Convert generator output to 120vac
Convert generator output to 120vac
(OP)
Hello, I have a Stamford S0 series alternator head controlled by an AS540 avr that is currently set for 120/240vac. I would like to change the winding outputs to 120vac. I know how to change the wiring and set the jumper on the avr but I have a question about the maximum output power.
The field coil is 17.5 ohms and the avr's maximum output power is 82 volts at 200vac. The avr wants a minimum of 15 ohms on the field at 240vac but states a minimum of 10 ohms below 175vac which is where my conversion will be operating. My calculations say that at 4 amps (avr max), the field voltage is 70 volts.
My concern is that the avr won't be able to generate the voltage on the field needed to get maximum power out on the gen set. Will I have to make other changes or will this work just fine?
Dave
The field coil is 17.5 ohms and the avr's maximum output power is 82 volts at 200vac. The avr wants a minimum of 15 ohms on the field at 240vac but states a minimum of 10 ohms below 175vac which is where my conversion will be operating. My calculations say that at 4 amps (avr max), the field voltage is 70 volts.
My concern is that the avr won't be able to generate the voltage on the field needed to get maximum power out on the gen set. Will I have to make other changes or will this work just fine?
Dave
RE: Convert generator output to 120vac
RE: Convert generator output to 120vac
RE: Convert generator output to 120vac
RE: Convert generator output to 120vac
If this is a single-phase generator the line-line voltage is 240 V and line-neutral voltage is 120 V so you have dual voltage available at full kVA but if you wants only 120 V and full kVA available you must check the winding connections, if actually, the winding is connected in series then you can reconnect the windings in parallel for getting 120 V and full kVA. Just note the current will be the double 240 V current so you will need leads with at least the double size of the originals.
Best Regards
Petronila
RE: Convert generator output to 120vac
RE: Convert generator output to 120vac
I believe there might be a way to connect the actual AVR to 120 V only, as you said changing the jumper. Try!!
You can also buy a dgeneriuc AVR that will works for arange of 120-240 V, there are a lot of them in the market.
What the generatorĀ“s manual and nameplate parameters said?