PSV Selection

PSV Selection

PSV Selection

(OP)
Hi All,
I'm reviewing fuel gas system documents that includes, KOD, Filter separators and pressure reducing valves. contractor engineering team has selected fire case psv for KOD and filter separators while fuel gas is natural dry gas with dew point -30 C. I feel that contract engineering team don't have idea how to select psv case. Can anyone put more light on this issue and how discuss with contractor to change fire case to blocked case.
Best Regards

RE: PSV Selection

The contractor needs to evaluate EVERY credible scenario, and select the worst case/largest relief area required. Defaulting to fire case works a lot, but not all the time.

Good Luck,
Latexman

RE: PSV Selection

The contractor should at the very least be considering the causes of overpressure contained in section 4.0 of API-521.


*** Per ISO-4126, the generic term
'Safety Valve' is used regardless of application or design ***

*** 'Pressure-relief Valve' is the equivalent ASME/API term ***

RE: PSV Selection

(OP)
Thanks for quick response, i will communicate with contractor to share details fire case selection.

RE: PSV Selection

As a contract company engineer working on just this FG handling unit, you may not have all the details of the system upstream of the FG system. Until you know what process controls, safety devices, process design pressures/temps are installed or specified upstream, it is often not possible to judge if there are process safety concerns with overpressure protection shown on drawings you've been given. Operating Company plant process engineers may disclose such info if requested, but they may not always.

RE: PSV Selection

(OP)
George,
Thanks for your input. I know that operating company engineers will drive the contract company engineers to complete the task as per company operating and control philosophy. anyhow your inputs give me more clarity for further communication with contract company.

RE: PSV Selection

We need data.

Does the blocked in case exceed the MAWP of the vessels??

If not then the fire case (also blocked in) becomes that is actually the design case

We don't know as you haven't provided any details.

Remember - More details = better answers
Also: If you get a response it's polite to respond to it.

RE: PSV Selection

(OP)
Sir LittleInch, contractor not yet submitted details, he just sent us BFD and P&ID for our review. I noted that he selected fire case psv while our system have no sources of fire around. Fuel gas supply to cement and power plant. total design capacity is 92 MMSCFD and design pressure is 42 barg. my concern is if there is no fire source then why selected fire case psv.

RE: PSV Selection

Quote (MIANCH)

... our system have no sources of fire around... there is no fire source ...

Quote (MIANCH)

... fuel gas system ... includes, KOD, Filter separators and pressure reducing valves....
If there is supposed to be any normal liquid level in a vessel then pool fire case to be considered. See table 4 API 521-2014 for details.
What about a pool fire caused by spilled combustible liquid accumuilated in KOD and separators? Do those have liquid level measurement or control means?

RE: PSV Selection

(OP)
Yes shvet, liquid level measurement included. will check API 521 as you mentioned.

RE: PSV Selection

SWAGs since no data:

Can pressure reducing valve fails wide open be a scenario?

If level instrument fails wide open and you get FG blow through, is that a scenario? Perhaps to downstream equipment.

Good Luck,
Latexman

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

Low-Volume Rapid Injection Molding With 3D Printed Molds
Learn methods and guidelines for using stereolithography (SLA) 3D printed molds in the injection molding process to lower costs and lead time. Discover how this hybrid manufacturing process enables on-demand mold fabrication to quickly produce small batches of thermoplastic parts. Download Now
Design for Additive Manufacturing (DfAM)
Examine how the principles of DfAM upend many of the long-standing rules around manufacturability - allowing engineers and designers to place a part’s function at the center of their design considerations. Download Now
Taking Control of Engineering Documents
This ebook covers tips for creating and managing workflows, security best practices and protection of intellectual property, Cloud vs. on-premise software solutions, CAD file management, compliance, and more. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close