Miami Beach, Champlain Towers South apartment building collapse, Part 16
Miami Beach, Champlain Towers South apartment building collapse, Part 16
(OP)
thread815-484587: Miami Beach, Champlain Towers South apartment building collapse
thread815-484717: Miami Beach, Champlain Towers South apartment building collapse, Part 02
thread815-484915: Miami Beach, Champlain Towers South apartment building collapse, Part 03
thread815-485059: Miami Beach, Champlain Towers South apartment building collapse, Part 04
thread815-485171: Miami Beach, Champlain Towers South apartment building collapse, Part 05
thread815-485223: Miami Beach, Champlain Towers South apartment building collapse, Part 06
thread815-485379: Miami Beach, Champlain Towers South apartment building collapse, Part 07
thread815-485535: Miami Beach, Champlain Towers South apartment building collapse, Part 08
thread815-485637: Miami Beach, Champlain Towers South apartment building collapse, Part 09
thread815-485844: Miami Beach, Champlain Towers South apartment building collapse, Part 10
thread815-486084: Miami Beach, Champlain Towers South apartment building collapse, Part 11
thread815-486593: Miami Beach, Champlain Towers South apartment building collapse, Part 12
thread815-487022: Miami Beach, Champlain Towers South apartment building collapse, Part 13
thread815-488247: Miami Beach, Champlain Towers South apartment building collapse, Part 14
thread815-489644: Miami Beach, Champlain Towers South apartment building collapse, Part 15
Rather than think climate change and the corona virus as science, think of it as the wrath of God. Feel any better?
-Dik
thread815-484717: Miami Beach, Champlain Towers South apartment building collapse, Part 02
thread815-484915: Miami Beach, Champlain Towers South apartment building collapse, Part 03
thread815-485059: Miami Beach, Champlain Towers South apartment building collapse, Part 04
thread815-485171: Miami Beach, Champlain Towers South apartment building collapse, Part 05
thread815-485223: Miami Beach, Champlain Towers South apartment building collapse, Part 06
thread815-485379: Miami Beach, Champlain Towers South apartment building collapse, Part 07
thread815-485535: Miami Beach, Champlain Towers South apartment building collapse, Part 08
thread815-485637: Miami Beach, Champlain Towers South apartment building collapse, Part 09
thread815-485844: Miami Beach, Champlain Towers South apartment building collapse, Part 10
thread815-486084: Miami Beach, Champlain Towers South apartment building collapse, Part 11
thread815-486593: Miami Beach, Champlain Towers South apartment building collapse, Part 12
thread815-487022: Miami Beach, Champlain Towers South apartment building collapse, Part 13
thread815-488247: Miami Beach, Champlain Towers South apartment building collapse, Part 14
thread815-489644: Miami Beach, Champlain Towers South apartment building collapse, Part 15
Rather than think climate change and the corona virus as science, think of it as the wrath of God. Feel any better?
-Dik
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Here is the image of liquid rust I had in mind:
It is possible to see the liquid dripping from the PVC drain in this excellent video by our friend Jeff:
Link
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Edit: Someone watched one too many flex seal commercials. Anyway sealing threaded pvc fittings is not always as simple as it should be. Too much tape and they crack. Where is the documentation that shows these drain pipes were ordered to be installed to drain onto the floor. And how did they decide where they should go? Or did Joe the plumber do it under cover of darkness?
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Agreed, it is disturbing. That is/was a junction box. If you watch the video you will see there is a bucket below to catch the runoff.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
After more looking and comparing I think what see jutting from the wall is circled below in a different view. And what you see as the slab is a diagonal crack going up the wall. And it looks like the wall is partially collapsed here. Well that would be something.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
There was a conduit that ran along the wall feeding the light on the corner of the 8-foot wall and possibly also the water cooler at the corner of the pool deck. I'm sure that is what that diagonal line is.
Thanks zebraso
I see the lump sticking out, that appears to align with the hole in the CMU wall above. Looking at that 7 news image.
The wall was also cleared.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
I had to enhance your image to see it, but I think it's there.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Thanks, I was thinking that was a possibility. The perspective is pretty tough. Not sure. I agree it looks far away. It looks like it's halfway to the end of the wall but I can't quite say for sure if that's right, because the farther things probably appear not as far as they really are. I think that's correct as to the perspective. It's a bad angle.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Maybe. Maybe not.
I see a LOT of brown goo on top of what looks like a small transformer (not a junction box). I don't see evidence of how it got there from above. Nor do I see how it could have been generated by the POSSIBLE transformer inside.
Please stop "reaching", and come of with real evidence!
spsalso
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Good spot, that pic shows down into the hole much better.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
That post demo damage is farther to the west too. I had to find a photo back about 6 threads ago. It more than 2 cmu faux columns down from the still standing wall. So there is no deformation in the area of interest that would suggest a wall collapse. On a positive note there appears to be no tar buggy in that hole either.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
I'm pretty sure it was a chemical reaction between the salty water and the carbon steel box.
FeCl2 + H2O -> FeO + 2HCl
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
It is most likely a transformer deferring to electrical. Transformer boxes can have cooling vent holes in the top. So they might have covered those holes to keep the dripping water from entering. Did they use a brown garbage can lid? Maybe. That's code right?
And the stains on the white bucket are reddish brown.
Edit: closer look at video and it look like a rectangular enclosure that may have ventilation holes under a drip edge. The spots with water running down may be bridges created by iron oxide deposits to the drip edge. (Lot of conjecture). Probably designed for damp environments. NEC?
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
https://www.corrosionpedia.com/2/2017/corrosion/in...
A black swan to a turkey is a white swan to the butcher.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
The competitor/comedian in me says don't, quit your day job.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
I think it most likely that it was supplying low voltage (12 or 24 V) for something, but there isn't enough field of view to puzzle that out.
IF the water-stuff dripping down was leaking from a planter, then MAYBE that transformer was supplying low voltage lighting in it. Alternately, it could have been supplying power for a low-voltage irrigation system for the planter.
spsalso
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
I think the label shows 120 and 240 connections. It says for voltage X on lines... connect secondary.... (something like that)
From the catalog these are general purpose transformers and they come in several different versions for different voltage standards. The they are resin encapsulated (potted). So that is the thermal management (no air flow needed). Oh yeah this might be to convert 208 to 120/240 If you could read the original label then we would know. But I don't think these are low voltage.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
I agree, that transformer looks close. The top certainly looks closer than the 1416 series, but the item in the video doesn't appear to have a screw, or screw hole, at the bottom, dimples on the sides or flanges for wall mounting. And there is another box behind the rusty enclosure in the video.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
[img https://res.cloudinary.com/engineering-com/image/u...]
When you hold the camera that close you can't see the flanges. More pics here:Link
The bottom is two pieces held on with three rusty screws. Dimples may have been added as a design change for the newer model year. Now, imagine the bottom access cover filling with water, rusting the corner you pointed out, and the one screw that holds that part of the cover on, allowing it to fall off. Or imagine anything you like. I'm not the one trying to sell a story. And I don't care who believes me when I'm not under oath.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
I think there is a possible explanation here, with hydrochloric or muriatic acid (muriatic meaning "pertaining to brine or salt") being the main concern:
As has been noted above, the effect of Cl- ions on CS corrosion mechanisms has been much less
widely studied than the effect of SO2. A high Cl- concentration in the aqueous adlayer on the metal
and high moisture retention in very deteriorated areas of the rust give rise to the formation of ferrous
chloride (FeCl2), which hydrolyses the water:
FeCl2 + H2O -> FeO + 2HCl, (8)
Notably raising the acidity of the electrolyte. In this situation the cathodic reaction (3) becomes
important, accelerating the corrosion process. The anolyte on the steel surface and in the pits that
have formed becomes saturated (or close to saturation) with the highly acidic FeCl2 solution. Both
the metallic cations and hydrogen ions require neutralisation, which occurs by the entry of Cl- ions,
but this leads to an increase in the Cl- concentration which intensifies metal dissolution, giving rise
in turn to the entry of more Cl-, which further intensifies the corrosion process. This attack
mechanism is fed by the corrosion products themselves (feedback mechanism), and it is sometimes
referred to as “autocatalytic"
The complete document is available here: Link
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
https://www.youtube.com/watch?v=YZFzVlpPSyg
Rather than think climate change and the corona virus as science, think of it as the wrath of God. Feel any better?
-Dik
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Rather than think climate change and the corona virus as science, think of it as the wrath of God. Feel any better?
-Dik
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
@Dik,
Thanks. In addition to the HCl here are a couple of details that caught my eye:
p8
The concentration of marine aerosol decreases with altitude.
Marine aerosol is comprised of fine particles suspended in the air (jet drops, film drops, brine
drops and sea-salt particles), solid or liquid, whose sizes vary from a few angstroms to several
hundred microns in diameter
p9
In Figure 4, Morcillo et al. note that the wind only needs to blow short time at speeds above 3 m/s in
directions with high entrainment of marine aerosol (they call them “saline winds”) for atmospheric
salinity to reach important values
[average wind speed at Surfside is above 10mph (4.47m/s)
https://weatherspark.com/y/18654/Average-Weather-i...
p13
The influence of the distance from the sea is one of the most important aspects of MAC [marine atmospheric corrosion] in coastal
areas. Empirically, it is known that the effect of the marine atmosphere
Unfortunately, CTS had a few design features that exacerbated these conditions.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
"The equipment space mentioned in 110.26(E) pertains to specific electrical equipment. All switchboards, switchgear, panelboards and motor control centers shall be located in dedicated spaces and protected from damage. Dedicated equipment space is not required for all types of electrical equipment, just those mentioned above. While there is nothing wrong with having dedicated space for equipment such as safety switches (disconnects), motor controllers (starters), meter socket enclosures, and transformers, it is not required".
Unfortunately, the NEC rules for dedicated equipment does not apply to transformers.
This is a good example of building codes being a minimum standard that we can and should exceed.
While it would have been good practice to provide a drip pan or a simple deflector, it does not a appear to be a code violation.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
If someone decides they need to pee on it, that might turn out to be an unfortunate decision.
spsalso
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
I can't find evidence of a "stay".
On the right side of the transformer, there is attached an unpainted section of flexible metal conduit (flex). It appears to be attached to the bottom side of the transformer with a 90 degree connector. I see no evidence that it is not secured to the box.
On the left, which I will presume is the low voltage output, appears to be some sort of white (painted?) piping assembly. It is attached to the transformer using some sort of tight radius 90 degree connector.
It is poor quality video.
spsalso
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
I just listened again and I think what he says is "clipped into place". It's a one hole strap.
It looks like the flex was damaged and got replaced but the new one was too short and didn't reach the strap. The connector is NOT considered support.
On the left is typical non-metallic liquid tight conduit and 90° connector. I'll bet they forgot the ground wire too.
348.30 (a), FMC (flexible metal conduit) shall be securely fastened in place by an approved means within 300 mm (12 in.) of each box, cabinet, conduit body, or other conduit termination and shall be supported and secured at intervals not to exceed 1.4 m (41/2 ft). Where used, cable ties shall be listed and be identified for securement and support.
So yeah, typical "handyman" poor workmanship.
Jeff was also way off on the location. There is no corner parking spot in the area he was pointing to.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Your comments got me looking again at the video, and I have now seen the strap. That implies that an earlier installer was much more competent than the final one.
I do wonder how it came about that the flex needed replacement. Usually it's the transformer than needs replacement, and you re-use the flex--just swing it out of the way, to the right.
So, where in the garage would there be a need for a small transformer, and also be near a pipe that might leak some sort of liquid? Certainly the walls weren't covered with such pipes (or transformers). And the pipe WAS located at a wall, though it could have done other things in the unexamined area higher up.
I still think this transformer was providing low voltage for something related to the planters.
spsalso
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Doesn't make much sense to assume most electrical stuff would be centrally located to me. No logic to his train of thought. Especially when we know the main electrical room was in the North-West corner.
8.3 amps @ 120v is plenty of power for an automatic lawn sprinkler system. Nothing but timers and solenoids in those older systems. They often ran 3/4" white PVC distribution lines too. What does that "T" look like to you? A solenoid perhaps?
Only one place with a corner parking spot that I see on the drawings. North-East corner.
208v 20 amp three phase power for the exhaust fan in that same corner would leave plenty of excess current to feed that transformer. Perfect location for a sprinkler system for that nicely landscaped BBQ area to the East of the building.
All speculation of course.
https://res.cloudinary.com/engineering-com/image/upload/v1644871599/tips/APTOPIX_Building_Collapse_Miami_53686_sq37ov.webp
Edit: Another pic... Flex, wires and some boxes but no pipes or transformer.
The same water issue that rusted the transformer would destroy the flex as well, but flex is cheap and that transformer is over $500. Maintenance man could replace the flex but may not want to tackle a transformer.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Interesting possibility. So then the transformer and plumbing could be associated. That could be a simple explanation for some things that otherwise look bizarre. I could figure out more reaching around there in the dark than I get from that video. Which cable looks like the primary/secondary? If the secondary were on the right it would make some sense feeding up to a solenoid or controller. Since there is a junction box to the left it might be going there. I assumed the secondary was on the left but could be wrong.
Edit: I had not seen your photo yet. Wow. Transformer could have been knocked off the wall. Not as protected by overhang.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
spsalso
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Ummm... No idea. Transformer and plumbing could be related, or it could be a condensate line. But I can't think of why they would have anything with a condensate drain in that area. Any other kind of drain should be larger unless it was engineered by the maintenance guy.
All the old conduits didn't survive site cleanup so there is nothing to follow to try and understand what the intent was. There is no way of guessing how many changes were made or why over the years. The only conclusion I have is that the average person has no clue how to take a decent video. Closeups don't show the big picture and most people pan way too fast.
Red pipe is likely fire sprinkler, question mark could be exhaust fan inlet but not sure. Grd, no idea.
Edit: red pipe is definitely fire sprinkler. It's Kilsheimers pic #0295 if you want to zoom in yourself.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
NE corner shows an overturned fan in the grassy area.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
He must have missed the .5 seconds that showed the right angle wall (or whatever angle the "corner" is). Are there any other corner parking spots this could be than NE or SW? west of ramp? There were lockers in the SW corner right? Assuming NE the rust stains were blasted with the paint. none of these corners would have water running out to the from a leaky pool deck. Just saying that dripping water must just be a thing there that is ignored/tolerated.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Both West corners are rounded. Other East corner has the pool.
West of ramp is the only other possible location I see but without better as-built drawings I can't rule it in or out 100%.
Video from CTN show it wide open under the ramp with the generator fuel tank and transformer oil tank located there.
Morabito's drawings show a maintenance area under the ramp at CTS but there is not enough detail to know if it's enclosed or not. So I can't rule out West of ramp, yet.
Not sure if it really matters either way.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Yes, there is an exhaust fan in that "rounded corner" also. It is the South-West corner.
That big thing on the wall I believe is an access port where the natural gas connection for the new generator would have been if the 40 year rehab thing happened.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
I am leaning towards apace 82. I don't see that small step curb at the perimeter.
Edit: except there is no wall in front of 82. Are we sure that transformer is in CTS? lol.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Edit: If I am not mistaken this catch panel is under the front driveway and the room on the other side of the wall is under landscaping. So this is not related to the collapse, other than to say well there were leaks the front also. But that was already commented on by Ostroff when he voice tracked the walkthrough I believe referring to where water was found on the floor. If anything I can't quite figure why there is much water coming in from the from front drive because it has cover. Or am I all wet? Is irrigation water running onto the drive?
Edit2: Ostroff noted the catch pan also and the water below it. I just happened to notice there was a wall beside space 107 which makes it fit the transformer video. It doesn't prove the audi in the transformer video was in spot 107. And I can't really see how the things in that video are on the wall in the walkthrough video, because there are no facility connections coming down the wall that I can see. So it's probably not there. I'm not saying that it's there.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Thanks for all the effort in tracking this down.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
"Marine concrete" is all concrete that will be in contact with
seawater or brackish water, tidal variations, splash, or spray from
water in navigable waterways. Piles driven on land that extend below
the water table that contains saltwater or brackish water shall be
designed as marine concrete. Components of a marine structure that
are permanently buried in soil shall be considered marine concrete.
In addition, structures may need to be designed using these criteria
even though they are not adjacent to the waterfront. For example,
structures located several hundred yards from the waterfront often
deteriorate prematurely due to salt spray and salt fog brought to the
structure by prevailing winds. An assessment of existing structures
near the construction site can be an excellent indicator for the
Engineer of Record and Owner to decide if the proposed structure
should follow the guidelines for marine concrete.
From here: Link
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
@dik, I was wondering whether sulfates would really be an issue in Surfside with that fresh sea breeze.
https://www.transportenvironment.org/discover/crui...
https://www.wlrn.org/news/2021-02-03/at-portmiami-...
https://archive.ph/puSt9
"Luckily, the dangerous fumes that can cause serious illness are largely blown away [where?] by Miami’s famous ocean breezes."
But the results for SO2 results for L086-0019 look low even in 2019 & 2020 before COVID.
https://floridadep.gov/air/air-monitoring/content/...
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
IanCA, thanks, and you still can, if you want to open it on a desktop or laptop computer. I could not open link on my phone. I felt it was 'Out of Phase' with current topic, and just raising the noise floor of current discussions.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
IanCA, I realize this question was for dik, but I have some thoughts for consideration.
We know from core samples that the interior portion of the structural slab was the part that looked powdery like gypsum. In addition, we know from Morabito's Mechanical Engineer inspection, at least two exhaust fans needed repair (belts and bearings).
I annotated in thread 15 on Morabito's Drawings where the 4 exhaust fans were located. The only air intake I see on plans for exhaust fans is thru the entrance gate to the parking garage.
If you look at the location of fresh air intake from garage gate source to the 4 exhaust fan locations, that results in a stagnant air flow area at South wall from around pool room doors on east side, and along south wall towards the west, where slab to wall connection appears to have failed first.
There is a pool room exhaust fan that is ducted from pool room to planter above structural garage roof deck. The only air intake for that exhaust fan appears to be either a gap between the pool and the East retaining wall, or perhaps a louver in pool room doors to pull air into pool room. This exhaust system is separate in function from the other 4 exhaust fans.
What about auto tail pipe emissions in parking garage and sulfates like sulfuric acid? I believe diesels produce more sulfuric acid at tail pipe than gasoline engines.
We know there was Great water source on top of garage ceiling structural slab.
Point is could the interior change of state concrete layer be due to tail pipe emissions and poor exhaust fan layout and maintenance such that a lot of tail pipe emissions were staying in garage for extended periods to react with interior layer of concrete?
Could we have multiple things going on as far as acid and base reactions at different locations?
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
From the electrical drawing, the only thing in that corner is a three-phase exhaust fan. It is called 3600W in one location and 2HP in another. It is fed by a three-pole 20A circuit breaker. Aside from the ceiling lighting, there was nothing else there on the plans.
The only reason I can think of for a transformer at all is to, uh, transform. Thus, whoever installed that transformer did NOT need 208 three-phase, but something else. It is common not to run a neutral in a circuit designed only for a three-phase load, so that means there was no source for 120V at that location (other than the nearby lighting circuit!).
So, yes, they could have wanted 12/24V. Or they could have wanted 120V.
I will point out that there was a surface mounted 4" square box, to its left, with a blank cover. And a pipe leaves vertically from that box.
Up above this location was a patio/planting area. In examining the plans, I found no indication that an automatic irrigation system was planned or installed. What with that leak, and this transformer where there wasn't one on the plan, I'm still inclined to think we are looking at parts of an added on irrigation system for the garden area above. The leak may have been from the piping system itself, or a failure in the controls that dumped too much water into the planting area, from which it then leaked by a convenient route.
It's a real reach to blame the brown stuff (probably rust, but not for sure) on the pool, or the pool deck membrane, or exposure to salt water or sea air.
spsalso
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Agreed, I came to the same conclusion and based on the information presented in my post on 14 Feb 22 00:34 we know "The concentration of marine aerosol decreases with altitude." or phrased another way we know the concentration of marine aerosols is highest at ground level.
Agreed and I understand that HVAC best practices dictate a negative static pressure in pool equipment rooms adjacent to occupied spaces to ensure that air is drawn, with added vehicle exhaust fumes, from the garage space occupied by residents while parking their vehicles, into the pool equipment room, rather than vice versa.
The warmed exhaust air from the pool equipment room is then vented upwind (relative to the prevailing wind direction) from the planter at the edge of the parking deck.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Thanks very much for your detailed and systematic evaluation of that condition.
If it's not rust, or some similar iron-based corrosion product, how do you explain the hole in the corner of the enclosure?
I'm simply trying to establish that some corrosive liquid was present in the structure. I will go on to propose what I consider likely sources, I welcome you making alternative suggestions or disproving my suggestions.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Maybe the hole, if that's what it is, was caused by something other than the brown stuff.
If it's rust, and the flex was replaced because it was horribly damaged by rust, how did that happen? Could this collection of crap be related to anything other than an irrigation setup? If so, what?
If it's related to irrigation, then I'm assuming there was a long term water problem that happened right above, either a few inches or a few feet. And repairs were, uh, not wonderfully done.
So this establishes the abilities of Maintenance Man, but it doesn't tie in very well to a building falling down; said falling happening on the other side of said building.
Einstein: "Spooky action at a distance."
spsalso
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
I found a total of six fans with enough capacity for six air changes per hour. Many fans I've seen have two belts so if one is damaged or missing it will still function at a reduced capacity. There should be somewhere you could look up how many cfm of vehicle exhaust to expect from a 120 space parking deck. Then you would have to estimate what the concentration of corrosive contaminants would be. Seems like this might be a problem in every other parking garage there is. Is this one somehow different from all the rest?
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
That is a dry transformer. It has no oil to leak out. They are embedded in epoxy resin.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
HaHa! Yes Fans again! I found six (6) as well in garage. Storage Room, Pool Room, and Four (4) for garage parking area.
I liked IanCA's point about the pool exhaust fan was exhausting into the prevailing wind. It is a 1/4 HP 1945 CFM fan that is competing against Four (4) Two(2) HP 12000 CFM fans, and one 1/2 HP 4000 CFM fan for air intake from their shared parking garage gate area. So 52000 CFM fans and their little brother at 1945 CFM, and little brother has the static pressure of duct work to overcome as well.
I wonder how much negative static pressure that 1/4 HP motor is gonna pull on pool equipment room against the 5 other much larger fans? Especially with the 1/4" exhaust having to over come prevailing winds?
And who wants to bet the pool equipment room doors are not always shut?
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
I'd like to see the math on how much static pressure those fans create with that huge hole at the ramp being wide open. Must be like dividing by zero.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
You make a great point on static pressure.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
The aerial drift of salt-laden water droplets that are deposited on trees and shrubs causes salt spray damage. When droplets evaporate, the salt’s sodium and chlorine ions can penetrate stems, buds and leaves, causing direct damage.
Maintaining appropriate soil fertility and moisture conditions to reduce additional stresses, and to help combat desiccation.
Leaching the soil with thorough irrigation after salt exposure. Flush salt through the soil by applying 2 inches of water over a 2-3 hour period, stopping if runoff occurs. Repeat this treatment three days later if salt levels are still high
https://www.urbanforestry.frec.vt.edu/STREETS/docu...
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
One of the main reasons I'm working on this is because I want to help discover, and share, all of the potential engineering risk factors involved with this incident. Would you be interested in starting a new spreadsheet that we could use to document the potential risks? The items on the list may not have been directly or indirectly involved with, or responsible for, the collapse, but they could be important for helping to avoid future incidents for other structures.
For example, I am thinking about topics such as concrete cover over rebar, column load rating, spans, marine exposure, thermal expansion, waterproofing, maintenance. I think there is a long list that many of the members here have good knowledge of and it would be helpful to have them organized in one place.
I am familiar with your CTS collapse spreadsheet posted 25 Jul 21 17:20, but I suspect that is difficult to contribute to because it may require the explanation of multiple complex factors, but the individual risks can be considered independently and may be easier to agree upon. The headings could be: risk factor, evidence, conditions, category, identification & monitoring methods, proposed mitigation.
What do you think?
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
For example here is the flex that is feeding the fan in SW corner. It is running up from low on the wall. And yet again there is a drip tray running over to the wall so the water can track the cable to it's source. If the transformer video image was mirrored this could be the spot but it's not because the escutcheons on the care are correct. So I guess one just has to imagine this in the NE corner. But that would mean water is on the floor there as well. One question is if this fan is 3 phase does, it make sense that the cable would be coming from down on the wall. For example it would not need a transformer. per se. But is it a wet location thing to use one for isolation? Just more dumb questions.
Edit: I just realized that where the flex disappears a bit up high, that three phases could be going to the fan and one phase down to another mystery transformer. There is always a piece missing.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
It seems extremely unlikely that that is flex, anyway. IF it's supplying the fan, it would have been installed by AT LEAST a drug-crazed apprentice, who would have used conduit. 'Cause it's already straight. And easier to pull. And you don't HAVE to pull a ground wire.
I think it more likely that it's a half-assed water line, used for my latest hobby-horse, planter irrigation. There's an isolated planting area just above.
As I mentioned earlier, you can't use one phase of 208 3-phase without a neutral. And there aren't too many electricians who throw in a free neutral when they're supplying a 3-phase motor. I have, but then I'm a thoughtful and considerate guy.
spsalso
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
If you use 1 phase of 208 with a neutral it would be 120 right? What your saying is you have to run another line with a neutral. And a free neutral would be an "illegal" ground. How would you get 208 to a transformer and why would anyone do that if they could just run 120 separately?
Edit: I realize 208 is 120*3^(1/2) and where that comes from.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Yes
"What your saying is you have to run another line with a neutral."
I am saying, minimally, you have to add a neutral wire. Whether or not you have to run another hot ("another line") can be a matter for discussion. But without a neutral, you don't have any 120V.
"And a free neutral would be an "illegal" ground."
I'm not sure what a "free" neutral is. It is VERY BAD FORM to use the ground as a neutral. Only Maintenance Man's younger brother would do that, which is why he is only hired for summer work installing insulation in attics.
"How would you get 208 to a transformer and why would anyone do that if they could just run 120 separately?"
If you've got 208 three phase at a location, you can use TWO of those wires, which gives you single phase 208. A transformer can then be used to step it down to 120V. (Or 24V. Or 12V.) What it does NOT give you is a grounded neutral. The reason why one might do this transformer thing is that you have ONLY 3 phase at your work location and it is a long way over to a source of 120V. With that transformer, now you do--pretty much what happened in our brown-topped example in Florida.
I'm not too interested in exploring possible code violations when some DOES do the above. I'm talking more about physical reality.
If I was a building inspector and found such a thing, I might let it pass for a light duty "control system" or something. Maybe. If it didn't look dangerous. Perhaps.
When I do typical industrial stuff, I do separate systems for the three phase and the single phase. I don't mix them. I DON'T do that thing above. If I need 120V, I take it off of the single phase 240V/120V system. And I do that even if I'm doing 240V three phase. I DO tend to run a neutral with the three phase, because once in a great while, someone will buy new equipment that includes some little bit of 120V. It's happened. Once or twice.
spsalso
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
This building didn't even have a 240v/120v system.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Wait, what? So there is no neutral in the building back to the wye? I think I see how that would work.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
I didn't say that. Every 120v circuit in this building has a neutral that goes back to the wye.
Edit: here's a hint, 120/240 volt systems don't have a wye.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
edit: i.e. there is no dedicated 240/120 entrance. Slight vernacular problem on my end.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Nowhere did I say THIS building had a 240/120V option.
In my last paragraph, you will notice I used the term "...typical industrial stuff,...". THAT would not apply to THIS building. "Typical industrial stuff" is usually 240V Delta (or 480V, etc), and DOES usually have 240/120V single phase available.
zebraso,
In THIS building, there are three hot wires and one neutral. Across any two hot wires is 208V single phase. Across any single hot wire and neutral is 120V single phase. Most of the heating devices in the building used the 208V single phase. These would be electric ranges and dryers, especially. There was also 3 phase power, integrally included, which needs to use ALL the hots (and no neutral). This could, and did, supply various motors throughout the building. It could also supply "non-residential" heating systems, but I don't think there were any.
What is neat about the above system is that, not only do you get three phase, but the supply is fully symmetrical. When you wire stacks of apartment units, or you alternate floors, you just keep going 123123123123...
What you DON'T get is 240V single phase. The OTHER style of three phase WILL give you 240V single phase, but on only two of the three wires.
Anyway. It ain't easy to get it all first time out. But it DOES make sense. Generally, 208V three phase is used in large apartment buildings, and 240V three phase is used in industrial buildings.
spsalso
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
I apologize for misunderstanding you.
I'm also fully aware of "Typical industrial stuff" and their voltages.
We have a reactor cooling pump motor replacement coming up this outage and need more workers if you're interested. It's only 6000hp and 12.5kv. It might be too small of a project for you though.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
What happened to the old one, that it needs replacing?
spsalso
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Thanks, I wouldn't be asking stupid question if I had the prints in front of me. I know you guys have looked at it.
There used to be a small industrial manufacturing out building across the street from me. They had 3 phase 240 (a+b) going in there from the same lines that fed the residential blocks and same sized center tap pole transformers as residential. What I have to absorb is that is not 3 phase 208 (the difference). They had some equipment related to textile industries that go back to the mid 20th century. But then again it was an outbuilding. The main buildings had a different feed and was about 100 yards away. One of those transformers also fed the street lights. A lot of context. Anyway, thanks for the edumucation.
Edit: Other than that I understand there is no A/B until the center tap comes into it. So the single phase street lights were returned to neutral/center tap. and 240 three phase went into the building. That would have to be delta also. but I never looked that close.
Edit2: And funny I once worked in a coil/transformer shop in engineering. A long time ago. Not a lot of 3 phase but doesn't mean I recall all the theory either. Forgive my stupidity. Small shop = many hats.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
It's fun work and a lot of interesting things to learn about. Each unit gets refueled around every 18 months, usually in the spring or fall when power demands are low.
DC Cook has two units with four pump motors each that are on a ten year replacement schedule. We keep a spare motor in the plant in case it's needed for a total of nine motors. We replace one motor each outage with the spare and send the old one out to be rebuilt. When it comes back it goes on the spare motor stand until the next outage. When they have all been changed we get a couple outages that we don't need to do it but then it starts all over again.
There is a lot of other work that needs to get done at each outage. A lot of testing of systems that can't be tested when it's running. They test the thickness of steam generator and condenser tubes and other safety related systems. That sort of thing. Usually six twelve hour days for four or five weeks. Some plants use only union workers and some use non-union. There is a background check and psych evaluation. Nothing too hard to get through. Search the web for your nearest plant or do some traveling. I've worked at five different plants from Iowa to Pennsylvania.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
I got no idea what you are trying to describe but it could be 120/240 open delta. It only needs two transformers on the pole and can be up-rated by adding another transformer. The power company can usually supply whatever type of power system the customer asks for depending on their needs. Not all industrial customers have the same needs. I've worked in General Motors plants that have their own sub-stations and 13,800 volts running through the plant.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Interesting for sure! It's fun to hear about other people's work.
I assume that there is only bearing wear on a motor. I suppose other things could be checked, of course, like insulation resistance. I asked because I've assumed that big stationary motors under relatively smooth or continuous loads don't have bearing wear. Bearing lubrication and its pressure can be nicely controlled, I would think.
spsalso
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
I worked in a plant that had to test a switch tube that operated at 100kv at a pretty high current. I think that was used in a microwave grain dryer. Lot's of x-rays with that tube. There was a substation in that plant too. Luckily I did not have to work around that tube. That guy was pretty nervous most of the time.
IOW all 3 kv lines (ABC) transformed and feeding building. Nothing special other that they also took a 120 from one of the transformers.
Edit: so it was closed delta. I put out a lot of jibber jabber. The main thing I was coming to grips with is 208 comes from a Wye connected setup. I had no good reason to throw in the stuff about what is a standard delta 240.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
LOL. 20 years ago I heard that nuclear power plants make a million dollars a day for each unit. It's probably more now. They really don't like down time not to mention the safety concern if one fails unexpectedly. One developed an oil leak a few years ago and they had to pump in many gallons of oil while it was running. There is no comparison between the complexity of these motors and the operating conditions they run in with the typical exhaust fan motor. They have air coolers to cool the air that cools the motor because of the ambient heat inside containment. The standby motor needs power continuously running through the windings to keep them warm to keep them from absorbing moisture out of the air. So yeah, every component that could possibly fail and result in down time gets checked over and replaced if it will keep the lights on. It is an interesting place.
Link
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Just to derail things even more, a 120/240 delta is also called a wild leg system and has 208 volts from the wild leg to the neutral. But they don't make any equipment that uses it so...
A 120/240 three phase panel that is only feeding single phase loads will have two breakers and a space, then two breakers and a space etc, because the space is the wild leg and is useless.
Google "mercury arc rectifier" and see if anything looks familiar.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Thanks man, Getting derailed is how I make progress.
As far as the mercury arc thing. I think it was more akin to a lighthouse tube. I know there was a large metal cage with a bank of very large capacitors that no one went into and a guy from the utility once was killed in there when he fell off a platform. That's where they got the 100 kv from. You had the tube and the cage. I wish I knew more. I don't know if the switch tube was for turning on and off power to the microwave tube or developing 100KV DC via a doubler etc. They made Klystrons also. But they were only testing the switch tube in this spot beside the cage. It was surrounded by a very thick lead shield for testing. It could have been a rectifier that got you to 100 KV but there was no mercury in it that I heard of. I had to calibrate the meter that measure 100kv (by divider) once in the active system. Strict procedure and the product engineer was nervous just doing that. I never had to get a probe close to the 100 KV that I can recall. But I could be wrong. I don't think the rig I had went up that high. That was a prior life.
Something akin to this: look up S94000E Power Tube 120kv at 90 amps. So megawatt range I would say, anyway. Probably higher than that.
entertainment: Link
That should be right up nukeman alley. They were doing neutral beam stuff where I worked too. I know I said grain dryer, whatever.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
"The all-electric monster pickup weighs 9,063 pounds and, according to new documents filed with the EPA, nearly a third of that is thanks to its battery."
https://www.foxnews.com/auto/the-electric-gmc-humm...
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Edit: this concept seems to go beyond the basic idea of "rising damp" where the water will permeate to a height were the evaporation rate equals the ingress rate. That is true with or without salt. What I think the above theory is saying is that as salt concentration in the concrete increases the rate water coming in will increase as a result. The mechanism for increasing the salt concentration is compounded by evaporation rate. I would like to see the study that shows that. Still looking.
While I am looking I thought this article on capillarity goes a long way. Link It's not about sulfate corrosion/erosion. But it addresses the forces of osmosis, which I think are the basis for the effect I am trying to describe. Interesting quote from article: "The theoretical limit of capillary rise in concrete is about 10 kilometers". Ouch.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
We can then compare our theories with the facts.
It'll be fun!
spsalso
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Interesting thoughts, analysis and link. The ventilaton and circulation fan drying effects on underside of elevated parking/patio structural deck accelerates salt accumulation into lowest layer, in addition to gravity, then salt attracts moisture more.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Thanks for adding that. There was a "but what about the pool deck" thought going on in my mind as well. But I thought I should focus on one concept at a time. I was following a thought process based on the article Maud posted for now. Please feel free to add any additional thoughts about the grade level drawing water based on the idea. The article I posted talks about damage going into wood flooring and members at or above grade level, but that's a different animal. The idea here was the membrane was supposed to do a certain amount of protection. But that seems to not have worked so well.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Sorry I jumped on the ceiling fan air flow drying train of thought on the ceiling of garage.
The fan drying the inside surface of garage walls, seems also to accelerate effects on walls too based upon your and Maud’s post, especially at upper portion of wall.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
It is interesting. The stampcrete fractures look pretty good. I hate to call that "curious", but.....
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Thanks for the entertainment. Out of my comfort bubble but thought provoking.
Sorry Victor, I don't do vectors. I got a phone app for that maths stuff.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
I think the way the stampcrete has come up in sheets demonstrates how it was not bonded to structural deck below and trapping moisture between stampcrete and non waterproofed structural deck. I also feel the way some of the stampcrete is shifted at columns and the major concrete failure cracks in parking deck area near south wall and patio deck junctions, definitely point to the parking deck failure being due to chemical reactions in that area could be a huge factor in that area being initial failure point, near south wall. Couple that with construction vibrations next door, and cyclic loading of parking deck from auto movements and that area is a very stressed area.
I will be first to admit, my chemistry education ended as freshmeat in College, and had long been forgotten except for times where it affects everyday life like the voltaic cell battery in my autos. I remember as a kid my dad storing a 12V auto battery on a concrete pad outside our home and how it ate the paste in the concrete at a rapid rate and left honeycomb of aggregate and voids showing. From that time on, dad burned in my brain to put a wood board under auto battery to protect concrete. He was mechanical engineer so not chemistry major. Concrete patio was under a cover so not a lot of rain getting to it, but perhaps some in blowing rains.
Interesting short read on "Case Studies Show Galvanic CP Effective on Corroded Reinforced Concrete Structures". Interesting to note that repaired areas create a potential difference between old and new areas and basically cause the cancer to spread to new areas around repaired area. Here is quote below form short article:
"Chloride-induced corrosion of reinforcing steel in concrete is a major problem worldwide. Chlorides can be introduced into concrete through deicing chemicals, seawater, soil, or as contaminants in the concrete mix. This can lead to pitting corrosion and concrete deterioration."
"Localized repairs are often performed to address concrete corrosion damage. When a repair is completed, new corrosion sites can form just outside the repaired area and are driven by the residual chloride contamination and the difference in potential between the steel in the chloride- contaminated and chloride-free sections. When incipient anodes form, further repairs will be required. The patch repair process may be repeated several times over the remaining life of the structure."
https://blogs.ampp.org/case-studies-show-galvanic-...
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
"Types of chemical attacks on concrete structures per link"
"Following are the different chemical actions on concrete structures
Sulphate attack
Chloride attack
Alkali aggregate reaction
Carbonation
Acid attack"
"Magnesium sulphate also reacts with hydrated calcium silicate and makes concrete into powdered mass." "Concrete with low water cement ratio is less affected by magnesium sulphate while high water cement ratio concrete is highly affected. Sulphate-resisting Portland cement should be used where sulphates are present in the soil, water or atmosphere and come into contact with the concrete."
https://theconstructor.org/concrete/chemical-attac...
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Edit: since you mentioned vibrations next door...what if that cracked the non-structure supporting deck just beyond the membrane and that became the primary entry point for water? just throwing spaghetti. Is this where we have to do vector math?
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
I am thinking the after construction aftermarket membrane stopped at pool deck side of planters between parking deck and pool deck. Planters create sag, so water is drained towards planters and ponds there making that already overloaded K-Line even more vulnerable with decaying reinforced concrete, probably construction joint in that area too. Then add vibrations to loosen things up even more, and Shazam!
How is that for some meatballs to go with your spaghetti? I assume vector math has to do with diagonal parking slab failure across a rebar grid, and motion vectors on columns from the vibrator next door?
Personally I am up for linear vector math, but not non-linear equations.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
I don't know. IanCa mentioned in reference to vibrations. One of the things that is missing in terms of another type of timeline is when and how severe the water entry was. Supposedly there was a mention by a worker that pumps were burning out running 24/7 to keep up. When was that? Were they pumping out a sump? When did it first become necessary to put up drip panels and where were they needed first? Who did it? were they approved by someone? Someone know these answers.
Edit: one might assume the pumping was from the drainage wells (not proper term), but would one king tide be accountable for burning out pumps? Too many questions. I can't imagine water from grade is what that was about. I mean at the point where Ostroff made the walk-through analysis I don't know if he was considering the drainage wells. But the question stands was that water on the floor of the garage or not. I still say there are people associated with the building that know these things. And I assume they have been questioned.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Please can you check, assuming they are at the same frequency and in phase?
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
If the three components are aligned in phase and each is 1 unit, the resultant will be sq root (3) units, ie 1.732 units.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Yes of course. Sorry. any distinction there that I may have been trying to insert does not have merit. And whatever I was trying to say should have been stated differently to convey what I meant. That way it could be determined if it had merit. There is no need to rehash that. I never had a bone about it.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Well, as you probably know, a solar flair did apparently contribute to the loss of 40 Starlink satellites launched Feb 3, due to increased drag, but they were a bit higher up. Link
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Once again I don't have the answer but I have a quote regarding the British standard or at least a subset of it:
For continuous vibrations, the British
standard states:
The guide values . . . relate predominately to
transient vibration which does not give rise
to resonance response in structures, and to
low-rise buildings. Where the dynamic loading caused by continuous vibration is such as
to give rise to dynamic magnification due to
resonance . . . then the guide values may need
to be reduced by up to 50%. Note: There are
insufficient cases where continuous vibration
has caused damage to buildings to substantiate
these guide values, but they are based on common practice.
Edit: I have to be careful not to be misleading. For the British standard this still put the threshold for continuous in the 30 hz range at around .8in/sec. BUT it is 1/2 of the USBMRI8507 for the same conditions (with nothing mentioned about resonance), This is different still from the Swiss standard which is about .3 in/sec for continuous at 30 hz for this type of building ("well designed and maintained"- love that). DIN would be .3 in/sec for transient at 30 hz at the base and even lower for continuous but that is at the top of the structure so it's not comparable. The only one that calls out resonance seems to be the British. Don't take my word for it
Link
While that is about historic building preservation it does a really good job of comparing standards, even superimposing them on each other.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
I was looking at a study from Sweden trying to model vibration for sheet pile. They drove 7 piles monitoring 1,2, and 4 while they were all driven in interlocking succession. they have sensors top middle and toe. frequency is 35 hz. Anyway on the 4th pile measured on that pile the top sensor near the end of the drive was hitting around 40 g longitudinal. unless I am mistaken at 35 hz that is 70 ips peak. Is that sort of level going to be attenuated down to .5 in the distance we are talking about?
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Yes - by nearly double in this case. But in the context of a slab or column with clearly defined primary axes, the primary stress axes (which is what you should be measuring) are likely to line up with the geometry. Perhaps this is not the case at the end of the slab where it meets the wall though.
The idea of airflow inside the garage drying the inside of the walls and encouraging salty water to migrate into and through the concrete by capillary action is an interesting one. Surely though if that was something that could happen on this kind of timescale, we'd know about it and there would be rules about waterproofing the outside of sub-grade concrete lined spaces, because otherwise this would apply to every building near the seaside with underground parking.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Oh, certainly, I'll get right on that, Victor, err..vector. Unfortunately my batteries couldn't hold up to the strain but just before it died I was looking for an input value that corresponds to the third order harmonics of the pile driver and some kind of assurance that the frequency and amplitude would remain stable throughout the time period in question and also the modulus of elasticity of the soil type at the site of the alleged damage. I'm currently studying up on the works of the great mathamagician Paul Simon and his thesis: "There Must Be Fifty Ways To Shake Your Tower".
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
I found that to be an interesting and helpful document, thank you. Here are the points that stood out for me:
Fig 2 put 30Hz at 0.5in/sec into the intolerable region.
Internally Amplified measurements can be 4 to 8 times higher than at the base of the building.
52,000 cycles at 30Hz is less than half an hour.
Strains in walls caused by thermal expansion are several times higher than those caused by vibration.
Key factors:
1 - Building type and condition
2 - Continuous vibration
3 - Importance
All structures should be evaluated on their own physical condition.
Applies limit reduction 50% for 1,000 to 100,000 cycles. Applicable to CTS and vibratory sheet pile driving.
60% above 100,000 cycles.
Resonance and preexisting weakness can be problematic.
Stipulation of protocols to be followed if recorded vibrations exceed the specified limits. Were any specified for CTS?
Post-construction condition surveys. Were any done?
Surveys should be repeated after any above-limit vibrations. Were any done?
Elevation surveying for settlement, crack-width measurements, and visual surveys of general building conditions.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
I'm beginning to wonder whether that calculator of yours is real or imaginary. Don't worry AusTony2046 already came up with the answer to my specific question and Red Corona put things into context:
I suspect the vertical component is the critical one.
The most important point for me is that if you pay an expert for professional advice on vibration monitoring, and they give you a limit not to exceed, and your on-site measurements, made in accordance with their recommendations show that you are exceeding that limit, then you need to take action to reduce the vibration or seek advice to understand why the data could be erroneous and you need to check whether there was any adverse effect on the structure.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Because it's possible to gradually inform the skeptics, reducing that percentage, and everyone stands to benefit if we can come to an agreement.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
My calculator is just another tool I use in exchange for proper compensation to support myself. I see no reason to allow it to be used by persons who wish to deny proper compensation to the real victims of this tragedy.
With a grain of salt...
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
You might want to rethink that Inspiring thought, as what came to my mind immediately was Jeffery Epstein?
EDIT: But my elevator does not go to top floor.......
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Personally, I am fully in favor of the real victims receiving proper compensation. As an engineer, I'm also committed to helping to improve our understanding of the risks involved so we can reduce the chances of events like the collapse of CTS happening again in the future.
Thanks for your advice thermopyle2.1.
Reposted with a clarified signature line.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
I must not understand how signature lines work.
I thought I'd need your password to be able to insert my favorite Mythbusters quote in your signature line.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
No need for all that credential nonsense, just make the substitution in your mind.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Suggestion: Just Following the Science!
Edit: I can see the vibration damage being a valid complaint against 87 Park, but I am having trouble with the water entry into the wall due to removal of 87 Terrace. The reason I am having a problem with water entry is that CTS was built all the way to the property line, with no provision to prevent water entry from property line side of wall. Anytime you build all the way to a property line, you are inviting trouble from your neighbor. You can not even paint your retaining wall without getting permission to be on the other person's property.
But then I have always thought Condo's and Townhouses were a stupid concept that can make life painful depending on who your neighbor is.....
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
On one hand 'neighbor' purposely drained towards wall, which is wrong, but when folks build up to line there is no room for U&D easement. And I agree neighbor's should NOT drain water on to their neighbor's
Again, building to line invites problems
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
I concur with the valid points about the street / public right of way and the original drainage.
Is it possible that the removal of 87 Terrace also had some impact on the lateral stability of the CTS property line wall? With respect to thermal expansion of the parking deck & pool deck?
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Interesting thought, as the concrete walk was poured up against wall. Not sure whether poured against concrete wall though. But definitely had a water change due to removal, and yes I guess road way and concrete curb and walk did provide lateral bracing to concrete wall, at least due to compaction of ground under street and walk.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
I concur. I was thinking "terrace" was the old Hotel that was torn down. So the removal.... well that's where I missed that it was the road you were talking about. So not just was the road removed as such but the land was repurposed with no apparent interest in what function it was providing to CTS before or whether it was access or whatever. It just had no priority.
That is a very interesting point. Does this explain why they did not even attempt to fix the water coming it, assuming they knew about it. If this was all understood as a fact before the collapse, why didn't they use the law to address it? This kind of crap is Judge Judy territory. Damage caused by action of neighbor? But because of politics maybe they couldn't? This part really seems to stink and suggest there is more going on that has been told. These are the questions that beggar the imagination. And I believe they are claiming this now as if it was a known fact then.
Edit I now see Morobito attributed about $80K in damage to the privacy wall to 87 Park construction. I don't know is this is just where they scraped it with an excavator or more than that. And he noted the drainage being funneled towards CTS - which is denied by the developers. So there is the pissing match.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
If CTS's real property line was the center of the street it may explain why 87 Park wasn't able to build right up against CTS's sheet piles and why they were required to rebuild a public sidewalk access to the beach on the old easement.
So did only one city own and maintain this street or did they share that? Were both cities required to sign off on the sale of the street? Is the city responsible for the water problems caused by it's sidewalk? Seems like some real murky legal issues need to be resolved before the other blame games can continue.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Did anyone at CTS think it appropriate to get an engineer's opinion on problems they could encounter with the neighboring construction?
If so, what did that engineer say?
If not, why not? Was it considered not important enough?
spsalso
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Is there any chance you could check to see who owns that public sidewalk?
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
From Miami Dade GIS Maps
https://gisweb.miamidade.gov/eMaps/
Here is legal description on 8701 COLLINS AVE CONDO. Looks like 6 lots, part of erosion way and adjustments to Blocks 1 and 10, plus 50 ft road closed. Would need to look at plat books, and deeds cited below to see full details. But it appears City Sold Right of Way of Road from this. Perhaps public access is an easement on property?
ALTOS DEL MAR NO 2 PB 4-162
LOTS 1 THRU 3 INC BLK 1 & LOTS 1
THRU 3 BLK INC BLK 10 & PORT OF
EROSION WAY LYG BETW & ADJ TO
BLKS 1 & 10 PER PB 105-62
& 50FT RD LYG N & ADJ CLOSED
PER RES #2014-28608 & 2014-28839
AS DESC IN DECL 31691-1664
LOT SIZE 101179 SQ FT
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Is that considered good enough for legal work in Florida?
Were all the laws adhered to in the sale of a city street to a private entity?
I seem to remember some of those issues haven't been fully explored in court yet.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
In my state, property lines are typically not the center of streets. In plat mapped residential sub-divisions the street Right of Way is say 50 feet wide, but road is only perhaps 30-35 feet curb to curb. The other 15-20 feet are divided evenly on each side of road and are basically used for utilities. So property lines for lots are typically not at curb of street but 7-10 feet past curbs. So you end up maintaining part of the right of way for the city.
Definitely some shady dealings went down, and I expect it to be interesting legal battle.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
No. I was talking about the WEST edge that runs along Collins Ave. But then your other image shows the property crossing the city limits into Surfside on the North. Not sure how that works. Really doesn't matter, it's not going to get resolved here.
I know if I don't mow that 15-20 feet of lawn along the street, the city will come do it for me and send me a bill.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
I assume the city just has easement on your property, thus you are still the owner and have to cut the grass? I know here, if the lot is vacant, and a complaint is filed the City will cut the right of way grass in front of vacant lot and not charge the land owner, since the land belongs to City. But I do not know what would happen if I quit maintaining the ROW in front of my house for the City. Perhaps they would come cut it too as it is their land, but I am not aware of anyone who has tried not cutting the ROW on a developed lot.
My guess is City would cut it on developed lots too, but it would NOT endear the land owner with the Power Brokers at City Hall?
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
I started from here: Link, zoomed-in and clicked on the location. But it's not as user-friendly.
The GIS version you shared has more features and information, but the land use data is different. It still shows 87 Terrace as a road.
The story I heard was that sale of public roads was not permitted so it was given in exchange for a cash donation.
Looking at Google street view. The width of the sidewalk was approximately doubled when 87 Park was built. The property line aligns closely with the original sidewalk.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
As an engineer. Did you know it was engineers week? I would say that the data available in the public copy of the official record indicates that the beach access path entirely crosses the property referenced by Folio: 02-3202-165-0001, which is abutted immediately to the north by the property previously occupied by CTS and referenced by Folio: 14-2235-025-0001. As such, as far as public records show, there is currently no publicly held land located between Folio: 02-3202-165-0001 and Folio: 14-2235-025-0001.
Good question. I completely agree.
I suspect the Miami Beach council was simply under pressure to maintain public beach access, but from what I can see, they still transferred the entire piece of land previously occupied by 87 Terrace to the owners/developers of 87 Park.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Yes, it seems everyone has a manufactured holiday based on their job title to make them feel good about themselves and forget they are nothing more than a cog in someone else's money machine. When the cogs are worn and out of spec they get tossed in the scrap bin with all the rest of the used up dregs of the world.
There is no children's day because every day is a holiday for children. There is no holiday for retiree's for the same reason. Cogs that are not yet useful and cogs that are no longer useful. And the useful cogs and the machine owners have no use for either one.
If you build your own money machine you will find an ample supply of cogs looking for a place to fit in. If you work the machine too hard, some cogs will break from the stress and some will be ground to a fine powder. But churning out money is the only freedom that they know. Slaves to someone else's empire of greed.
And yet we keep building larger and larger machines. Soon we find Cogswell Cogs and Spacely Sprockets are competing with each other to have the largest money machine ever imagined. Rakes and shovels and implements of destruction to scoop all that money into the largest pile of money that man has ever known.
I have no idea where I was going with this and no idea why you thought a made up holiday was relevant.
Welcome my son. Welcome to the machine.
Is this question rhetorical too?
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Is this creative writing or has a Sparky set up ring and pinion gears in a differential?
What I would like to see if the complete deeds and plat maps posted on line from before current 8701 Collins owner purchased property and tore down existing building, coupled with before and after ROW transfer from City to current 8701 Collins owner, and today's plat maps and deeds.
In my County and City all this information has been digitized and these public records can be accessed on line, rather than the old method of going to county record room to manually research deeds, mortgages, plat map, etc. records. At least ours are digitized back to around 1990 time frame. Beyond that manual look up still required.
I could not find access to actual deeds and plat maps for Miami-Dade on line, where we could see complete legal descriptions of parcel's of land and how title was transferred on these properties over time.
Perhaps someone 'Dangerous' in the South Flordia area has access and would be willing to post this information???
These are public records, and yes you may have to visit the real estate property room to copy the information, if there is not an online digital access in Miami-Dade?
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Perhaps that's why I feel it important to be here.
Maybe I was just testing to see if you were an engineer or a philosopher or both.
Not relevant to this collection of threads, but to the site in general?
Thank you for your profound and thought-provoking response. I tend to agree.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Agreed, that would be very helpful. Let's hope something turns up.
I will soon get back to clarifying the possible sequence of events as I see them with a diagram and some more information. This weekend I hope.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
WOW, I seem to have my very own groupies. Strange days indeed. Most peculiar even.
Maybe I'm not an engineer.
Maybe I'm not a philosopher.
Maybe I'm not some random idiot on the internets.
Like you, I have received training in multiple disciplines. Master of none as they say. But don't sell me short.
When a person is not obsessed with money they are free to pursue whatever their heart desires.
But with some people it's "All About Money". AmIright?
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Trust me, I would never sell you short based upon your post showing an obvious broad background! I was impressed with your Jetson enhanced post and how you knew about gear backlash!
It brought by memories from childhood cartoons coupled with auto rebuilds that most have never even thought about!
You earned another Star!
BTW, I did not know answer to your West sidewalk question, however it could be 87 Park just wanted wider sidewalk in front of their Spaceship 🚀?
Finally, Netflix has a documentary film, ‘Downfall’ explaining how ‘All About Money’ culture change was behind 737 Max MCAS criminal coverup and failure by Boeing, after McDonnell CEO took over joint company. It shows how good engineering culture gets replaced with short term Stock Price focus.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
I look forward to reading your full sequence post.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Precision guess work based on information provided by those of questionable knowledge
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Edit: Perhaps Nukeman will confirm if I understood his question correctly.
Edit 2: I must say I am impressed that you got 2 Stars for answering the question incorrectly! That is impressive.....
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
It's an easement for that vacant lot owned by the Public works that is essentially public beach access. The town sold off the road only, but not the easement or beach access lot. 87 park developers would more than likely have "permission" of some sorts from Miami-Dade to renovate their property so long as it all fell in line with code and permits.
Folio 02-3202-006-0670
Maybe it was nukeman who asked. *shrugs*
Anyway, yeah, sidewalk is owned by Miami-Dade Public Works.
Edit: If gold stars in Kindergarten were this easy to get, I might have gotten somewhere in school.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Thank you.
The public beach access, who owns it and who is responsible for it, was the point I was trying to get clarified. I only mentioned the Collins Ave. sidewalk to point out that the information, as presented, did not seem likely to be accurate.
Miami Dade GIS Maps disclaimer:
Miami-Dade County provides this website as a public service to its residents and visitors. The County is continually editing and updating GIS data to improve positional accuracy and information. No warranties, expressed or implied, are provided for the positional or thematic accuracy of the data herein, its use, or its interpretation. Although it is periodically updated, this information may not reflect the data currently on file at Miami-Dade County and the County assumes no liability either for any errors, omissions, or inaccuracies in the information provided regardless of the cause of such or for any decision made, action taken, or action not taken by the user in reliance upon any information provided herein.
Trick question of the day: How many links does a chain have?
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Demented, Municipalities don't own easements. Easements are NOT ownership in land, but right to use that part of someone else's land. Right of Ways are owned by Municipalities. It appears that West of property line has to be ROW, and East of property line on Collins has to be easement if city is using for utilities and such.
Edit: Or as Nukeman now is saying, the data base is CRAP!
Edit: Nukeman's original cryptic question was concerning only sidewalk along Collins avenue in the question I was referring too. I was NOT talking about Beach Access.
This is a prime example of why this forum is a waste of time for all of us, on this kind of stuff. It is like texting vs talking to someone directly, in that a lot of context is lost.......
PS: Whoever gave you the 2 Stars reminds me of the old saying, "Ignorance is Bliss"......
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Here is a diagram indicating what I believe to the approximate sequence in which elements of the parking deck, pool deck and building support columns failed.
The positions of most of the cracks in zone one are taken directly from photographic evidence, but some are inferred.
With reference to MaudSTL's timeline summary posted on 3 Feb 22 17:50.
I believe the failure of zone one occurred relatively slowly and agrees with timeline item 2 (banging heard from 11PM onwards increasing in intensity) until the southern extremity of the deck detached from the wall. That could coincide with the loud crash described in timeline item 3. I believe that area of concrete was very degraded and could explain the dust.
I believe the collapse of zone two occurred fairly rapidly due to the forces involved as an increasingly larger area of the deck begins to fall. This could likely coincide with the very large crash described in timeline item 5. I have added a letter suffix to indicate the relative time of the collapse. The progression is generally from south to north but the collapse of the eastern region is delayed slightly until it finally reaches the wall at 2E.
I'm interested to hear comments. I can explain the sequence in more detail and I still need to explain why some areas of the structure are exposed to more salt than others.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Good start on graphic depiction. I would suggest adding column labels from original CTS drawings to make discussions of a particular column easy to reference. Perhaps add legend with timeline events to label those on drawing as well. One graphic could tell a lot of story.
I am interested in complete decay theory in Zone 1 causing loss of steel grid or concrete deterioration in that area.
Also interested in your vibration resonances leading up to further delamination and punch shear readiness.
More description of what is happening on time clock at each column or area would also be inciteful.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
I made a small change to my name as a joke and changed it back.
When I used one of Thermopile's aka thermopyle2.1, and Thermobaric's aliases "All About Money" he feigned ignorance.
He created a new account with his old screen name after abandoning his old account under the alias "gonefishing2".
What is he trying to hide with multiple accounts and constant name changes?
I'm not sure what his motives are and I have no reason to accept any explanation he may offer. The same goes for his two friends.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
So I assist in answering your question with true facts, and because you don't like the answer you attack me, and make false accusations rather than simply googling definition's of ROW's and Easements to confirm that what I said is the legal definition of those terms, and you don't even mention your question about property line on West side splitting new wider sidewalk.
Fine, I was done anyways because of the agenda's of some of the folks like Nukeman948 that add no value....
To my apparent two friends, as per Nuke's False Accusations, whoever they may be, I wish you luck if you choose to continue on.......
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Timeline by MaudSTL.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
I would like to see construction joints noted in different color on your graphic, perhaps a dashed yellow line? The one on East is not shown, however it appears the white straight lines that cross at K15 are construction joints?
I have a hard time following flow of progression from 2A. I would like to see notations beyond 1,2,3 A,B,C,D like .column labels thru .column whatever extensions showing progression flow at each involved column. I clearly see spread for example from 1 to 2A, but as to why different pieces fall in sequence beyond that, it is nor clear. I think it takes narrative to go with picture and perhaps photo thumbnails referenced to logic to tell story.
Good work and I hope you continue with your attempt at explaining the puzzle.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Agreed, that would be a good addition, but I'm not sure about the locations of some of those construction joints. Do you know if there is a drawing anywhere showing them, please?
Yes, the narrative is important but it will take me some more time to put it together.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
All I have seen is the construction 🚧 joint section view in the original drawings. I have not noticed locations of joints identified.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
https://www.youtube.com/watch?v=HsUVT5nv2YA
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Nukeman948/Nukedude948's “RULES FOR THEE BUT NOT FOR ME” MINDSET
I guess one could ask why does NukeDUDE948/NukeMAN948 use a unique signature block on all his posts, but then I just consider the source and the answer is clear..........
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
spsalso
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
As far as design architects or even design engineers, Josh Porter, made it clear a pure designer is not qualified nor has the right experience and skill set to perform Milestone Structural Inspections and design Structural repairs. He even went on to say he specializes in the inspection and repair side, and does not feel qualified to design say a new 10 story building.
His point being, Milestone Structural inspections needs to be performed by a qualified engineer specialist, not a pure designer, and conversely.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
(starting at line 195) "For phase one of the milestone inspection, a licensed architect or engineer authorized to practice in this state shall perform a visual examination...and provide a qualitative assessment of the structural conditions of the building"
(line 205) "If the architect or engineer finds no signs of structural distress...phase two of the inspection...is not required."
Mr. Friedman was an architect. He would have been permitted to do phase one of the milestone inspection of CTS. If he found no problems, there would be no need for a more in depth phase two. Since he was probably more familiar with the building than any other architect, it would make sense to choose him to do the job.
For that matter, it looks like Breiterman would also have been "on the list". Another good choice, since Surfside approved of him inspecting his own work, rather than finding someone else.
And we know how good a job Friedman and Breiterman did. I'm sure they would have kept on doing following work to that same standard.
spsalso
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
I just wanted to clarify that 11 PM is the earliest report of banging that we currently have, because that’s what time Chani Nir got home to 111. The banging may have begun before that time, but we have no statement to confirm what time it started. We don’t know, for example, what time Security Guard Shamoka Furman came on duty in the lobby, nor do we know if she was able to hear the banging too. If she was able to hear the banging, it might help us to know what time she began to hear it. If she heard it during her entire shift, then we ought to find out if the guard on duty in the previous shift also heard the banging, and, if so, what time they started hearing it,
I am scheduled to meet this coming week with Dr. Ganapati of FIU, who has joined the NIST team to work with witnesses, among other things. I will do my best to bring to her attention questions like these that would be helpful to get answered.
>>>>>Edit. I think another detail that would be good to know is which space the Vazquezes parked in. They arrived right after the loud crash at 1:10, and it would be good to know their likely line of sight as they walked to the elevator lobby.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Thanks for letting us know. I wish you the best for your meeting.
I'm still trying to find time to work on the collapse sequence narrative and joint details.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
I uploaded the link to the Witness Statement Timeline to NIST on their data portal back on 8/19/2021.
If the active sub-team working out a collapse theory right now feels confident in their theory, it would make sense to share it with NIST, even if you want to use screen names for professional reasons.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Becker, a law firm that represented the building’s condo association, said it would pay $31 million; Morabito Consultants, an engineering firm hired to inspect the building for its 40-year recertification process, said it would pay $16 million; and DeSimone Consulting Engineers, a structural engineering firm for another building nearby, said it would pay $8.55 million under the deal. Sale of the property will also be divided.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
In case it would help, here’s how the Miami Herald infographic House of Cards depicts the construction joints. Dr. Lehman would have reviewed this prior to publication, so it may have been acceptable to her from an engineering perspective.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
We all have a few questions for the suitcase lady from the Justin Willis story if she is ever found. What made her think the building could collapse at any moment?
I am also interested in how long the deck collapse lasted. Witness statements make it hard to tell if it was a single boom or it was a series of loud bangs and rumbling over 5-10 seconds, which would be my guess.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
1. Original story, headlined "The Herald built a computer model to explore how Surfside tower fell. Here’s what it showed" By Dawn E. Lehman and Sarah Blaskey Updated January 12, 2022 4:45 PM -- per Dawn Lehman, "... describes the timeline of the collapse that we used to support the modeling we did."
2. The follow up story, headlined "The last stand of Champlain Towers South. Computer model, witnesses reconstruct the tragedy" By Sarah Blaskey Updated January 21, 2022 2:31 PM -- per Dawn Lehman, "... the modeling approach and different scenarios that we evaluated."
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
I think the Miami Herald infographic is slightly off because it appears to show the joint to the West as a straight line, but I think it actually steps about 2' - 3' further to the West, in the area south of column row 14 (South of the lobby area). This is based on photos that show the joint in the stamp-create aligned with the East face of the columns in row I as shown below:
But the joint in the structural deck appears to be further West than the West face of the columns in row I as shown below:
In order to predict where the joints were in the parking deck and pool deck I looked at the joint spacing in the garage floor slab, because the actual as-built positions can still be observed.
If the garage floor slab joints are overlaid on a drawing of the parking/pool deck they appear as shown below (with parking garage column positions emphasized):
The spacing of those joints can be aligned with features on the parking deck by mirroring the joints and shifting West as shown below:
New version showing regions, due to uncertainty.
The point I am trying to establish is the probability that there was an intermediate construction joint beneath the planter running South to North close to columns on line K, in addition to the two shown on the Miami Herald House of cards infographic.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
All the witness statements I have ever read (Nirs, Furman, and Vasquezes) are clear about hearing the deck collapse as a single, very loud crash rather than a sequence of bangs and rumbling over time. The MH calls it “one loud cascade of concrete” in the article explaining the House of Cards infographic.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
I think we still have to take the MH timeline with a grain of salt, at least until they reveal the witness statements they used as the basis for their timeline.
There are three areas where the MH timeline is at odds with contemporaneous, publicly available witness statements made in the days immediately following the CTS collapse.
The MH claims that banging was heard starting around 1 AM, yet Chani Nir stated at the time that she could hear banging when she got home to 111 at ~11 PM.
Sara Nir, who clearly and repeatedly stated at the time that the “first collapse” (that she thought was a wall collapsing above 111) occurred at 1:10 AM. Yet the MH states that crash occurred at 1:14, which is the time that Sara said she went to the lobby. This means there was a five minute interval between the “first collapse” at 1:10 AM and the deck collapse, which was the “second collapse” at ~1:15 AM.
The MH also claims that witnesses were able to describe the area of the deck collapse. In this article the MH states,”Witnesses described the collapsed region as initiating from the southern perimeter wall and extending to the northern edge of the pool deck, where a video shows the debris from the deck collapse at Column Line 9.1 near the southern edge of the 12-story tower. (That portion of the building was covered with debris after the tower fell and therefore the exact boundary is unknown.)”, which is not accurate. There is not one publicly available witness statement identifying the extent of the deck collapse. Sara Nir, Gabe Nir, and Nico Vazquez only saw the deck collapse after the fact, from the lobby and the porte cochere. The late Cassondra Stratton only saw the deck collapse after the fact from 410, having been awakened by the building shaking. Mike Stratton says she told him she could see the pool (meaning pool deck) had fallen into a sinkhole. Floridians seem to use the words “pool,” “pool deck,” and “parking deck” interchangeably, so the witness statements can be confusing, especially when you take into account that many witnesses are speaking English as a second language.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
A grain of salt or with a liberal dose? I see now that their modeling assumes the slab abutting the south perimeter wall rather than resting upon it. Of course, if that were the case, a catastrophy would be in the making if the connecting rebar corroded. I just can't see this as supported by the photographic evidence nor with standard construction practices.
The media industry pumps out content because that's what it does but I'm dismayed with the lack of quality found in too much of it.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
As far as the Timeline: CTS Collapse Witness Statement is concerned, I get frustrated that the media creates flawed narratives that become accepted as factual. People go through the NYT and MH infographics and think they are looking at proven facts, when what they are really looking at is a combination of fact, fiction, and conjecture.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
This does not inspire much confidence. Those poles are not there to support the balconies IMO. I bet they finally got around to testing the concrete used throughout. This should be a big deal.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
When this collapse occurred everyone said the building "pancaked", although it did collapse straight down for the most part...watching the video and rescue operations, it looked more like the floors just turned to sand, the balconies and columns were the only large chunks/slabs being retrieved by the cranes.
There has to be a problem with the concrete.
Yes, Sym I would be wanting out and selling at a loss to get out of that building.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
After watching Jeff Ostroff's video on shoring poles on the balconies, I noticed they did NOT shore all the way to the ground. This appears to imply that the shoring is just a safety factor while they work on repairing the area above the shoring. I counted 4 floors of shoring and it would appear that implies a balcony slab repair and not column repair.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
So clearly this part of the building is much more robust than the part that collapsed, which has me questioning, even more, why did they need to put the shoring poles there.
So this points more in the direction of they think there are shearing forces along the outside of that wall even though the columns are 16 inches, and they are taking steps to prevent the shearing along that wall, where the patio slab meets the wall at the start of the cantilever.
It seems they suspect weakness at that connection, maybe from lack of adequate rebar there.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
I still dispute the MH contraction of the timeline: Chani Nir’s contemporaneous interviews stated that she heard banging when she got home at 11 PM, but the Miami Herald doesn’t start the timeline until 12:50 PM. Also Sarah Nir’s original interviews stated that the loud bang (which Gabe called the first collapse) occurred at 1:10 AM instead of 1:14 AM, when she went to the lobby.
The MH now says that Sarah Nir was able to see the pool deck had collapsed all the way to the southern perimeter wall. Sarah never made this claim at the time of the collapse. I feel skeptical that Sarah was able to see through the dust and dark at that time, and would like to hear Sarah make that statement herself, rather than hear a reporter make that claim.
Next week, Episode 6 will be Ileana Monteagudo of 611 and the late Cassie Stratton of 410.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
(from the second link below)
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
with the plans:
They've set up a sensationalized detachment scheme that allows a > 1" drop along the perimeter wall as a precollapse stress riser.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
spsalso
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Have to disagree... slabs are poured with monolithic thickened edges, depressed beams, and stem walls all the time. It wouldn't necessarily be my first choice to do it that way, but it can be done without much drama.
Don't feed the troll. We've been down this road before with this guy.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
I agree that certain vertical elements can be placed monolithically with slabs (like thickened edges, etc.), but I would find it very unusual for a basement-type wall to be placed monolithically with an elevated slab.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
These 15 or so threads have been unbearable at most times, nor am I an expert designer, rather a curious one parsing through the crumbs that are out there for us to feed on.
The point I was trying to raise was whether it was constructive to model a vertical shear fracture of the slab at the interior face of the perimeter wall for analysis purposes or how such a structural defect would evolve.
From a structural design standpoint, does the slab diaphragm not offer lateral support to the tower structure and as such require adequate connection to the perimeter vertical elements?
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
I don't think as a group we know for sure that the pool-deck-level slab was a critical structural element from the standpoint of maintaining stability of the building itself, because no one has done the big heap of math needed to figure that out... but based on the pile layout and the detailing at the joint between the perimeter retaining wall and the slab, it appears that one of the following is true:
1) the pool deck level slab was a critical element for maintaining lateral stability, and its failure put the foundation system into an unstable condition (in other words, sawcut out the pool deck slab and the building is now unstable)
2) the pool deck level slab itself was not critical for maintaining stability of the foundation system, BUT the failure of the pool deck put unaccounted for horizontal load into the foundation system through catenary action as the slab came down, and those horizontal loads caused localized failure(s) at the joint between the exterior pool deck level and the perimeter of the actual building, and those horizontal loads and localized failures put the building into an unstable condition (in other words, if you sawcut out the pool deck slab the building is stable, unless you then put some big horizontal loads into the top of the basement columns)
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Yes, I understood your point. In my reply, I was trying to explain how that joint may have been constructed with a cold joint at that location. This isn't necessarily a defect, as cold joints (aka construction joints) with rebar dowels are commonly used in construction. If there were a construction joint at this location, it should be readily determined from an examination of the joint. I remember when the event first occurred, photos (although taken from a distance) seemed to show a clean vertical break at this joint in some locations. It could very well have been a vertical construction joint with steel dowels taking the gravity load.
The ground level slab may have been considered as a brace point for the building columns, but I would expect the columns could still survive if the slab was hypothetically removed from the analysis. But failure of the slab I agree could impose some lateral loading on the columns, which could initiate a collapse. I tend to believe the slab collapse progressed from the property line until it took out that one slender column near the planters, causing one end of a beam to drop and wrench down on one of the main building columns.
I haven't been following closely for a long time and have just been waiting for the investigative report to be published.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Surfside became known for deadly condo collapse. Now the town looks to champion reforms
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
I believe that if the saw cut was made first along the North side of the pool deck, it would isolate the north wing of the building from collapse. Cutting the East, South and West sides of the pool deck / parking deck first would allow columns to punch through and eventually the deck becomes a massive lever, torquing the columns on column line 9.1
I imagine that as columns punched through, the deck is located by them. If the deck is inclined, lower in the south and higher in the North (at the connection with the building) geometry dictates that either the deck must stretch (but it is extremely stiff) or the columns along column line 9.1 are pulled to the south.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
The vibration limits are intended to prevent effectively non-structural damage (stucco etc). According to the quote in the Herald, Wiza was talking about replacing a wall, not stucco. That's the basic problem. It's a damning statement.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
It's a "damning statement" that he is willing to replace a concrete block privacy wall, in order to move his project forward?
That would be a wall that is completely non-structural. And it's my impression that it has mostly not even fallen down. Unaided.
Perhaps he should get a gold star for doing whatever he did so as to ensure that wall did NOT fall down.
I am not understanding how Wiza's actions are the least bit connected to the collapse of the building.
spsalso
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
And also your thoughts on the seismologist not (apparently) reporting his concerns to management higher than Wiza, or the City? Or anyone?
spsalso
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
After the fact, it appears the wall was not damaged enough to replace it. Surely the CTS tenants would have complained if it had needed it done.
spsalso
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Unless someone can demonstrate that the pile driving operation next door actually caused damage to the Champlain Towers foundation system, this is a false hole to fall down. In his shoes, I would've done the same thing and probably used the exact same obscene phrase to instruct the crew to continue their work.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
....ummm. Structure??
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
I am not seeing the words "CMU", "concrete block", or "privacy" in the quote. He is not making a distinction. But even if he was it would be just as curious. How do you damage the CMU wall, without going through the perimeter basement wall with the vibrational force via the earth? It's another matter yet to define whether a CMU wall is a "structure" in its own right in regard to the vibration standards. It's clearly not the same type or level of damage to replace stucco vs relaying/replacing a block wall whether or not it supports a roof. And it was stated by a structural engineering consultant in one of the links Maud provided that the concrete at the top of the perimeter wall, (post collapse) shows signs fracturing from intense vibration force in the area of concern. The only thing that is left is to determine whether that wall is "structural" in a strict sense, and it seems there is a certain faction here that strongly believes it is.
Having said all that I'm not sure the idea that the wall has "mostly not fallen down" is a test that could be written into any standard.
Edited once for clarity.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
The only damage to that wall that was described in the article was done previous to the pile installation. I don't see anything about it being damaged BY the vibration from the pile installation.
"... the concrete at the top of the perimeter wall, (post collapse) shows signs fracturing from intense vibration force in the area of concern."
As far as the concrete at the top of the wall being damaged by intense vibration force, a person could wonder whether there was any such vibration when the building fell down. I am surprised that the wall stood at all.
spsalso
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Semantics.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
How many times was this wall rebuilt over the life of this complex? There were at least some sections that blew over in Hurricane Wilma in 2005 (video appears to show the failure of the entire eastern section abutting the pool deck, shown approximately 3:30 in https://youtu.be/X4BwnI0VyPM). Do we know if that was the original wall, or if it had sustained damage previously and/or subsequently due to tropical force winds? I can't recall how thoroughly that was hashed out here.
Infiltration was a known issue at this location on site, as was shoddy construction and maintenance. I have little faith that any potential damage to the connections at the pool deck and subterranean structural wall was repaired properly if at all. I'm sure the vibration from the pile driving didn't help, but it was likely just another irritating factor on top of decades of neglect and mediocre construction. This entire disaster should be seen as a cautionary tale, but we know how that goes.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
To clarify, this was a building that made noises over time…it was not silent until the 24 hour period described in the Timeline spreadsheet. Residents specifically complained during the period of construction next door (which started 2016) and also during the roof work that was going on when it collapsed. At the time of the collapse, there was an interview quoting a resident stating that the building always made sounds, but I don’t have a citation or know how long that person had lived there.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
In this scenario you are stating the wall disconnection at most should provide stress relief to the remainder of the deck support, stabilizing it or isolating it from certain forces...all else being equal. And I guess by "equal" I mean not delaminated, spalled, corroded, or otherwise dilapidated. etc. Posing this as a question so I can understand. Or maybe that is reading too much into it. Do you mean that the entire deck in more or less one piece is simply required to generate the required vertical catenary. And I am sort or reading as a question that the shock wave of the wall disconnection is involved in getting the process going (stack of cards thing). Sounds like a new brain stormer. Who is going to model that?
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
spsalso
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Thanks for clarifying that. It's a complex thing with multiple elements ready to go super critical. The idea that I have a bit of trouble with is that the wall was compressing the deck and and holding the whole thing together. But then from what Josh was describing that is not very likely in terms of the failures. i.e. that the wall was not a required structural element in that sense. You are I think looking at it without that idea being incorporated at least. So anyway I get you are talking about what more likely fits the timeline. And of course the ductility is in that. If the perimeter wall is not holding the building up (wild theory there) it's a little harder to explain, in simple terms.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
06 MAY, 2022 BY ROB HORGA
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
SF Charlie
Eng-Tips.com Forum Policies
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Sorry, I haven’t been staying caught up.
From a witness statement perspective, a two-stage deck collapse doesn’t work. The Vazquezes drove into the garage, parked (I still have not found out which space they parked in,) walked to the elevator lobby, heard loud cracking sounds, and got into the elevator just as the deck collapsed at about 1:15 AM. They have never reported seeing any evidence of fallen concrete in the garage in the minute or two before the collapse.
The loud crashing sound that Security Guard Shamoka Furman heard in the lobby and the Nirs heard in 111 occurred at 1:10. Because the Vazquezes saw no evidence of collapse, could the 1:10 sound have been rebar failure at a column or at the south wall?
Note that none of the witnesses talked about banging or crashing sounds in the five minutes between 1:10 and 1:15. I doubt that anyone has asked the witnesses what they heard in those minutes.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
It will be interesting to learn NIST’s findings someday…the Miami Herald states the failure of the connection of the south perimeter wall triggering the deck collapse as a fact.
One of their reporters called me up this week to tell me that the Miami Herald timeline deviations are insignificant and must surely be the result of expert advice they have received from people they have hired, as opposed to actual witnesses describing their lived experiences.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
spsalso
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
If you scroll down in the Miami Herald piece, there’s a list. Morabito is one, but there’s a structural from 87 Park listed too.
The developers of 87 Park get to keep their settlement amount a secret because they are only contributing to be nice and make the lawsuit go away…they maintain they are not liable.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
>>>>>Edit: A subscriber in a FB group I monitor copied out the text.
SURFSIDE CONDO WAS ‘SCREAMING’ AS AN ALARMING CRACK FORMED JUST WEEKS BEFORE THE COLLAPSE
By Sarag Blaskey, Ben Conarck, Nicholas Nehamas
Updated May 14, 2022
Less than a month before Champlain Towers South collapsed last June, the building manager noticed something that made him pause on one of his near-daily walks around the property: A large horizontal crack, maybe 20 feet long, had formed in the planter along the western edge of the pool deck.
So he called a structural engineer working for the building to come check it out.
The long crack hooked upward on one end in a gaping vertical fracture as if the planter was being torn apart at one corner, photos taken during the June 8, 2021, inspection and included in court records showed. The concrete-block wall on one side of the vertical crack appeared to be about an inch lower than the other, as if part of the planter had started to slump into the garage below.
The planter itself did not play a role in the building’s structural integrity. But the dramatic change in the height of the wall on one side of the vertical crack suggested the structural slab below could have been starting to fail a possible canary in a coal mine warning of the deadly collapse that would happen on June 24, six structural engineers who reviewed the photos told the Miami Herald.
A cracked planter alone isn’t enough to cause major alarm, the experts said, but the slab nearby had been showing signs of distress for months. Photos exclusively obtained by the Herald show water had poured through the slab, cascading down a column supporting the pool deck just 20 feet from the planter. The file names suggest the photos were taken in November 2020. Josh Porter, the president of Punta Gorda-based Consult Engineering, said the photos from November were already “evidence of imminent collapse.”
“This building was definitely screaming that it was in dire straits,” said Porter, a structural engineer who specializes in restoration of high-rise condo buildings.
His concern was more than water damage to the column.
The amount of water streaming down it was a sign that the slab was already severely cracked around the top of the column, Porter said. It looked to him like the slab might soon break away from the column supporting it. “Most engineers would say this is a serious problem: Part of your pool deck could collapse,” Porter said.
The crack in the planter months later suggested the problems in the pool deck slab had likely worsened, although more inspection was necessary to be certain the two problems were linked, the engineers consulted by the Herald said. Although it’s unclear exactly when the problem in the planter started, a photo dated April 20, 2020, shows no vertical displacement between the two planter walls and no cracking at all. “That’s a lot of movement in one year,” said Florida engineer Nestor A. Cueto of Miami-based Cueto Engineering. “If it was noted that significant movement of that area occurred after the previous inspection, that would be a cause for additional investigation.” Cueto, who performs 40-year inspections, said that given the other problems in the basement, he would have also requested temporary emergency shoring while simultaneously investigating the underlying cause of the crack. The town of Surfside requires a permit to place temporary shoring, which generally involves positioning adjustable, steel support jacks to relieve some of the pressure on weakened structural elements.
A spokesperson for the town’s building department confirmed no permits for shoring were taken out for Champlain South in the month before the collapse.
On June 24, just two weeks after the cracked planter was discovered, the slab broke away from the columns a type of failure known as flexure-induced punching shear that the engineers told the Herald was both predictable and likely preventable based on what they observed in the photographs. The planters and pool deck crashed down into the underground garage below, kicking off a chain reaction that resulted in the collapse of most of the 12-story residential tower. Ninety-eight people died.
MISSED SIGNALS
Scott Stewart, the building manager of Champlain South since 2019, kept a close eye on the structure that was approaching its 40th birthday. “We did a property walk almost every day for safety of the property,” Stewart told the Herald in an exclusive interview. Whenever he saw anything out of the ordinary, Stewart said he immediately called Frank Morabito, the engineer first contracted by the condo association in 2018 to inspect the building in preparation for the required 40-year recertification of the structure. Records show Morabito and his team inspected Champlain South frequently between 2018 and 2021, taking photographs and writing nearly half a dozen reports noting the pool deck slab was in urgent need of repair.
Despite the building’s history, when Stewart called about the cracked planter he noticed early last June, the manager said Morabito wasn’t worried and told him the problem could wait a few days until the next scheduled visit. “Discussing it with the engineer, it wasn’t determined to be an emergency situation,” Stewart said. “So when the junior engineer came out to do the inspection of the roof, he [Morabito] had him look at it then.” The inspection of the planter on June 8 didn’t last more than 15 minutes, Stewart said. He said Morabito determined from photos sent by the engineer on site that the problem was cosmetic and caused by roots penetrating the cracks of the decades-old planter.
“It was determined there was no immediate action needed,” said Stewart, who appears in one of Morabito’s photos from the day. The planter would be removed as part of the overall renovation plan just getting underway at the tower, he said.
Stewart said he remembered seeing some roots in the crack, but engineers consulted by the Herald say that wasn’t enough to determine the cause of the break definitively. “Part of these visits was to monitor the building, so if you see a significant change in something, that should be a red flag,” said Dawn Lehman, professor of engineering at the University of Washington and a consultant on the Herald’s collapse investigation. While it is possible that roots damaged the planter, it is not the only explanation for the gaping crack, nor even the most likely given the timeline and condition of the slab below, Lehman said. “If you come in time and time again and you see a change, you don’t make an assumption, you do your job,” Lehman said. “The building was talking to Morabito and he wasn’t listening.” Given previously documented evidence of damage to the slab in the area and how rapidly the cracking formed in the planter, engineer Shankar Nair said Morabito’s team should have considered potential structural causes.
“I believe this was a very serious warning sign,” Nair said. “If the structural engineer saw what I see in this picture [of the water coming through the slab] and then saw the crack in the planter … he should have put it together.” At the very least, Nair said engineers should have checked the slab for evidence of structural problems. Problems with the slab would have been obscured from view from above by planters and decorative pavers on the pool deck. So, experts said, Morabito’s team should have gone to the basement-level garage to look up at the slab from below, where cracks, sagging or other more definitive evidence of structural problems would have been more obvious. “If he didn’t, that would be on the edge of being irresponsible, to not run downstairs right away,” Nair said. “He absolutely should have done that.”
But Stewart told the Herald he didn’t remember anyone from Morabito’s team going to check the slab from below after they photographed the cracked planter on June 8. He would know, he said, because he would have been the one to bring them down there. Nor was there any immediate plan to tear up the pavers and planters to look at the slab below them something that would not begin until phase II of Morabito’s restoration plan, documents show.
The photos of the cracks in the planter wall were included in exhibits filed as part of a massive class-action lawsuit seeking compensation for unit owners, survivors and relatives of those who died in the tragic collapse. “Proper and immediate shoring under Morabito’s direction may have prevented the collapse of the entire building,” according to the filing by Stantec, the architects of Eighty Seven Park a luxury condo tower next door to Champlain South that victims partially blamed for the collapse. All the firms associated with Eighty Seven Park denied that their construction project had anything to do with the collapse, which happened years after construction ended.
“Certainly, Morabito should have immediately evaluated the condition and stated its structural engineer[ing] conclusion as to whether the partially collapsed planter required immediate and emergency shoring,” the filing continued. On Wednesday, Champlain South’s court-appointed receiver announced that the plaintiffs and defendants, including Stantec and Morabito, had reached a global settlement of nearly $1 billion. None of the defendants admitted wrongdoing. Morabito will pay $16 million through its insurance firm. The plaintiffs had accused the firm of failing to warn residents that the building’s structural problems necessitated immediate repairs. and possibly even evacuation.
A spokesperson for Morabito Consultants did not respond to the Herald’s specific questions about what actions were taken after the crack in the planter formed and whether there was any investigation of the area below the planters, but defended the firm’s work and reputation. “Morabito Consultants are structural engineering experts with a well-earned reputation in the industry,” Brett Marcy, the spokesperson, said in a statement to the Herald. “We share the desire to better understand what may have caused this tragedy, and we are hopeful that the global settlement announced today between the many parties involved will bring some closure to all those impacted by it.”
Records show Morabito warned the condo association about structural problems at the building. But in a court filing the association said he never determined whether the building was “safe, safe with qualifications, or unsafe,” as required in his contract. The federal National Institute of Standards and Technology continues to investigate the cause of the collapse, although its report may not be released for years.
AN EXPERIENCED ENGINEER
In the spring of 2020, the Champlain South condo association met under mounting pressure to do something about the laundry list of deferred repairs that were becoming impossible to put off any longer ahead of the building’s 40-year recertification. The association was chiefly considering hiring Morabito, a reputable engineer from Maryland with decades of experience who was establishing a foothold in South Florida in the latter stages of his career. Morabito describes himself on his website biography as a dual citizen of Italy and an active philanthropist of Italian charities.
“Some might be surprised by his skill on the billiard table, though he’s more likely to be found playing golf or reading golf books while enjoying a glass of red wine,” the biography reads. Morabito spent the bulk of his career expanding his business in Maryland with his two brothers Fred and Anthony all of them having University of Maryland degrees. In 2018, Morabito pivoted to South Florida as his primary business hub. His state license is active, and he first registered his company with Florida regulators in 1990. Huddling in May 2020, the Champlain South condo board noted that a prior board had already hired Morabito to perform an inspection on the troubled tower, which went well enough to earn him a recommendation from the association’s 40-year committee. The board ran several reference checks on Morabito, citing various South Florida projects he had worked on. The feedback was overwhelmingly positive, though he had been described by one person as expensive.
It wasn’t noted in the board’s presentation, but Morabito did battle one high-profile lawsuit in his career. In the late 1990s, the College of Notre Dame of Maryland sued Morabito Consultants for negligence and breach of contract over a 1991 renovation of Gibbons Hall, an administrative building on campus. The project included converting residential space on the fifth floor into classrooms and offices, and Morabito Consultants was hired to perform the structural engineering. Several years later, in 1997, a separate engineering outfit performed a routine inspection and described “significant movement ‘internal to the building’ on the fifth floor,” according to the lawsuit. The firm concluded that Morabito Consultants failed to properly calculate the increased load brought about by the change in building usage, causing the building’s trusses to become overstressed. A Maryland circuit court and appellate court both dismissed the suit, saying it was filed after the statute of limitations had expired. Abieyuwa Aghayere, a Drexel University engineering researcher, said that type of mistake was not a run-of-the-mill mix-up, based on his review of an appellate ruling. “You typically would design for the new load and check it, and maybe reinforce the [trusses] if need be,” he said. “The fact that [Morabito Consultants] didn’t do that here is concerning.”
Aside from that lawsuit, Morabito Consultants earned favorable marks from the condo buildings that Champlain South checked with. On his website, Morabito cites his favorite renovation project as the Dolphin Towers condo renovation in Sarasota, which had been evacuated in 2010 after a giant structural slab between the third and fourth level failed. Morabito Consultants was called in to help fix the condo tower. Jim Toale, the president of the condominium association, said Morabito was hired by the contractor who handled the Dolphin Towers renovation, and came up with a solution for the issue with the slab. While he was there, Toale added, Morabito flagged warning signs of punching shear in the parking garage, prompting future repairs. “We’ve had no issues with Morabito,” Toale told the Herald. “What they fixed, it’s still solid.”
A BUILDING ‘CRYING OUT’
In November 2020, Stewart, the building manager, was touring the underground garage with someone from Morabito’s engineering firm. It had just rained, Stewart said. And, as usual, puddles covered the floor, proof of the failed waterproofing on the pool deck, which Morabito had noted was causing “major structural damage” to the slab. In one report, Morabito said urgent repairs were needed to prevent the problems from becoming exponentially worse. That day, the engineers focused on an area around one column in particular a 12-by-16-inch pillar of concrete painted with the number 76, demarcating a parking space in the middle of the garage. Photos taken that day showed water streaming down the column, causing the paint to run and sediment to build up at its base. “We were trying to figure out basically where the moisture was coming from,” Stewart said.
Other columns around the garage were sometimes wet, mostly from leaking pipes, the manager said. But column 76 was by far the worst. One engineer who looked at the photo for the Herald called it a “waterfall.” Stewart said Morabito’s team snapped the pictures of the column and slab above it to include in a bid for the upcoming concrete restoration process set to begin the following year. But if they had more immediate concerns about the structural integrity of the area, they never told Stewart.
They took the pictures and then did “nothing” more, Stewart said. Morabito made no mention of the column in any reports to the board reviewed by the Herald. “It’s shocking,” said Aghayere, the Drexel professor. “This column was almost crying out; it was the structure crying out saying ‘fix me, do something about me,’ ” he said. Knowing that the structure was poorly designed, with almost no redundancy, Aghayere said the problems documented in the photographs that day “would have scared the daylights out of me.” “I would have shored it up with a goal to evacuate the building, knowing what I know about the structure and how it was designed,” he said.
The western half of the pool deck, which caved-in on June 24, was held up by narrow columns placed up to 30 feet apart to maximize parking space in the garage below. It was a flawed design that left the 9.5-inch concrete slab cracking and bending under its own weight from day one, computer modeling by Lehman, the University of Washington researcher, showed. The building designs had originally included beams to support the planters from below, but they were removed in the final drawings, leaving the slab and columns alone to support the boxes of heavy wet earth.
Over the years, pavers and sand were layered on top of the original tiles, permits show, adding more weight to the overburdened deck. Roots from the planters penetrated the slab and cracked drain pipes causing water damage to the concrete and reinforcing steel bars within it, records show. Post-collapse photos show the connections between the slab and columns did not contain all of the reinforcing steel that was called for in the plans, reducing the strength of those critical connections. Photos also show damage and corroded rebar along the deck’s connection to the southern perimeter wall, which experts said played a role in the overall structural stability of the tower. In a well-designed structure, experts said the localized failure of a pool deck should not cause the collapse of a whole tower. But at Champlain South, the design defects, construction errors, damage, degradation and poor maintenance came together in a perfect storm leading to one of the deadliest collapses in modern history. It began when the deck collapsed at 1:15 a.m. Columns punched through the slab, which disconnected from the southern foundational wall. After losing that critical connection, computer models showed damage propagating into the tower.
But missing from the public understanding so far has been what initiated the collapse. The collapse could have been triggered by column 76 suddenly punching all the way through the slab, as it had apparently been threatening for months, engineers said. Or, they said, some failure of the connection between the deck slab and structural perimeter wall or elsewhere could have triggered the punching shear at column 76 and across the western pool deck. “Are we ever going to know what the very first thing was? I doubt it,” said Porter, the Florida engineer, who has studied the collapse extensively and posts his findings on a popular YouTube channel. “Whether [column] 76 happened before the south wall failed, or vice versa, you’re going to end up with the same result.” Regardless, if the connections between the vertical and horizontal elements of the structure had been stronger and the columns had never punched through the pool deck slab, it’s possible the deadly collapse of the tower would have never happened at all, engineers agreed. “This could have been prevented,” Aghayere said.
Porter cautioned against assuming the warning signs were as clear without the benefit of hindsight. No one would have expected the building to fall down solely because of a partial pool deck collapse, he said. “When you do this for 30, 40 years and see horrendous buildings and bridges and none of them collapse, you end up with this false paradigm that buildings can’t collapse,” Porter said. “You’re so stuck in that paradigm that you can’t fathom that something catastrophic is about to occur,” he said.
#FeaturedArticle #investigation #CTS
https://www.miamiherald.com/.../sur.../article2613...
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
(Also, amusingly, had an issue with the file name uploading this. Got a 500 .net error, I assume from | or some other default symbol from my PDF print original filename)
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
It also puts to shame the prior MH exposé supposing that the slab sheared at the south perimeter wall first.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Those photos are incredible. I can't recall that ever being seen widely such as on this form or previous links. that could be the early predicate of a E-W catenary. There is a sudden step change the deck height from that point east. The long crack going north has not dropped much. So the entire progression *to* the S perimeter and step beam may have happened over weeks. This might argue that the deck started to collapse well before the wall disconnection. Unbelievable that this photo was not widely seen until now...nor witness statements about what it shows.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
>>>Edit: Yes, we can thank Jinal Doshi of Structural Madness for identifying this area long ago. Here is his video, which he posted around August 2021. https://www.youtube.com/watch?v=fFQ7ey5CDLc&t=...
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
thirteen(my bad) sixteen days prior to collapse, Morabito photographed the cracked planter.Even more telling is that the crack in the planter is absent above the column upon which it sits. This would indicate that the punchout is in progress.
Markup transferred to aerial
The remains of two columns supporting the planter in question.
Meanwhile, I was looking at the 29/30 column. The damage previously photographed was either repaired or did not progress through to collapse.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
And yet one has to wonder to what extent he could or should have realized this put the entire structure at risk. To what extent could he have imagined that? Yes he should have shored the deck and the deck should not have collapsed.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
The piece closes with Josh warning that most engineers would not imagine that such damage would lead to collapse, as everyone has seen buildings with similar or worse deterioration. But before the closing, the MH practically slanders Morabito via critical comments made by various engineers, at least some of whom are on the Mh payroll.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
WOW!
SF Charlie
Eng-Tips.com Forum Policies
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
My apologies to the MH
In this MH photo in 2020 we see stanchions and colored tile.
In this USAToday photo we Don't see the colored tile, we see paving for parking
leading to the vestibule of the office.I think the MH miss located the planter in their photo.No they didn't
Please see "area detailed:
from a real estate site:
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Without hindsight, would any of those who are stating the Morabito firm was negligent have foreseen the tower being at risk using the observations at hand? The pool deck is showing signs of poor drainage and corrosion, the pool service area is in need of rehab and some planters are cracking and/or sagging. Would that immediately have raised concern the tower is at risk? For the age of the building, were the misalignments of door frames, cracks and reports by some residents of creaking/banging noises obvious indications of impending failure? Or is it all clear to the observer, now with knowledge of the actual collapse?
The Champlain collapse appears to be a failure that is going to change (or should change) the analysis and methods used for building design and structural integrity evaluation.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
SF Charlie
Eng-Tips.com Forum Policies
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
SF Charlie
Eng-Tips.com Forum Policies
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
I've been aiming at that for quiet some time. The photo of the planter now brings this to the forefront. It's (the deck) a 30' span that can't support it's own weight and has cars driving on it (the 30' span for all intents and purposes extends into the parking area!)
Column 76 is the next column east of the planter column. This suggests that two columns have at least partially punched through. This is where Josh's (edit: Building Integrity @ Youtube.com) theory of tensile forces comes into play. A significant area of slab that should be resting on columns is now suspended as though it were a tightrope and is pulling on the building to the north and the south perimeter wall to the south (not to mention east/west). The idea that the south perimeter wall let go first is nonsense.
Column 76, center foreground. July 17, 2020
recently from Miami Herald (photo taken Nov 2020)
The property owners were in on the problem. Likely, they couldn't commit themselves to vacating the property unless "told" by an authority to do so. Though unfortunate, it is part of the human condition.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
The planter wall is not a structural component. The slab punches through and the flaky planter wall falls over or is pushed out of the way. If the drawing overlays are taken literally, the planter wall is offset from the column center line anyway.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
This might have hidden both top and bottom surface indications of its presence.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
This is consistent with the column layout with the greatest span south of these two columns at 29'-8". If that span is not properly supported (edit: by the two columns in question), the area of slab affected is roughly 67' x 49'.
As a curiosity, these two columns also create a bulls eye for the deck collapse though likely only since there were interruptions one bay away on each of the four sides.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Edit: is that pipe coming down the plater column from the planter drain. It dumps onto the floor? If so I am not surprised it is dry under it.
Edit again: the actual drain is slightly s/e of the column. But I guess if you were going to dump it you would route it over to a column. And that's the closest one. That's not the only pipe down column I noticed in the walk through. In fact I don't think I noticed that one until now. I just can't recall that it mattered much.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Yes, I mentioned this several threads back and said I would put some reasoning into what that might mean, but I never got around to it, did I?
Amazing that this pic has just come out now. It seems to clearly show the planter has dropped a long way, maybe 2", at its NE corner. Hard to see how that's possible without the slab already starting to detach from that column just to the N. And while it might only be clear in retrospect that that puts the building at risk, surely a responsible engineer can see that that was already putting the pool deck (and therefore the garage) at risk, and should have ordered immediate shoring and investigation?
> What I'm curious about is why or how the column that was supposedly under the wall, punched through east of the wall?
Interesting question. You'd think, if the slab was failing from the east, the planters sitting on top of it would drop to the east as well, and end up east of that column, but that doesn't seem to have happened. That whole section of deck, to the next column line west, is all punched through, so did the deck hinge from that western extent of the break and pull the planters west of the column?
I still don't think this can have been the first part to visibly collapse into the garage though because it's quite close to the garage level elevator entrance, surely those people that parked up last in the garage would have seen it. They got into that lift only a few seconds before the main deck collapse.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Edit: as well as the angle. It's further away near the trash can. So then the deck was hinged north to south when it landed. It fell further toward the south. Does that make any sense? probably not. The missing part would be that it slid down the slope further on the lower end. so the the deck would have to be angled down towards the s-e. I think.
edit2: scratch that. the effect of falling over the car lump probably pushed it out further on that end. I mean if that is actually the top layer of the wall, which it mostly has to be. I would like to know why it did not break into more pieces though.
once more: well maybe the top of that wall is a lintel. obviously.
Ok this is the last one: Forget all that. That is likely a column remnant from the tower. My apologies. Missing cmus are probably buried. I thought this was far enough away to not have a debris pile on top. Hard to believe the trash can is sitting there like nothing happened. There might, *might* be a piece of the planter cmu east of the trash can.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
From a witness statement perspective, whatever fell first fell after the Vazquezes got into the elevator. They heard a very loud cracking sound while in the elevator lobby, just before they entered the elevator. They were within the elevator and going up to the lobby when the deck collapsed at ~1:15 AM.
Also from a witness statement perspective, all witnesses who described the deck collapse at ~1:15 AM describe it as a single big collapse rather than a series of two or more discrete collapse events.
If you’re thinking about the crashing sound at 1:10 AM, it may have been rebar breaking and not not concrete falling, as the Vazquezes did not report seeing anything fallen in the garage. However, we don’t know what space they parked in or what their path was from the parking space to the elevator lobby. So it’s conceivable that a chunk of ceiling fell down outside their line of sight.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Yes, this makes sense. The situation appears to be quite complicated for an engineer and/or engineering group to be responsible for a structural integrity analysis. If a highly cautious approach is taken and nothing bad happened later, then you would probably get hammered as 'chicken little' by the residents/owners for inconveniencing them with all the shoring, cost and access closures and/or sued for harm due to potential reduction of property value and your competence would have been questioned. If a conservative approach is taken ( as appears for the Champlain Tower), working within the wiilingness and financial ability of the residents/owners and something does happen then your competence will be questioned. Certainly, many of those who could have affected the tower outcome have pondered many 'would have/ could have/should haves'.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Some evidence that the top course of cmu could stay together if the wall falls. This was said to be after hurricane Wilma. I assume the wall caps are responsible. I called them lintels for some strange reason.
There is also this capture from CE3527 from the same thread edit: note added by me.
Within his red circle of the column is the opposite side view of the line of concrete (resembling a column)and this angle looks like CMU. I hesitate to say it's the top of the planter wall, but.....
Thank you for your patience.
edit: second photo to add marks pointing to horizontal concrete section I am referencing. Forgot to add question mark. CMU (bottom opposite caps) apparent to the right of "planter column".
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
https://m.youtube.com/watch?v=M0UtmbRAL9M
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
testcase study/precedent study on failure propagation - only in hindsight is the threat to the tower recognized. Were the materials and techniques of construction at Surfside dramatically different than standards of the time? Maybe it has already been asked or stated in the many parts of this thread: Is there a risk to a whole generation/era of structures built in a similar manner?RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
I'll play devils advocate here. The timing and location are very suspicious that this was a deeper problem related to the collapse. However correlation never implies causation. There is a nonzero possibility that the planter crack was just do to roots and nothing more.
Arguments for this being roots:
Roots were observed inside the crack.
A large part of the crack is vertical, hard to accomplish by deck sagging.
Arguments against roots:
The location is very near the heavily loaded part of the deck
The timing is right before the collapse
It appeared suddenly
These type of major cracks were not seen in other planter boxes (As far as I've heard)
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Perhaps from certain builders.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Edit: watched the BI video now, and he also addresses this, and points out that you'd also expect a much slower crack growth and water/organic staining if cracks were caused by roots.
You can actually see (and probably measure) the amount by which that slab is not planar from the pics, as well.
Edit 2: and you could do that from the 2020 picture, too - which shows a significant depression already, not sure if that was designed or if it shows flexure already a year before - and compare
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
I may have failed in the ambiguous nature of copying the original photo from a prior thread in which column 75 was already circled and the actual subject. I'm talking about the horizontally laying column-like feature that is about 6-7 feet of so to the right of 75 in the photo I provided. The reason I used that photo (other than convenience) is from that angle you see the opposite side of the feature which appears to show the hollow structure of cmu's. As far as I have known from the beginning 75 is not lying horizontally on what remains of the deck. So I am not talking about 75. In Reverse Bias photo the feature stretches left-right in the foreground in front of 75. It was once speculated to be a column that fell from the tower. There are such columns to be seen. But that was from a much further view point from above. If it's a matter of enlarging the photo to focus more on what I am talking about I can do that.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
How can the deck and part of the planter fall downwards, but leave the upper part of that planter wall behind?
spsalso
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
It appears that there is a course of cmu's capped by concrete, or the upper layers of cmu's have longitudinal reinforcement. Either way, it's obvious that it has longitudinal rigidity that spans high/low points in the deck deflections. Apparently, the reinforcement did not extend around the corner.
edit: Longitudinal reinforcement may have been required so that the planter contents don't push out the walls.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
EDIT: I am not implying anything right or wrong about IanCA's theoretical sequence, rather would like this crack layout information added to Sym P le's animation.
Edit 2: If you look at Green/Yellow/Red Sag Diagram posted by Reversebias, clearly there is a large area of red sagged area along the South Wall after corrosion factored in. The only way I can see that much sag at the south wall is if the concrete/rebar has sheared from the wall connection in that area which would shift stresses to the South, East and West.
Edit 3: Or the foundation supporting the south wall had settled in relation to the interior columns.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
OK. So the slab drops, but somehow leaves the decking in position (leaving a void)--there seems to be no damage to the decking (see, for example, the "area detail" shot that shows the joints between the two walls and the decking). But the wall on the left is still neatly connect to that decking, as is the bottom of the wall on the right. So that would imply it stayed with the decking instead of dropping with the slab. But then the upper part of the wall on the right would somehow have to have raised itself up an inch to make the crack.
It appears that there is a course of cmu's capped by concrete, or the upper layers of cmu's have longitudinal reinforcement. Either way, it's obvious that it has longitudinal rigidity that spans high/low points in the deck deflections. Apparently, the reinforcement did not extend around the corner.
We don't see evidence of any deck deflections. It all looks nice and neat-ish, and pretty well connected to the bottoms of the two walls.
edit: Longitudinal reinforcement may have been required so that the planter contents don't push out the walls.
And that needed reinforcement would have been in the horizontal plane, not the vertical."
spsalso
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Was the planter box fractured by the column breaking an inch through the concrete slab and into the CMU but being held and supported by the rebar alone at that time? If that is the case, then it makes some sense that the planter box may not have fractured on the side facing the parking area so no need for photos. That could also mean that more catenary forces were being applied to the deck for a longer time period than what we have been thinking.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Good stucco with elastomeric coating? eg: BEHR PREMIUM® Elastomeric Masonry, Stucco & Brick Paint No. 68
The upper corner flap is a good example of quality product ;')
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
The column is not doing a stabbing movement. It's the slab falling down around the column "as though it was punched". The planter merely remains in place atop the column/slab shim until it looses any semblance of stability as the wider remaining structure drops out from under it. The slab section south of the column is showing greater downward movement which would be consistent with failure of the slab/column connection being initiated at the south edge of the column where the stress is greater from the 30' span.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
The displacement in the corner of the planter is not representative of the movement everywhere else. I would read that corner as an indicator of displacement but would exercise caution on what it means. The upper corner of the planter wall being perpendicular to the structural member of interest would exaggerate any gaps due to slope changes in the slab. The vertical drop on the south side of the column is very real and and given the columns proximity to the corner (which is a low traffic area) the aggregate of all the materials may just be floating over a discontinuity in the slab and waiting for a good thump.
Regarding planter wall reinforcement, although a primary benefit in this case may be for horizontal reinforcement, a simple lintel reinforcement scheme would benefit in both directions.
Really, I don't have all the answers, I just hope I'm right enough to be able to defend my posts. Thanks for the feedback.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
I've made more than a few posts debunking the Miami Herald's analysis. For instance, the graphic you posted starts with edge conditions which include the slab along the south perimeter dropping 1" in an undamaged state. That just doesn't make any sense. That's not to say that punch out doesn't happen, it's just that their graphics are way off. A better analysis would have been to examine progression given slab punch out at the most stressed column/slab connections, which are easily determined, and the results would have been more interesting in areas they highlighted. I think the Miami Herald was trying to sensationalize the impact on CTS of the work on the neighbouring property and as a result did the discussion a disservice.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
SF Charlie
Eng-Tips.com Forum Policies
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
The slab drops.
What does it take with it?
It can't be the "return" wall (the one on the left of the picture), because the slab would have pulled it through the decking (which, it has been argued, separated from the slab), and there would have been a crack between the decking and that wall.
It can't be the bottom of the long wall, because there also was not crack generated when that part was pulled past the decking. The detail photo shows the two walls meeting at the deck, without any apparent damage at all.
That leaves us with a slab that fell, leaving the decking and those two parts of the wall in place. AND the top part of the right wall, which decided to jump upwards. By about an inch. Because it was in the mood?
I do believe that is a correct description. Am I missing something?
spsalso
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
I had to download the file before I realized what it was you were getting at --> Column_came_though_planter_box_AP_Building_Collapse_Miami.jpg
As I stated earlier, the column didn't go through anything, everything else fell down around the column.
Perhaps they should rename this failure mode "falldown" as opposed to "punchout" but that would just confuse everything else.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Possibly, there is differential movement between components that the imagery isn't tuned to convey. We don't know the time stamps (day?) on the various images either.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
SF Charlie
Eng-Tips.com Forum Policies
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
SF Charlie
Eng-Tips.com Forum Policies
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Though I don't see the point, I tried to do an overlay but just seemed to make a mess. You are welcome to mark up my images and show your results.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Moses: "We just did it"
Reporter: "And you're not even wet!"
Moses: shrug
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
I think you are correct Sym P. Le. Here is a sectional elevation of the planter from the 1979 drawing set, showing an 8x8" concrete cap with 2 x #5 bars:
I think that detail was drawn with the southern wall in mind, but I imagine it was applied to other planters and explains the longitudinal rigidity you describe.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
I am wondering why the top of the column underneath isn't sticking out of the deck an inch. If there was a "buncha" sand between the deck surface and the slab, it could have absorbed the displacement. I suppose.
And all this happened a few days before June 8.
Since the slab and etc. dropped down over the supporting column, there should have been signs of that in the garage. But no one reported such a thing, it appears.
spsalso
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Thank you my power-pointy hero. At least you understand that the planter box has an East wall and a West wall at this section and that if the box had been positioned so that it's walls straddled the column then we would have likely never seen any damage from the relative motion of the column and slab moving in the vertical plane.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
This should give folks pause for concern and at the same time relief. Their buildings won't just fall down, however ...
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
But looking at the planter pictures, imagine if it wasn’t the column under the planter that was punching out. But the column to the left
of that area. Wouldn’t the bending moment in that wall at the planter column cause that long longitudinal crack that is formed there?
Essentially popping the top of the wall up an inch as someone else above postulated. When the vertical joint in the corner of the planter failed, that seems like what the top of the wall would do if it were being subjected to bending restrained by the column beneath.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
"Oh, look. This whole damn building is just falling apart. Sure does need work!"
instead of:
"Oh, look. This building is FALLING APART!!!!!"
That's likely because I see a lot of buildings "falling apart", but very few (if any) "FALLING APART".
So I have some sympathy for someone thinking it was root damage.
spsalso
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Column 76 is likely a low point of slab and as such was drain relief point for slab, before planter column failed. I don’t see much rust at column 76, rather I see more white chemically changed concrete. Therefore steel is perhaps only thing prevented punch.
Is planter drop due to slab sag or a shear crack opening up?
Lots of cracks radiating South and west from planter.
Edit1: I concur with Spartan5’s comment and point out this is in line with IanCA’s earlier posts.
Edit2: Live load cycling on deck is a factor and no waterproofing under parking deck
Edit3: Could it be I14.1 that punched first? I believe that was one of IanCA’s theories?
Edit4: How does a delaminated deck affect water drainage and variations between what is happening on top and bottom of slab? Could delaminated deck cause water drainage at column 76, on what was originally a flat deck?
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
SF Charlie
Eng-Tips.com Forum Policies
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
There's no sugar coating that crack
I was thinking along the same lines. The slab didn't need to drop from its perch, braking its back creates some interesting differetials. This also has implications in puddle depth and drainage around a puddles perimeter.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
An inch or more of separation is breathtaking but it doesn't defy basic physics.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
You're awesome.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
It's when engineers start sketching on the backs of restaurant placemats that breakthroughs are made...
SF Charlie
Eng-Tips.com Forum Policies
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
when I started to wonder "why was the April 2020 photo taken?"
SF Charlie
Eng-Tips.com Forum Policies
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Unless it was cropped, the subject seems to be "cleanup time". You've got the broom, dust pan, and garbage can. I might have taken that if I had to buy more trash bins and had to make sure I got the model. But seriously, it's a good question. It's a bit bothersome.
Add: anyone look at meta data on these files to see if the cameras are the same camera? Does that get stripped when posting? does png have meta data? It would be interesting if the same person took both (as in the engineer).
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Your PowerPoint arrow interpretation looks fair to me, in which case that part of the slab and planter dropped pretty much straight down. The idea that it moved west is probably an illusion of the photo from the other side.
If the collapse did initiate on the deck, and that looks pretty likely with this new information, it's still worrying that the night before there were noises within the building as well. That implies that the whole thing was badly built and in trouble, not just a single flaw - and how many other buildings of a similar age might be like that too?
> why was the April 2020 photo taken?
An interesting question in itself, particularly as it looks like there's already significant deflection there to me.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
What I am trying to show is correct column labels on some of the columns of current interest, and that the center line of the slab running under the planter 1" drop aligns with Column I14. And Not I14.1 as I incorrectly stated earlier, and that Column 76 is L13.1, unless I made boo-boo, as I have not received the "color between the lines" class yet.......
And all that displayed on the Outstanding GIF, I just plagiarized.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Edit: suggested in this photo (tight crop from a WSJ photo previously posted)
Note the garbage can for perspective. pavers and deck south of can relatively planar and undisturbed. Trash can sits at a level a step below. Pavers north of this line are disarranged and deck is
deskDIS- continuous. Does it mean anything? Don't know. There is tower debris encroaching from the lower left. did the falling debris cause this fracture to propagate? All an illusion? Time for my pills now.RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Clearly in the second image below, now that I have high resolution from WSJ, I can see the diagonal break in parking deck that is either radiating towards the trash can and dropped planter, or radiating from?
Did anyone else notice that the planters were to be water proofed in 1979, however "weep holes in planters where practical" ? In detail posted by IanCA.
GREAT way to keep that structural slab soaked around the planters...
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Edit: About the second image with diagonal break. I realize that was identified as significant by several posters recently. I guess the question is whether that is what is propagating all the way out and near column 76. That's the gist of what I am trying to ascertain.
edit again: Weep holes. I saw that. Where practical? That must be with foresight of the drains clogging after a month of use. Actually not too bad of an idea if the deck would be adequately sloped. And that turned out not to be the case. Are the drains bigger than a weep hole for long?
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
I suppose you might if you assume incompetent construction methods. But then, the AHJ would catch that, and require correction. Which, of course, the City of Surfside did.
Or not.
spsalso
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Maybe there was some odd internal voids within the slab causing this? It almost points back to the delamination theory.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Sure seems like it. Eye witness testimony of water poring into sunken deck. Voids filled with water that pours out when the deck falls. Josh described 76 as covered with efflorescence and water very wet (from the photo he was shown by MH). for the water to contain that much dissolved mineral content it seems like it might be continuously wetting concrete. When he said that I was thinking the water is not just running in around the top of the slab straight down around the column whenever it rains. Just a brief thought. But now you made me recall it.
Edited for dumb stuff.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Perhaps the runoff from the planters was more acidic than usual. If the salt and chlorine ion levels were higher?
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Here is the PDF of his report as provided by the local NBC affiliate in this story. The links within it don’t seem to work, but the embedded photos are there.
https://s3.documentcloud.org/documents/22017784/su...
I will update the spreadsheet, which lists the initial survivors of the collapse. Having occurred after the collapse, though, this has no effect on the timeline leading up to the collapse.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
I tried a toddler diagram but I could not keep the coloring between the lines.......
Clearly the water intrusion from planters was degrading concrete faster in deflected areas of slab, which is probably where epoxy injection was first performed to keep water out of garage, but creating a sorta artesian well effect around column 76?
Edit: But never emptying fully, thus leaving lots of water sitting in low area. So the top draining of water pond, lets sediments to fall to bottom of depression
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
My concern with that statement is the uncertainty. To quote Jeff Ostroff "If you don't tell the water exactly which route to take, it will take the most expensive".
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Please remember the cars under the deck supporting it in odd ways.
SF Charlie
Eng-Tips.com Forum Policies
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
SF Charlie
Eng-Tips.com Forum Policies
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Interesting to note the linear E-W crack in bottom of midspan depression, that lines up parallel between the column lines, thus the planar crack line that Zebraso was seeing in his Pixelizations......
The Planter roots could have made their own path for the water in the depression also...... after they clogged the drain lines in planters....
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
https://www.miamiherald.com/news/special-reports/s...
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
SF Charlie
Eng-Tips.com Forum Policies
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Do we have all of those reports and supporting material?
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
However, I find it very interesting that the 'As Designed' Model shows cracks in the areas of interest that seem to align very well with the current evidence we have, except for South Wall (which I have hard time believing we have the deflections in red they show along the wall, with it still standing?
So yes take it with a grain of Salt, but I don't think you throw the whole thing out either at this point.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Structural Madness's model, though also imperfect, lends better insight to this collapse. Note how the deflection across the 30' span creates a high stress zone along the south edge of the 13.1 columns and north edge of the 14.1 columns. This is consistent with the evidence seen regarding the planter and column 76.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
I guess what intrigued me was the linear crack in line E-W with Column I, which was NOT mid span.
Edit: I Yield! You are right! Yes Vibrations add a whole other complexity, even different from parking deck cycling.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Every time it rains the dynamic weight load goes up and every time it dries the weight load goes back down. Seems to me like the slow-motion bouncing of a trampoline.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
I also wonder if the E-W rebar was actually the final straw that broke the camel's back. Specifically the drop of the planter could have been the E-W rebar loosing it's grip at Column I14 connection. Once it lost grip, the other columns were already in partial punch and ready to go.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Edit: I may have spoken to soon. The column you are looking at is misplaced in the model so it doesn't reflect CTS exactly but the results as presented are interesting.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Of course not. Their Building Department appears to have done something close to nothing in ensuring that this building was properly built, but also accepted $40,000 in permit fees to ensure that it WAS. It just MIGHT be a little short, dollarwise. And then there's criminal negligence:
If you accept money to do a job (inspect a building during construction), and you don't do the job (by delegating the PE to inspect his own work), and people die because there were flagrant construction errors, does that not sound like criminal negligence?
I could be in error here in my assumptions, so please correct me if I am wrong.
spsalso
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Thanks MaudSTL.
The statement that concerned me in podcast Episode 11 was this at 17:50: "This exact same area had been photographed a little over a year before, in April 2020, and in those pictures, there is no sign of the cracks, at all."
But when I zoom in on the April 2020 photo, there certainly looks like some signs of prior damage to me.
And I think the area that Josh described as 'blurry' needs further study to understand why the horizontal crack is not clear in that area. It doesn't look like any of the usual optical or digital artifacts. Perhaps it was another area with prior repairs?
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
So I will ask, could we have dissolved rebar grid in this area, which just happens to line up with column Line I14? We know we have a diagonal crack headed to this area from the parking deck.
So loss of a square of rebar grid/concrete failure in this area, could lead at first to localized drop.
Loss of grid in this area, would appear to start transferring load to surrounding columns. Which in this case are K13.1, K15, and I14. Which breaks the rebar tight rope in this area, and now 1-3 columns at once loose what little punch shear resistance rebar they had on at least one side of each column,
Boom!
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
SF Charlie
Eng-Tips.com Forum Policies
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
SF Charlie
Eng-Tips.com Forum Policies
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
SFC, Outstanding Power Pointy! Now to digest
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
SF Charlie
Eng-Tips.com Forum Policies
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
SF Charlie
Eng-Tips.com Forum Policies
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
In the June 2021, it appears to be much less of a dip.
I am basing this on the helpful color lines overlaid onto the photos.
I wonder why that is.
spsalso
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Edit: belaymylast 2020 not 2012
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Rather than think climate change and the corona virus as science, think of it as the wrath of God. Do you feel any better?
-Dik
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
As mentioned earlier, would failure at South Wall Under Planters actually cause the 'Catenary Stub Area' to initially move upward, until things let go? Basically the South Wall to Column K15 becomes a bigger lever arm load on the span between K15 and K13.1 for 2 weeks and 2 days?
Edit: Middle Span is 30 feet and much longer than adjacent spans, which begs the question, how in the world do you design a flat slab with same rebar everywhere and same slab thickness when spans are not equal? Looks like it was designed in that 30 foot span would deflect more than adjacent spans, thus providing 40 years worth of unbalanced stress on pool deck? Not to mention the various column sizes and layouts?
On the next two images below, are we seeing evidence of slab drop at South Wall? Note Dark base board like area at wall/patio deck joint?
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
please see the following from Josh (building integrity):
1. Engineering Failures Found in the Champlain Towers South Drawings - Surfside Collapse
(Toward the end, where he talks about the changes in the area of the valet parking planters)
2. Zeroing in on the Initiation of the Surfside Collapse
3. 16 Days Before the Surfside Collapse - The Warning Signs Were There
Thanks.
SF Charlie
Eng-Tips.com Forum Policies
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
I added where roughly Column 76 is, and lowest point near that column from Survey Posted. This clearly shows why Column 76 was such a good drain path for deck, after perhaps the nearby cracks were epoxy injected.
Edit: Also shows 9.52 low spot on parking deck side of gate from pool deck, with 9.5 drain elevation nearby.
Edit2: I do find it interesting that Building Integrity has NOT linked the Pool Exhaust Fan Exhaust venting East along South Wall, as a probably contributor of accelerated corrosion and slab shear in that area of south wall. I did notice in BI's links provided by SFC, that on one of the original drawings he uses, the exhaust fan originally exited on the West Site of Planter Wall at South Wall, and not East as built.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
As you can see, trying to draw contours was a disaster.
SF Charlie
Eng-Tips.com Forum Policies
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
SF Charlie
Eng-Tips.com Forum Policies
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Edit I assume the elevations in the planters is at bottom of planter, which indicates that there may be a layer or concrete forming bottom of planters that is on top of structural slab. Or some sort of elevated base inside the planter, perhaps part of a drain system, or maybe just the dirt level in planters.... Duh!!
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
SF Charlie
Eng-Tips.com Forum Policies
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
But Morabito stated in his report the architect had a flaw in his design, of no slope. That is false because the floorplan clearly shows the slope in the 1979 drawings on that pool deck That is what I was puzzled about why he stated the architect scared that up when the drawings clearly show the slop in it. So we will never really know. Morabito provided no photos showing a flat spirit level on the actual as-built pool deck slab, to confirm his claim.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Edit: it's a bit unclear to be now whether the claim was that the structural deck has no slope or is insufficiently sloped as built. I'm not sure it matters. I mean the deck as constituted by the cores that were taken.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Also, if there is lippage between the pavers, that could inhibit the downward water flow. One of the great ideas Morabito had was to add grout between the pavers. This would, in my opinion, help reduce the amount of water going down between the pavers, as the grout provides a smooth pathway down to the drains for the water to run down.
BTW I am working on a new video covering some of this, and other item, the settlement, the lost first responder audio files, and some new theories I have on what could have caused the planter to crack in the Miami Herald photos
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Looking at the report on the cores I can see they have identified the structural slab, topping slab, tile and mortar layer (sloped), water proofing, sand and paver. Apparently the sand and paver are not actually in the core sample as shown even though they they are listed.
So I think what I should have said is structural deck, topping, tile and mortar, for the original slope - or what was under the water proofing.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
The drawing is from Morabito's package for remediation. A note on the drawing states the elevation survey was conducted on 08/07/2020. Units are decimal feet as far as I can tell.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
SF Charlie
Eng-Tips.com Forum Policies
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
SF Charlie
Eng-Tips.com Forum Policies
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
The elevations are on page 71 in part 3
Or use Town of Surfside Public Records Search
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
https://www.geodose.com/2018/05/how-to-create-cont...
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
He just shows Patio Deck Slab, Edge Beam and garage wall as existing, with no indication of repairs to South Wall, other than Block Privacy Wall on top of deck slab.
This indicates no visible signs of problems when Morabito did his original field data collection to base repairs design on?
8.7.20 Survey also shows elevations good at South Wall.
Last page in SymPle's first attachment above.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
SF Charlie
Eng-Tips.com Forum Policies
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
2. The issue at the south wall is not that it dropped, it is that it release tension on the pool deck, allowing it to droop ("bend or hang downward limply.").
SF Charlie
Eng-Tips.com Forum Policies
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
The issue of the slab dropping at the south perimeter is a product of the MH exposé.
The idea that it released tension is a misnomer as it never was tied in to the perimeter wall as though anchoring a tightrope.
Morabito's idea of an edge beam would seem to be wishful thinking.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
I know they raised the finished paver floor height around the pool when they raised and rebuilt the pool edge gutter system.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
SF Charlie
Eng-Tips.com Forum Policies
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
you missed the last part of the sentence. The tie-in is not intended to anchor a tightrope.
no
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
SF Charlie
Eng-Tips.com Forum Policies
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
As far as my no answer, there is no such thing as drooping at the south support so it's a nonstarter.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Add: incorrect premise. The assumption has to be the tie-ins broke after the collapse initiated. I am struggling to see a way around that.
Add more: It might help me in my mind to say there is not tightrope the spans the length of multiple columns. I mean I think at this point that is as ridiculous as can be. And then to say the deck between two columns is like a tightrope in two way flat slab? Seriously. What planet are we on?
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
I'm not trying to put a damper on anything. Carry on.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
The cropped image below, IMO shows movement towards the sink hole.
Edit: Actually rotation of planter wall may be more of the opposite effect, or indication of movement West at South wall end.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
It appears to me that both models have significant deficiencies.
For me the most important criteria for both the Miami Herald and Structural Madness models are:
1) Are they based on reasonably accurate initial conditions?
2) Can they be developed in time, as the collapse of the deck progresses, to produce a similar arrangement of debris at the end?
The problems I see are:
a) Neither model appears to make provision for the construction joints that we know played a critical role in limiting the area of deck collapse and also played an important role in the geometry of the deck after the collapse. For example, the linear depression that runs East-West through the pool deck gate.
b) Neither model appears to include the 19"x19" penetration through the deck that was formed to allow exhaust from the pool equipment room to be vented at the corner of the pool deck.
c) The Structural madness model does not make any allowance for corrosion of the steel or degradation of the concrete and we know they are both critical factors in the collapse.
d) Neither model appears to include any provision for as-built, or as-repaired, conditions of the deck at the Southern edge, as shown below:
Credit to Construction Engineering and Failure Analysis for originally posting that clip.
e) Neither model explains why there would be a dramatic discontinuity in the deck between the pool equipment room exhaust vent and the gate. The area identified by thermobaric in the image above.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
The MH model is, in my view, more take-it-or-leave-it. Having a background in theatre (rigging) and outside-plant telephone engineering (pole setting and guying,) I am skeptical of the tightrope and compression theories for the south wall and don’t put Jinal’s failure model in the same class as the Miami Herald’s. Plus Occam’s Razor.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
When I duck 🦆 go’d - ‘BOTS’, the Green BOT was 2nd imagine displayed, so I used it.
Edit: Rather my post was referring to disinformation, destruction of evidence and cover up of evidence.
Since IanCA, posted the image of the exposed top of sheet piles in area of interest, I have gone and watched some of Construction Engineering & Failure Analysis’s latest videos.
First a warning ⚠️, prepare a stiff drink 🍹 to assist in the painful experience of listening to this guy think out loud in real time, and ramble and ramble to drag things out.
The reward is, you will see images I have not seen before, and receive data you have not seen or heard before.
Filtering thru the noise, is a lot of information not being released by ‘The Ministry of Truth’.
Like evidence of control joint E-W along I14, and crack pictures, and discussion of problem with columns being offset from straight line and the possible effects of that.
We are missing so much information that is being shared to this guy, that leads you down a better understanding of what may have happened.
Edit: No Pain - No Gain
Edit: Have run into some of his videos that say they are private, so I login to youtube and then it tells me they are unavailable. So information is being concealed, by youtube, for some reason, as author claims it is not him doing it.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
I completely agree.
What I would also like to see is his analysis developed past the point where the column which he identifies as the weakest, punches through the deck. In which sequence do the remaining deck support columns punch through? Does the collapse progress to the Southern wall? Does it result in the dramatically different final conditions we see at the wall East and West of column line K? If not, modify the initial conditions and repeat the analysis from the beginning.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
@thermobaric Understood. Thank you anyway.
Agreed.
I'm interested to hear what others think but I think the feature highlighted in the image in my 21 May 22 05:30 post is closely spaced rebar rather than the top of the sheet pile.
Cheers.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Agreed. Especially considering the condition of the deck-to-wall connection at the Southern wall between column lines G.1 and K.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
The exposed rebar seems to me to imply that the construction changed the structure of the wall.
I bet they didn't analyze this.
SF Charlie
Eng-Tips.com Forum Policies
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
SF Charlie
Eng-Tips.com Forum Policies
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Note the significant amount of sand (or additional topping) under the tile in the area between the hot tub and the pool. In the first image, it appears that the sand layer tails off to nothing.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Yes! A properly designed slab and column design will function like this!
I would have preferred to say "column connections to the slab fail", but yes!
Yes! The "drooping" in the slab, seems to have occurred between the wall and the first column, been worst over the 30 foot span, and between columns.
I apologize for not making myself clear!
SF Charlie
Eng-Tips.com Forum Policies
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Thanks for the photos. Do you think that was done intentionally to prevent rainwater from draining into the pool and hot tub, perhaps?
I agree with this in theory, but in practice, if design was weak (a single row of rebar at 12" centers, with minimal engagement), the construction was not well monitored (not considered a critical part of the structure), after years of corrosion, with regions bounded by construction joints, and the deck cracks as shown below (from thread 15), then the deck will be pulled from the wall.
Weak wall-deck connection:
Location of cracks and movement of deck matching photographic evidence (I hope you don't mind me using the version with your markup MaudSTL):
Edit: If the wall-deck connection was as strong as it should be in theory, why did it fail at all? I don't believe there is a mechanism that can achieve the tension cracks seen in the top of the stampcrete in the parking deck if the collapse begins North of column line 15. Can anyone sketch a sectional elevation showing the intermediate positions of the deck components that achieves those tension cracks in the top surface?
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Please can you be specific? I would like to understand more about your perspective and see if it can be improved at all.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
That section of the deck is supported in cantilever by the columns to the north:
Remember the crack in the top surface in tension runs from the South-West at planter at column line G.1 to the North-East column at Column line K as shown in the diagram in my post on 27 Feb 22 18:29. Included again here for convenience.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Approximately like this. With the section on column line I.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
A lot of Construction Engineering and Failure Analysis Videos are no longer available on YouTube, indicating the 'Ministry of Truth' had them pulled?
However, the recent ones I watched, suffering thru the noise, I did find nuggets buried in each once, which indicate that I14 and I 14.1 could be the center of initial failure area. He even showed Leman's Assumptions for her model that were way off, and drove the answer the model spit out. I see why you have to throw out the MH model now, based upon invalid constraints input into the model.
He also supports parking deck failing first, then patio deck, then building. He also makes an argument the insurance companies don't just settle out of court for a Billion Dollars without getting some benefit out of doing this. That being they would be able to raise insurance premiums drastically to recoup their payout.
He also shows NIST destroying evidence in a video, and dragging a rebar out of a sample they cut with jack hammers and sledge hammers. Also the fact they pulling samples in the wrong area, and had already destroyed the evidence in the potential root cause area, as if they had already decided what the cause would be.
Tough to listen to his videos, and you will need to keep your fast forward key warm. However, he is receiving information the general public does not have access to.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
SF Charlie
Eng-Tips.com Forum Policies
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Would you please link to that particular video? I’d like to try to listen to it.
FWIW, I listened to Kai’s early videos, quitting when he started focusing on insults received and starting fights with other YouTubers. But as I recall, he almost immediately after the collapse theorized that the locus of failure was the very area we are currently discussing, based on his construction expertise and analysis of how the punching shear scraped specific sides of the columns and how the slabs “butterflied.” I think Kai intuitively understands materials.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Are you speaking of Kai Kostack?
SF Charlie
Eng-Tips.com Forum Policies
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
SF Charlie
Eng-Tips.com Forum Policies
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
I remembered watching that video. Here is the link:
Champlain Towers Collapse Dawn Lehman WRONG GYM Disregarding VIDEO evidence
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
I completely understand that a lot of his comments are offensive and that is regrettable. But he does make some valid and important observations that should not be dismissed.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
@MaudSTL Please let me know when you have the link.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Far view of planter:
Near view of planter:
Inside view of planter:
If you look closely at the gap you can see two branches emerging. Both have been torn off, the top one appears to have scrunched the paint up as it was broken off.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
IanCA I appreciate you providing the link to Kai's video. I must say it is one of the easier ones to watch, and does contain logical conclusions from the evidence pictured.
I also stumbled upon the one where he gives you some perspective on how connected Michael and Cassie Stratton are to the White House, and casued me to duck duck go Michael Stratton. I will provide a quote from Michael Stratton's web site, and a link to it.
I leave it to the reader to come to their own conclusions as to whether this person's connections had anything to do with the large settlement for the individuals that lost their lives in the collapse. 'Quit quo pro' as they say.
Kai's message also could explain why NIST jumped in and took over the investigation, and that a Billion Dollar Settlement is reached on an unproved theory. I will also include an article from ENRsoutheast.
First a quote form Michael Statton's Web Site, and link:
"Distinguished Democratic strategist. Decades of on-the-ground campaign experience across the United States. Trusted confidant of business leaders and policymakers."
"Mike Stratton draws on his 50 years of frontline experience in Democratic politics managing campaigns and serving in senior government positions to shepherd clients through multijurisdictional policy issues. He served in top positions for 10 presidential campaigns, worked in the U.S. Senate, and served as an appointee in the Carter and Clinton administrations. Now, he offers clients keen insight into the interplay between federal, state and local policy arenas and advocates before all levels of government to advance industry objectives.
Trusted by mayors, attorneys general, governors and federal policymakers, Mike understands how to activate grassroots and grasstops organizations to achieve his clients’ business goals. He provides critical deal-specific consultations for domestic and international clients, negotiating sophisticated business deals, peace initiatives and foreign policy issues.
A leading voice in the hierarchy of the Democratic Party, Mike develops and executes strategies to achieve electoral victories for Democrats across the country. He has served as a member of the Democratic National Committee, and most recently, was reappointed by the Biden campaign.
A native of Durango, Colorado, Mike played an integral role in the successful campaigns of Sen. Michael Bennet (D-CO) and former Gov. John Hickenlooper (D-CO). He is active in state politics across the country and is considered the dean of advisors to the Democratic Governors Association and the Democratic Attorneys General Association."
https://www.bhfs.com/people/policy/michael-stratto...
Next the ENRsoutheast article:
https://www.enr.com/articles/54126-unproven-theory...
Edit: I think IanCA has identified that roots may have played a role in the separated planter corner, and perhaps that area had been trouble before and roots were cut back and it skimmed over and finally let go. I did see in some of Kai's video's where it clearly looks like the planters on both sides of the parking deck/patio gate were already sagging.
I would also like to note Kai talks about torque on two way slab created by columns that are offset and NOT aligned, and point out that the worst area in between K13.1(under East Planter wall) and K15 (parking deck west side of planters).
He cites ACI recommendations on column offsets and says design is not complaint even in 1979. I think SFC has a copy of those docuuments and could possible comment on that or provide confirmation of Kai's statements about allowable offset angles between columns on 2 way slab.
Edit: Link to some available Kai video's
https://www.youtube.com/watch?v=babReMh9Exs
https://www.youtube.com/channel/UC-_5I5xDiFVcxlnG7...
https://www.youtube.com/watch?v=jXdULPG7rQE
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Yes, and an example of how only certain information leaks to control the narrative. So is this another Red Herrin Leak?
So per IanCA's graphic, the roots are raising one side of planter wall, while displacing East the other side.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
SF Charlie
Eng-Tips.com Forum Policies
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
https://www.youtube.com/watch?v=babReMh9Exs
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
The red ovals have been IDed as elastomer, possibly from a previous repair.
Thanks the link worked
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
@Jeff Ostroff Let me know if you want me to delete my post with the link, please.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
I feel confident that the longer red oval contains a root or branch. It doesn't connect to other areas of elastomer, it has a different color, it has an outline suggesting fibers and less flexibility, and it extends from the crack, not the surface.
I did speculate about the contents of the upper red circle I cannot really see that clearly but I see the paint was scrunched up. That was possibly done by the object in the lower circle which sprang back down after being pulled up and broken off?
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
To me in the photo, I see a bias in the South Side rebar to the West (towards parking deck), but mostly a straight down drop it appears
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Please review my diagram at SFCharlie (Computer) 19 May 22 14:33. Thanks
SF Charlie
Eng-Tips.com Forum Policies
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
You make a good case. This might be an example of people seeing what they are most predisposed to see. Confirmation bias. Those darn photos. An engineer looked at the actual site and said it was roots. Why is it so easy just to dismiss that?
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
From the picture previously posted below, we know water was pouring down the South side of the column, so apparently already a crack on that side.
The compass heading to SW of that one rebar could be the tug from the parking deck area collapse?
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
I could picture 1 or 2 columns doing this but since it was every deck column, it points to a design or material defect in the columns as well as the slab.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
You probably see that as the deck drooped over the column, it bent the rebar down. What's being discussed is that the rebar appeared to have been running north south before it was bent down. I remember posts and video showing that the rebar in the deck also only ran N-S, Not W-E as it should have in the before construction plans.
SF Charlie
Eng-Tips.com Forum Policies
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
SF Charlie
Eng-Tips.com Forum Policies
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Of course they are bent down but they didn't turn to the north and south form their installed NE/SE/NW/SW directions. They weren't installed in the designed orientation. Not worth three posts explaining if it was even worth one.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Sorry, I respectfully disagree with you, on this one, at this time based upon evidence reviewed. However, I obviously did not articulate well the kind of details that Construction Engineering & Failure Analysis is looking at for clues in his videos.
Edit: Better to just watch his video's, if interested and can tolerate them. He actually has gotten a lot better since the first one I saw on the New Orlean's HardRock Hotel Collapse. After viewing one then, I quit watching his channel, and avoided it totally, until the last new videos were mentioned.
I could not finish some of the videos I found either, and only posted ones I thought were better and made good points.
EDIT on Two Way Slab Column Offset: The link below quotes ACI 318-11, and says column offset shall not be more than 10 degrees. Again, I think SFCharlie has the ACI Code from 1979, and could perhaps confirm what it said in 1979.
Under limitations, "Column offset of more than 10% of the span (in the direction of offset) from either axis between the centerline of the successive column is not permitted."
https://theconstructor.org/structural-engg/two-way...
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
I got bottle of Tums?
SF Charlie
Eng-Tips.com Forum Policies
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Haha! I actually saw one of his wedding cake video's too! He was proving something, perhaps about lighting in photography of a wedding cake???
I really have no idea what his name is, I just took MaudSTL mentioning Kai, and ran with it. Probably another BAD ASS_U_mption on my part....
Oh well, he needs a name since CE&FA is a mouth full.
Edit: Here is Structural Magazine Recommended details on offset columns. Spoiler alert, additional layer of rebar....
https://www.structuremag.org/?p=14580
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
I'm stocked up on Prilosec, thanks. Not an endorsement. There's a reason why they want the tensile vectors to align with the bar. And I am sure there are plenty of scholarly articles on what happens if they aren't. I'm just trying to formulate in my mind what happens. I'm too lazy to look it up. For starters I am trying to imagine them at 45 degrees. I know it's bad though. I'm not working too hard on it though. And I don't have a slide rule in hand.
Edit: well having found that you must used finite element analysis in the design where the column offset exceeds 10%, I came to a halt. The gist of it I think is that you get a torsional component at the column strips. And it might mean that eliminating that beam was a particularly bad idea. Does that mean that whomever made that choice was bad at finite element? Inquiring minds and all that. This most likely has been looked at over and over at this point.
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
SF Charlie
Eng-Tips.com Forum Policies
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
SF Charlie
Eng-Tips.com Forum Policies
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16
Please allow me to move the discussion to Miami Beach, Champlain Towers South apartment building collapse, Part 17, Thank-you.
Someone Please close this post to new postings, or message me how to do this, Thanks.
SF Charlie
Eng-Tips.com Forum Policies
RE: Miami Beach, Champlain Towers South apartment building collapse, Part 16