Hi,
We are commissioning a 2000 k VA generator and the current on each phase is balanced. There are four single cores cables per phase but the current on each core is not balanced at all. The cables are run in trefoil. What could be the cause?
Thanks
Guardiano

RE: Aternator current

Check your connections on your cables. A bad connection can cause this, also a bad cable is possible.
If you are using a clamp on to measure this that can be fooled by being too close to an adjoining phase wire.
Check the stupid things first, then proceed to the less likely causes.

RE: Aternator current

(OP)
Thanks Cranky108. The current reading is OK as the cable drawing the higher current is hotter.

RE: Aternator current

I'd also suspect a bad, high-resistance termination as already mentioned. Cable lengths should be approximately equal. The shorter the cables the greater the impact of cable length on division of current. A low-resistance ohmmeter can be used to check cable circuits to find differences in end-to-end resistance.

RE: Aternator current

(OP)
All the cables enter through a steel gland plate. We checked for loose connections but could not find one. Could Eddy current be the cause of the current unbalance? The steel gland plate is quite hot.
Guardiano

RE: Aternator current

How many entry holes in the plate?

RE: Aternator current

Dear Mr. Guardiano (Electrical)(OP)18 Feb 22 14:43
1. "... We are commissioning a 2000 k VA generator and the current on each phase is balanced. There are four single cores cables per phase but the current on each core is not balanced at all. The cables are run in trefoil. What could be the cause?..."

Check that the "trefoil" is arranged [viewed ccw phase sequence] (ABC), (BCA), (BCA) and CAB).

2. "...Could Eddy current be the cause of the current unbalance? The steel gland plate is quite hot..."
When the conductor current say >400A, eddy current heating comes into the picture.
2.1 Proposal:
a) with existing metallic gland plate: cut a thin slot say 0.5 mm between all holes into two semi-circles. Note: the gland plate will be in three pieces with 0.5 mm air gap,
b) replace the existing steel gland plate by [brass, aluminum or stainless steel] material.
Che Kuan Yau (Singapore)

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

Low-Volume Rapid Injection Molding With 3D Printed Molds
Learn methods and guidelines for using stereolithography (SLA) 3D printed molds in the injection molding process to lower costs and lead time. Discover how this hybrid manufacturing process enables on-demand mold fabrication to quickly produce small batches of thermoplastic parts. Download Now
Design for Additive Manufacturing (DfAM)
Examine how the principles of DfAM upend many of the long-standing rules around manufacturability - allowing engineers and designers to place a part’s function at the center of their design considerations. Download Now
Taking Control of Engineering Documents
This ebook covers tips for creating and managing workflows, security best practices and protection of intellectual property, Cloud vs. on-premise software solutions, CAD file management, compliance, and more. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close