Mixed AC voltage levels in the same multi-conductor cable
2

Mixed AC voltage levels in the same multi-conductor cable

Mixed AC voltage levels in the same multi-conductor cable

(OP)
Hi Folks,

A contractor is in discussion with a client stating that it is possible to run mixed AC voltage levels within one multi-conductor cable, e.g., a 5/Cx25mm²

The system in question is a supply cable feeding a step-down transformer at 460 VAC running from a panel and stepping it down to 127VAC single phase+neutral which should go back to the same panel. The load shall be HVAC units.

Is this possible and if not are there standards indicating this?

In advance thanks for any feedback.

RE: Mixed AC voltage levels in the same multi-conductor cable

In the US, it's generally allowed under the National Electrical Code, provided all conductors are insulated for the highest voltage. But the NEC is a safety code, and not a design guide. It sounds like the project is not in the US however.

RE: Mixed AC voltage levels in the same multi-conductor cable

(OP)
Hi @dpc,

Thanks for the prompt response. Indeed the project is not in the US but some NEC codes still apply here within the electrical regime.
We are mostly IEC governed. It just does not seem to be a common practice to mix two voltage level conductors in the same cable bundle. In this case, it will be an L1+L2(460VAC) "entering" the transformer and L+N+GND(220VAC) "leaving" the transformer in the same multi-conductor cable. That is why I was wondering if this is acceptable within norms and codes such as IEC/ANSI/IEEE, etc.

RE: Mixed AC voltage levels in the same multi-conductor cable

Dear Mr. sparkview (Electrical)(OP)4 Apr 22 19:05
"... the project is not in the US but some NEC codes still apply... We are mostly IEC governed. It just does not seem to be a common practice to mix two voltage level conductors in the same cable bundle..... it will be an L1+L2(460VAC) "entering" the transformer and L+N+GND(220VAC) "leaving" the transformer in the same multi-conductor cable. ... I was wondering if this is acceptable within norms and codes such as IEC/ANSI/IEEE, etc..."
1. Cable insulation voltage consideration: I look at it that the (incoming L1-L2 460VAC), the (out going L+N+GND(220VAC). They are within the LOW voltage rating i.e. <1000V per IEC/ANSI/IEEE/NEC, etc... The cable rated good for 460VAC, will be also good for (220VAC). Electrical insulation-wise OK.
2. Safety-wise, (460VAC) and (220VAC) are widely used; technicians generally are aware and considered it of the same danger level.
3. Core marking-wise: IEC L1(Brn),L2(Blk),L3(Gry),N(Blu), E(YwGn) ; ANSI/NEC/IEEE with different colours.
3.1 In your case, perhaps you should use all four 1,2,3 and 4 cores with BLACK colour, with E remain (YwGn). Sleeve core 1 and 2 "460VAC", core 3 (220VAC) L[Brn], core 4 (220VAC) N[Blu]; to avoid confusion and complied with BS7671 or IEC. But NOT to US practice.
Che Kuan Yau (Singapore)

RE: Mixed AC voltage levels in the same multi-conductor cable

It isn't commonly done because it rarely makes sense. The wire size of the reduced voltage will be twice the size of the primary needs. This means you'll be buying runs of much larger conductor than needed for the primary.

Keith Cress
kcress - http://www.flaminsystems.com

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

Low-Volume Rapid Injection Molding With 3D Printed Molds
Learn methods and guidelines for using stereolithography (SLA) 3D printed molds in the injection molding process to lower costs and lead time. Discover how this hybrid manufacturing process enables on-demand mold fabrication to quickly produce small batches of thermoplastic parts. Download Now
Design for Additive Manufacturing (DfAM)
Examine how the principles of DfAM upend many of the long-standing rules around manufacturability - allowing engineers and designers to place a part’s function at the center of their design considerations. Download Now
Taking Control of Engineering Documents
This ebook covers tips for creating and managing workflows, security best practices and protection of intellectual property, Cloud vs. on-premise software solutions, CAD file management, compliance, and more. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close