design from the specification. I use the Tables in chapters 3 through 6, which are pretty handy and are in both ASD and LRFD. It's the most current code and the legal code. Still using the 9th edition puts you at risk. Very little risk, but imagine sitting on the witness stand answering the lawyer,"...why aren't you using the current, legal code?"
My Green Book (9th)is the most worn of all of them because it wasn't replaced until the black book (13th edition). I used my Silver Book (LRFD 2nd edition) a lot as well because it had a lot of connection information (in the 2nd volume) that wasn't in some of the newer versions.
Anyone else agree? I've tried to replicate the capacity shown in some connection tables from the 13th and 14th editions. Even when following the design examples provided by AISC, there are values they provide in their design tables and I'm not sure how they arrived at those capacities.
I don't have a copy of the 15th edition manual. Is it worth buying just for the connection design tables? I've also noticed the new combined forces tables lists everything in terms of Moments, and you no longer have to take (8/9)(1/bx 10-3) just to determine available moment (I prefer table 6-1 over the unbraced length tables).
The proponents of this check didn't realize what they had done until the designers were banging their heads on their desks in frustration. Thankfully, this check is gone in the 15th edition.
It would be nice if AISC provided a reference to allow us to track changes on this specific level. Stuff like this leaves me wondering how engineers can stick to one code and not be concerned about constant changes.
That's only if the EOR says to design connections per specific design guidance, right?
Otherwise, WillisV is correct IMO. If nobody tells the delegated designer to use the single plate procedure in Part 10, the delegated designer can use another method as long as the Specification is satisfied.
It's similar to base plate design. The Specification gives the available pressure in the concrete, plate bending strength, and anchor rod strength checks. For the particulars of the calculations, I can pick the elastic method in Blodgett, the DG1 method, use finite element analysis, or whatever other method I can find. I don't have to use the Manual Chapter 14 or Design Guide 1.
1. Who's responsibility is it to determine whether or not to utilize specific design criteria in the overall design? It clearly isn't an agreement between the EOR and the owner of the project. An owner wouldn't even know what that means.
a. If the decision is to be made by the EOR, are they free to ignore any guidance that is not in the specification?
2. You mentioned this being outlined by the EOR to the delegated design engineer. Where I've worked, I've seen many EORs handle their own connections as the owner of the project doesn't want to pay two engineering fees (1 for the EOR on the design, 2 for the sealed engineering applied to steel shop or fabrication drawings with connection details). In that case, the EOR would have to decide how to handle the design of any extended single plate connections before a detailer ever set eyes on it.
This is usually merely a requirement that it meet the code requirements of the authority having jurisdiction over the permitting process. If there are multiple methods of design that can be used (ASD vs LRFD, for example) then it is usually up to the EOR to choose the method most appropriate for the project.
Yes, this is a more common practice on the west coast. But, there are still plenty of cases where the steel fabricator / detailer can save themselves (and the owner) a lot of money on a project by designing the redundant gravity only connections themselves. Though this is more common out east as I understand it.
I hope that we (as a profession) are getting better at exchanging information between engineers and fabricators than we were in the past. I think this is especially true for engineers / fabricators that have worked together multiple times.
Can confirm, having worked in both markets.
East coast: almost all connection design is delegated, including moment connections and braced frame connections. Other "non-primary" structural elements such as stairs and metal studs are also commonly delegated.
West coast / Rockies: almost all, if not all, connections (gravity/moment/brace) are designed in house - excluding "specialty" connections such as BRB and SidePlate connections since they are better/solely equipped to do that. Stairs, metal studs, etc are also commonly included in contracts but not always. Most owners do choose to have EOR design them because it cuts out a bunch of coordination and what have you.
Delegated design is a double-edged sword. Convenient? Yeah. Always ends up with me saying "I should've just done this myself"? Also yeah.
East coaster here. Yes, yes, and yes. This is one of the reasons that I'm working to move away from delegated connection design. By the time I've taken the time to consider all of the necessary items to coordinate the connection (design loads, etc.) and make sure that the connecting elements of the columns and beams work (ever had a connection engineer come back and tell you that your HSS wall is too thin for a moment connection? It's embarrassing...), I might as well size the bolts/welds and put it in a schedule with a typical detail.
I've been on projects with an owner's representative that was not part of the licensed design professionals providing design work on the job. I've also been on projects under the direct supervision of an architect. In either case, I haven't seen either one define any sort of requirement for design besides providing the applicable building code that the design was to satisfy. In some cases, not even that was supplied as we had to determine, on our own, the applicable code at the time of permitting. In my experience, I've never come across an architect who was familiar enough with AISC (as an example) that would be able to require the torsional checks for extended single plate connections.
From my experience, a majority of projects have been completely unguided and it was up to the structural engineer to satisfy all requirements as best as they could. If you are lucky enough (or unlucky), you get comments from a building department review in the areas that were lacking.
This hasn't been my experience in the east coast. When scheduling your design loads, do you provide a required moment, shear, axial, or whatever applicable scenario for each connection? Do you specify when loads occur in the same case or if you want the capacity to satisfy ASD or LRFD? It may seem strange that I'm asking, but I haven't experienced delegated steel connection loads.
Does anyone else feel like they've spent so much time learning demands, analysis, and design for a variety of materials and types of structures, that the art of practicing engineering is somewhat of a convoluted mess when it comes to jurisdictions, project politics, and economical decisions?
After answering 5000 RFIs asking essentially this question, I've started using a table with a whole bunch of notes. Table includes strictly nominal connection loads (load case basis) (DL, LL, LLr, SL, WL, EQ). I am very explicit about which code I have used to arrive at these loads, and I am very explicit about which code is to be used by the connection designer to combine the loads to arrive at the design load. This has reduced RFIs from connection designers and OWSJ designers, so that's good. Think of it as "if I were designing this, what information would I need?" As to which methodology they choose...it's kindof a grey area to be honest. A lot of folks I've worked with are adamant about using EITHER ASD or LRFD throughout the entire design, bar none. However, in my opinion, it seems that the connection designer should be able to choose which methodology will provide the most economical design. After all, that's kindof the whole point of moving to LRFD, no? But that's east coast market.
West coast / Rockies, you're most likely in SDC D+ (or D-? however you want to think about it...), so most of your SFRS connections are "special". I.e., capacity based design in a sense. So (moment frame example), you've got a beam size, beam size says connection needs to be *this* strong. And that's pretty much that - delegated or in-house. It's pretty cut and dry once you get over the fact that a 2" thick Gr. 50 end plate isnt the end of the world.
That's how we'd handle most brace and moment connections in earthquake town. Kinda like I said above - beam size >> spreadsheet >> end plate thickness, doublers, continuity plates, bolts >> schedule with Y-axis = beam size, X-axis = column size >> schematic detail + schedule >> connections fabb'd. Sometimes it works and the detailer knows the program. Sometimes you get some dude who does 'metalwork' in his shop and has no idea what the hell any of that means so you've got to essentially just do it yourself anyway.
So. I dunno where I'm going with any of that. If I had it my way I'd design my connections and delegate stairs and metal studs and all that overly-involved and uninteresting stuff to someone else who'd also rather not be doing that.