Cooling Tower Replacement
Cooling Tower Replacement
(OP)
Hello All, Newbie here, just want to get some expert advice, with regards to cooling tower replacement.
Do you just get the same specs of the cooling tower and replace it same for same? or you still calculate the heat load of the building to compare to existing?
second, when you change the cooling tower and condenser water pump, are you required also to replace VFD / controls or you can reuse what is there?
Third, for permit documents, do you add the rental cooling tower in the plans or just let the contractor figure it out? would really appreciate some advice. Thank you.
Do you just get the same specs of the cooling tower and replace it same for same? or you still calculate the heat load of the building to compare to existing?
second, when you change the cooling tower and condenser water pump, are you required also to replace VFD / controls or you can reuse what is there?
Third, for permit documents, do you add the rental cooling tower in the plans or just let the contractor figure it out? would really appreciate some advice. Thank you.
RE: Cooling Tower Replacement
You can re-use what still works and has lot of expected life left if the size is correct.
I wouldn't just re-use specs, you are installing a new tower, not the 30 year old one. And any blind copying also copies any old errors.
For permit, ask the JHA what they require. From my point, you could be in Qatar, Sweden, or Brazil. they all will require different items. Probably depends on how long you need the temporary tower. Decades, years, days?
RE: Cooling Tower Replacement
RE: Cooling Tower Replacement
RE: Cooling Tower Replacement
RE: Cooling Tower Replacement
Second, comply with the selection with ASHRAE 90.1 energy standard. These times, even the “low” efficiency towers are significantly more efficient than the Standard 90.1 minimum of 38.2 gpm/hp (3.2
L/s·kW).
Check the existing clearance around the tower to prevent the recycling of moist air, follow manufacturer's recommendation
The problem with the world is that intelligent people are full of doubts, while stupid ones are full of confidence.
-Charles Bukowski-
RE: Cooling Tower Replacement
I always try to meet the latest energy code when I upgrade any system.
I would just put a note for the rental and show where it's going to connect into the system. I might include it in a schematic drawing.
RE: Cooling Tower Replacement
RE: Cooling Tower Replacement
Some things that came up with the cooling tower- re-evaluate the deisgn temp of the water is being used for. E.g. could be WSHP's (Water Source Heat Pumps), or AHU's or a variety of things. Depending on the system type, you may have different needs for the controls of the cooling tower system. My project included replacing a shell-and-tube heat exchanger. Where I work, we typically provide VFD (VSD's (Variable Frequency Drives or Variable Speed Drives)) with the cooling tower fan. Depending on the area you are in, you may get credit for the make-up water for the cooling tower-in that case you may need to get a city/county provided water meter for you to get those credits.
If you haven't already, create a P&ID (Process and Instrumentation Diagram) which will help you visualize what's happening where. A P&ID will also make it more convenient for you to see what kind of controls will be necessary where.
I also second the others' opinions on here that you should reach out to the cooling tower sales reps on helping you select a cooling tower. There can be a lot of variation in how you set them up and how they integrate into your systems (bypass or no bypass being one example).
Depending on who you are designing for, getting in touch with the people who maintain the system would be a good idea. I ending up getting some services from a structural engineer to design some custom railing for accessing the top of the cooling tower.
Some other points in no particular order of any kind that I think will help you:
RE: Cooling Tower Replacement
RE: Cooling Tower Replacement
RE: Cooling Tower Replacement
Consider the document attached related to VFD.
Pierre
RE: Cooling Tower Replacement
consider chilled and condenser water reset configuration. using VFD for condenser water pump with a minimum flow setpoint to avoid scaling and low flow conditions may save power.