Chilled water evaporative cooling?
Chilled water evaporative cooling?
(OP)
I live in a reasonably dry location in South Australia, where evaporative cooling is quite adequate for comfort cooling for 75% of the cooling season. In periods of high occupancy or the occasional high ambient humidity (which usually occurs when the ambient db is not at its maximum) the evap cycle is inadequate.
The psychrometrics indicate that if I pipe chilled water through the evap coolers, I should achieve latent as well as sensible cooling. Further more if I pipe heating water through the media, I should achieve humidification as well as sensible heating.
Has anyone any practical experience of this issue?
The psychrometrics indicate that if I pipe chilled water through the evap coolers, I should achieve latent as well as sensible cooling. Further more if I pipe heating water through the media, I should achieve humidification as well as sensible heating.
Has anyone any practical experience of this issue?
RE: Chilled water evaporative cooling?
What you are saying about humdification also sound right; I think that the slope shifts in the other direction towards higher humidity and dry bulb (to the right of the wet bulb line).
RE: Chilled water evaporative cooling?
Depends if the temperature of the coil that is cooling the air is bellow the dew point of the air-vapor mixture. If the temperature of the cooling media is less than the dew point, the vapor in the air that is in contact with the cold surface condenses. When the media es colder the drying efect is larger. The drying effect depends on the depth of the cooling coil, the numbers off fins per inch ( both influence the by-pass factor of the evaporator) and also on the TD (Ambient air temperatura-cooling media temperature)
On the other hand when you heat air you make it more higroscopic, that is the reason because you use hot air for drying.